Error 327 on Rapid (Z Axis Move)
Moderator: cnckeith
-
- Posts: 817
- Joined: Thu Feb 08, 2018 7:57 am
- Acorn CNC Controller: No
- Plasma CNC Controller: No
- AcornSix CNC Controller: No
- Allin1DC CNC Controller: No
- Hickory CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC11: No
- CPU10 or CPU7: No
Error 327 on Rapid (Z Axis Move)
New error for me, not had this before.
I'm getting an Error 327 - same place each time when trying to cut a part. I dont have the code, but ive slowed down the Axis. Ill get the code across in a bit but Report attached.
From other errors it sounds like a noise issue but not had issues before, suggestions welcome.
Thanks
I'm getting an Error 327 - same place each time when trying to cut a part. I dont have the code, but ive slowed down the Axis. Ill get the code across in a bit but Report attached.
From other errors it sounds like a noise issue but not had issues before, suggestions welcome.
Thanks
- Attachments
-
- report_C8FD19C4742C-0309180722_2019-09-14_15-12-31.zip
- (281 KiB) Downloaded 110 times
(Note: Liking will "up vote" a post in the search results helping others find good information faster)
-
- Site Admin
- Posts: 9047
- Joined: Wed Mar 03, 2010 4:23 pm
- Acorn CNC Controller: Yes
- Plasma CNC Controller: No
- AcornSix CNC Controller: No
- Allin1DC CNC Controller: Yes
- Hickory CNC Controller: No
- Oak CNC controller: Yes
- CNC Control System Serial Number: none
- DC3IOB: Yes
- CNC11: Yes
- CPU10 or CPU7: Yes
- Contact:
Re: Error 327 on Rapid (Z Axis Move)
Hello.
the message logs contained in the report.zip file show communication issues with the CNCPC and the Acorn. Check connections both physical and software settings in Windows. Ping the Ethernet address to debug. make sure there is no Virus software installed and running to debug.
(4) 09-14-2019 15:06:54 4032 Reset Cleared
(4) 09-14-2019 15:07:06 944 MPU requested resend # 332
(4) 09-14-2019 15:07:06 946 PC resending # 1931
(4) 09-14-2019 15:10:58 944 MPU requested resend # 333
(4) 09-14-2019 15:10:58 946 PC resending # 1934
(4) 09-14-2019 15:11:00 944 MPU requested resend # 334
(4) 09-14-2019 15:11:00 946 PC resending # 1937
(4) 09-14-2019 15:11:12 944 MPU requested resend # 335
(4) 09-14-2019 15:11:12 946 PC resending # 1940
(4) 09-14-2019 15:11:22 944 MPU requested resend # 336
(4) 09-14-2019 15:11:22 946 PC resending # 1943
(4) 09-14-2019 15:12:04 944 MPU requested resend # 339
(4) 09-14-2019 15:12:04 946 PC resending # 1952
(4) 09-14-2019 15:12:04 946 PC resending # 1955
(1) 09-14-2019 15:12:31 Creating report...
the message logs contained in the report.zip file show communication issues with the CNCPC and the Acorn. Check connections both physical and software settings in Windows. Ping the Ethernet address to debug. make sure there is no Virus software installed and running to debug.
(4) 09-14-2019 15:06:54 4032 Reset Cleared
(4) 09-14-2019 15:07:06 944 MPU requested resend # 332
(4) 09-14-2019 15:07:06 946 PC resending # 1931
(4) 09-14-2019 15:10:58 944 MPU requested resend # 333
(4) 09-14-2019 15:10:58 946 PC resending # 1934
(4) 09-14-2019 15:11:00 944 MPU requested resend # 334
(4) 09-14-2019 15:11:00 946 PC resending # 1937
(4) 09-14-2019 15:11:12 944 MPU requested resend # 335
(4) 09-14-2019 15:11:12 946 PC resending # 1940
(4) 09-14-2019 15:11:22 944 MPU requested resend # 336
(4) 09-14-2019 15:11:22 946 PC resending # 1943
(4) 09-14-2019 15:12:04 944 MPU requested resend # 339
(4) 09-14-2019 15:12:04 946 PC resending # 1952
(4) 09-14-2019 15:12:04 946 PC resending # 1955
(1) 09-14-2019 15:12:31 Creating report...
Need support? READ THIS POST first. http://centroidcncforum.com/viewtopic.php?f=60&t=1043
All Acorn Documentation is located here: viewtopic.php?f=60&t=3397
Answers to common questions: viewforum.php?f=63
Gear we use but don't sell. https://www.centroidcnc.com/centroid_di ... _gear.html
All Acorn Documentation is located here: viewtopic.php?f=60&t=3397
Answers to common questions: viewforum.php?f=63
Gear we use but don't sell. https://www.centroidcnc.com/centroid_di ... _gear.html
(Note: Liking will "up vote" a post in the search results helping others find good information faster)
-
- Posts: 817
- Joined: Thu Feb 08, 2018 7:57 am
- Acorn CNC Controller: No
- Plasma CNC Controller: No
- AcornSix CNC Controller: No
- Allin1DC CNC Controller: No
- Hickory CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC11: No
- CPU10 or CPU7: No
Re: Error 327 on Rapid (Z Axis Move)
Thanks, saw them in the logs. Unusual, not had issues with this setup at all before.cnckeith wrote: ↑Sat Sep 14, 2019 12:21 pm Hello.
the message logs contained in the report.zip file show communication issues with the CNCPC and the Acorn. Check connections both physical and software settings in Windows. Ping the Ethernet address to debug. make sure there is no Virus software installed and running to debug.
(4) 09-14-2019 15:06:54 4032 Reset Cleared
(4) 09-14-2019 15:07:06 944 MPU requested resend # 332
(4) 09-14-2019 15:07:06 946 PC resending # 1931
(4) 09-14-2019 15:10:58 944 MPU requested resend # 333
(4) 09-14-2019 15:10:58 946 PC resending # 1934
(4) 09-14-2019 15:11:00 944 MPU requested resend # 334
(4) 09-14-2019 15:11:00 946 PC resending # 1937
(4) 09-14-2019 15:11:12 944 MPU requested resend # 335
(4) 09-14-2019 15:11:12 946 PC resending # 1940
(4) 09-14-2019 15:11:22 944 MPU requested resend # 336
(4) 09-14-2019 15:11:22 946 PC resending # 1943
(4) 09-14-2019 15:12:04 944 MPU requested resend # 339
(4) 09-14-2019 15:12:04 946 PC resending # 1952
(4) 09-14-2019 15:12:04 946 PC resending # 1955
(1) 09-14-2019 15:12:31 Creating report...
(Note: Liking will "up vote" a post in the search results helping others find good information faster)
-
- Community Expert
- Posts: 9958
- Joined: Tue Mar 28, 2017 12:01 pm
- Acorn CNC Controller: Yes
- Plasma CNC Controller: Yes
- AcornSix CNC Controller: Yes
- Allin1DC CNC Controller: Yes
- Hickory CNC Controller: Yes
- Oak CNC controller: No
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
- Location: Mesa, AZ
Re: Error 327 on Rapid (Z Axis Move)
Make sure you are using shielded ethernet cables. Make sure PC, ethernet cable are seated very well and routed away from anything that can cause EMIChaz wrote: ↑Sat Sep 14, 2019 2:54 pmThanks, saw them in the logs. Unusual, not had issues with this setup at all before.cnckeith wrote: ↑Sat Sep 14, 2019 12:21 pm Hello.
the message logs contained in the report.zip file show communication issues with the CNCPC and the Acorn. Check connections both physical and software settings in Windows. Ping the Ethernet address to debug. make sure there is no Virus software installed and running to debug.
(4) 09-14-2019 15:06:54 4032 Reset Cleared
(4) 09-14-2019 15:07:06 944 MPU requested resend # 332
(4) 09-14-2019 15:07:06 946 PC resending # 1931
(4) 09-14-2019 15:10:58 944 MPU requested resend # 333
(4) 09-14-2019 15:10:58 946 PC resending # 1934
(4) 09-14-2019 15:11:00 944 MPU requested resend # 334
(4) 09-14-2019 15:11:00 946 PC resending # 1937
(4) 09-14-2019 15:11:12 944 MPU requested resend # 335
(4) 09-14-2019 15:11:12 946 PC resending # 1940
(4) 09-14-2019 15:11:22 944 MPU requested resend # 336
(4) 09-14-2019 15:11:22 946 PC resending # 1943
(4) 09-14-2019 15:12:04 944 MPU requested resend # 339
(4) 09-14-2019 15:12:04 946 PC resending # 1952
(4) 09-14-2019 15:12:04 946 PC resending # 1955
(1) 09-14-2019 15:12:31 Creating report...
Reminder, for support please follow this post: viewtopic.php?f=20&t=383
We can't "SEE" what you see...
Mesa, AZ
We can't "SEE" what you see...
Mesa, AZ
(Note: Liking will "up vote" a post in the search results helping others find good information faster)
-
- Posts: 817
- Joined: Thu Feb 08, 2018 7:57 am
- Acorn CNC Controller: No
- Plasma CNC Controller: No
- AcornSix CNC Controller: No
- Allin1DC CNC Controller: No
- Hickory CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC11: No
- CPU10 or CPU7: No
Re: Error 327 on Rapid (Z Axis Move)
Thanks, its using the supplied Ethernet cable and is as it was before the problem started. I did install a small VFD however to run the coolant pump but its in its own box with the Spindle VFD. Ill disconnect it and see if the problem goes away.martyscncgarage wrote: ↑Sun Sep 15, 2019 11:32 amMake sure you are using shielded ethernet cables. Make sure PC, ethernet cable are seated very well and routed away from anything that can cause EMIChaz wrote: ↑Sat Sep 14, 2019 2:54 pmThanks, saw them in the logs. Unusual, not had issues with this setup at all before.cnckeith wrote: ↑Sat Sep 14, 2019 12:21 pm Hello.
the message logs contained in the report.zip file show communication issues with the CNCPC and the Acorn. Check connections both physical and software settings in Windows. Ping the Ethernet address to debug. make sure there is no Virus software installed and running to debug.
(4) 09-14-2019 15:06:54 4032 Reset Cleared
(4) 09-14-2019 15:07:06 944 MPU requested resend # 332
(4) 09-14-2019 15:07:06 946 PC resending # 1931
(4) 09-14-2019 15:10:58 944 MPU requested resend # 333
(4) 09-14-2019 15:10:58 946 PC resending # 1934
(4) 09-14-2019 15:11:00 944 MPU requested resend # 334
(4) 09-14-2019 15:11:00 946 PC resending # 1937
(4) 09-14-2019 15:11:12 944 MPU requested resend # 335
(4) 09-14-2019 15:11:12 946 PC resending # 1940
(4) 09-14-2019 15:11:22 944 MPU requested resend # 336
(4) 09-14-2019 15:11:22 946 PC resending # 1943
(4) 09-14-2019 15:12:04 944 MPU requested resend # 339
(4) 09-14-2019 15:12:04 946 PC resending # 1952
(4) 09-14-2019 15:12:04 946 PC resending # 1955
(1) 09-14-2019 15:12:31 Creating report...
(Note: Liking will "up vote" a post in the search results helping others find good information faster)
-
- Community Expert
- Posts: 9958
- Joined: Tue Mar 28, 2017 12:01 pm
- Acorn CNC Controller: Yes
- Plasma CNC Controller: Yes
- AcornSix CNC Controller: Yes
- Allin1DC CNC Controller: Yes
- Hickory CNC Controller: Yes
- Oak CNC controller: No
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
- Location: Mesa, AZ
Re: Error 327 on Rapid (Z Axis Move)
Might be the coolant pump vfd.
I'll be interested to know what you find
I'll be interested to know what you find
Reminder, for support please follow this post: viewtopic.php?f=20&t=383
We can't "SEE" what you see...
Mesa, AZ
We can't "SEE" what you see...
Mesa, AZ
(Note: Liking will "up vote" a post in the search results helping others find good information faster)
-
- Posts: 817
- Joined: Thu Feb 08, 2018 7:57 am
- Acorn CNC Controller: No
- Plasma CNC Controller: No
- AcornSix CNC Controller: No
- Allin1DC CNC Controller: No
- Hickory CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC11: No
- CPU10 or CPU7: No
Re: Error 327 on Rapid (Z Axis Move)
Indeed. The VFD wasnt running at the time but its connected and powered.martyscncgarage wrote: ↑Sun Sep 15, 2019 6:39 pm Might be the coolant pump vfd.
I'll be interested to know what you find
(Note: Liking will "up vote" a post in the search results helping others find good information faster)
-
- Posts: 817
- Joined: Thu Feb 08, 2018 7:57 am
- Acorn CNC Controller: No
- Plasma CNC Controller: No
- AcornSix CNC Controller: No
- Allin1DC CNC Controller: No
- Hickory CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC11: No
- CPU10 or CPU7: No
Re: Error 327 on Rapid (Z Axis Move)
Ok, tested again.
VFD disconnected, no problems.
VFD connected, not running, same issue.
The VFD is power from the same powersource in a cabinet adjacent to where the Acorn controller is. The only wiring going to it from Acorn is an unshielded 3 core cable, using 2 cores to switch on the VFD to run the coolant pump.
From the VFD it goes to the motor via a route nowhere near the Acorn setup.
What's interesting is that it shows:-
9031 DRIVE FAULT!
327 Fault
Yet there is no fault wiring going to the HSS86 drives, so how / why does Acorn think there is a drive fault?
New report attached.
VFD disconnected, no problems.
VFD connected, not running, same issue.
The VFD is power from the same powersource in a cabinet adjacent to where the Acorn controller is. The only wiring going to it from Acorn is an unshielded 3 core cable, using 2 cores to switch on the VFD to run the coolant pump.
From the VFD it goes to the motor via a route nowhere near the Acorn setup.
What's interesting is that it shows:-
9031 DRIVE FAULT!
327 Fault
Yet there is no fault wiring going to the HSS86 drives, so how / why does Acorn think there is a drive fault?
New report attached.
- Attachments
-
- report_C8FD19C4742C-0309180722_2019-09-16_19-19-04.zip
- (281.4 KiB) Downloaded 85 times
(Note: Liking will "up vote" a post in the search results helping others find good information faster)
-
- Community Expert
- Posts: 9958
- Joined: Tue Mar 28, 2017 12:01 pm
- Acorn CNC Controller: Yes
- Plasma CNC Controller: Yes
- AcornSix CNC Controller: Yes
- Allin1DC CNC Controller: Yes
- Hickory CNC Controller: Yes
- Oak CNC controller: No
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
- Location: Mesa, AZ
Re: Error 327 on Rapid (Z Axis Move)
ChazChaz wrote: ↑Mon Sep 16, 2019 2:38 pm Ok, tested again.
VFD disconnected, no problems.
VFD connected, not running, same issue.
The VFD is power from the same powersource in a cabinet adjacent to where the Acorn controller is. The only wiring going to it from Acorn is an unshielded 3 core cable, using 2 cores to switch on the VFD to run the coolant pump.
From the VFD it goes to the motor via a route nowhere near the Acorn setup.
What's interesting is that it shows:-
9031 DRIVE FAULT!
327 Fault
Yet there is no fault wiring going to the HSS86 drives, so how / why does Acorn think there is a drive fault?
New report attached.
Open your Report, then go down and file the file URF.ZIP. Open it and look at the MSG_LOG. TXT
You will see a bunch of this:
(1) 09-14-2019 15:12:37 Saved report to C:\Users\User\Documents\report_C8FD19C4742C-0309180722_2019-09-14_15-12-31.zip
(1) 09-14-2019 15:12:46 204 Exiting CNC...Normal Exit (66)
(1) 09-16-2019 19:00:43 199 CNC Started
(4) 09-16-2019 19:00:48 944 MPU requested resend # 20
(4) 09-16-2019 19:00:48 946 PC resending # 911
(1) 09-16-2019 19:00:51 CNC12 Lathe v4.18
(4) 09-16-2019 19:00:54 9033 Reset Initiated, Press Reset to Clear
(4) 09-16-2019 19:01:05 4032 Reset Cleared
(4) 09-16-2019 19:01:10 944 MPU requested resend # 21
(4) 09-16-2019 19:01:10 946 PC resending # 913
(4) 09-16-2019 19:01:10 944 MPU requested resend # 22
(4) 09-16-2019 19:01:10 946 PC resending # 915
(4) 09-16-2019 19:01:10 944 MPU requested resend # 23
(4) 09-16-2019 19:01:10 946 PC resending # 917
(4) 09-16-2019 19:01:10 946 PC resending # 918
(4) 09-16-2019 19:01:21 9033 Reset Initiated, Press Reset to Clear
(4) 09-16-2019 19:01:21 944 MPU requested resend # 24
(4) 09-16-2019 19:01:21 946 PC resending # 929
(4) 09-16-2019 19:01:22 4032 Reset Cleared
(4) 09-16-2019 19:01:28 944 MPU requested resend # 25
(4) 09-16-2019 19:01:28 946 PC resending # 932
(4) 09-16-2019 19:03:00 944 MPU requested resend # 26
(4) 09-16-2019 19:03:00 946 PC resending # 938
(4) 09-16-2019 19:03:41 944 MPU requested resend # 27
(4) 09-16-2019 19:03:41 946 PC resending # 943
(4) 09-16-2019 19:03:58 944 MPU requested resend # 28
(4) 09-16-2019 19:03:58 946 PC resending # 946
(4) 09-16-2019 19:04:00 944 MPU requested resend # 29
(4) 09-16-2019 19:04:00 946 PC resending # 948
(4) 09-16-2019 19:04:03 944 MPU requested resend # 30
(4) 09-16-2019 19:04:03 946 PC resending # 951
(4) 09-16-2019 19:06:32 944 MPU requested resend # 31
(4) 09-16-2019 19:06:32 946 PC resending # 953
(4) 09-16-2019 19:06:58 944 MPU requested resend # 32
(4) 09-16-2019 19:06:58 946 PC resending # 956
(4) 09-16-2019 19:07:00 944 MPU requested resend # 33
(4) 09-16-2019 19:07:00 946 PC resending # 958
(4) 09-16-2019 19:07:01 944 MPU requested resend # 34
(4) 09-16-2019 19:07:01 946 PC resending # 960
(1) 09-16-2019 19:07:30 204 Exiting CNC...Normal Exit (66)
(1) 09-16-2019 19:14:19 199 CNC Started
(1) 09-16-2019 19:14:26 CNC12 Lathe v4.18
(4) 09-16-2019 19:14:30 9033 Reset Initiated, Press Reset to Clear
(4) 09-16-2019 19:14:32 4032 Reset Cleared
(4) 09-16-2019 19:15:36 9033 Reset Initiated, Press Reset to Clear
(4) 09-16-2019 19:15:37 4032 Reset Cleared
(4) 09-16-2019 19:17:54 9031 DRIVE FAULT!
(1) 09-16-2019 19:19:04 Creating report...
The MPU REquest resend is bad ethernet packet data. Likely from NOISE.
Open your diagnostic screen (Alt+i) look at your Drive Fault input, what state is it?
I think you have a nasty VFD...
What is "3 core cable"?
I would use the digital inputs on the VFD to turn your pump on and off, not power up and down the VFD if that's what you are doing....
Marty
Reminder, for support please follow this post: viewtopic.php?f=20&t=383
We can't "SEE" what you see...
Mesa, AZ
We can't "SEE" what you see...
Mesa, AZ
(Note: Liking will "up vote" a post in the search results helping others find good information faster)
-
- Posts: 817
- Joined: Thu Feb 08, 2018 7:57 am
- Acorn CNC Controller: No
- Plasma CNC Controller: No
- AcornSix CNC Controller: No
- Allin1DC CNC Controller: No
- Hickory CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC11: No
- CPU10 or CPU7: No
Re: Error 327 on Rapid (Z Axis Move)
Thanks, saw those messages in the logs too. I dont believe I have anything connected to the input for drive fault. Need to check, the machine was retrofitted by another forum member here. Ive got some screenshots (Ive closed up the garage for now), so wont head back in tonight.martyscncgarage wrote: ↑Mon Sep 16, 2019 2:55 pmChazChaz wrote: ↑Mon Sep 16, 2019 2:38 pm Ok, tested again.
VFD disconnected, no problems.
VFD connected, not running, same issue.
The VFD is power from the same powersource in a cabinet adjacent to where the Acorn controller is. The only wiring going to it from Acorn is an unshielded 3 core cable, using 2 cores to switch on the VFD to run the coolant pump.
From the VFD it goes to the motor via a route nowhere near the Acorn setup.
What's interesting is that it shows:-
9031 DRIVE FAULT!
327 Fault
Yet there is no fault wiring going to the HSS86 drives, so how / why does Acorn think there is a drive fault?
New report attached.
Open your Report, then go down and file the file URF.ZIP. Open it and look at the MSG_LOG. TXT
You will see a bunch of this:
(1) 09-14-2019 15:12:37 Saved report to C:\Users\User\Documents\report_C8FD19C4742C-0309180722_2019-09-14_15-12-31.zip
(1) 09-14-2019 15:12:46 204 Exiting CNC...Normal Exit (66)
(1) 09-16-2019 19:00:43 199 CNC Started
(4) 09-16-2019 19:00:48 944 MPU requested resend # 20
(4) 09-16-2019 19:00:48 946 PC resending # 911
(1) 09-16-2019 19:00:51 CNC12 Lathe v4.18
(4) 09-16-2019 19:00:54 9033 Reset Initiated, Press Reset to Clear
(4) 09-16-2019 19:01:05 4032 Reset Cleared
(4) 09-16-2019 19:01:10 944 MPU requested resend # 21
(4) 09-16-2019 19:01:10 946 PC resending # 913
(4) 09-16-2019 19:01:10 944 MPU requested resend # 22
(4) 09-16-2019 19:01:10 946 PC resending # 915
(4) 09-16-2019 19:01:10 944 MPU requested resend # 23
(4) 09-16-2019 19:01:10 946 PC resending # 917
(4) 09-16-2019 19:01:10 946 PC resending # 918
(4) 09-16-2019 19:01:21 9033 Reset Initiated, Press Reset to Clear
(4) 09-16-2019 19:01:21 944 MPU requested resend # 24
(4) 09-16-2019 19:01:21 946 PC resending # 929
(4) 09-16-2019 19:01:22 4032 Reset Cleared
(4) 09-16-2019 19:01:28 944 MPU requested resend # 25
(4) 09-16-2019 19:01:28 946 PC resending # 932
(4) 09-16-2019 19:03:00 944 MPU requested resend # 26
(4) 09-16-2019 19:03:00 946 PC resending # 938
(4) 09-16-2019 19:03:41 944 MPU requested resend # 27
(4) 09-16-2019 19:03:41 946 PC resending # 943
(4) 09-16-2019 19:03:58 944 MPU requested resend # 28
(4) 09-16-2019 19:03:58 946 PC resending # 946
(4) 09-16-2019 19:04:00 944 MPU requested resend # 29
(4) 09-16-2019 19:04:00 946 PC resending # 948
(4) 09-16-2019 19:04:03 944 MPU requested resend # 30
(4) 09-16-2019 19:04:03 946 PC resending # 951
(4) 09-16-2019 19:06:32 944 MPU requested resend # 31
(4) 09-16-2019 19:06:32 946 PC resending # 953
(4) 09-16-2019 19:06:58 944 MPU requested resend # 32
(4) 09-16-2019 19:06:58 946 PC resending # 956
(4) 09-16-2019 19:07:00 944 MPU requested resend # 33
(4) 09-16-2019 19:07:00 946 PC resending # 958
(4) 09-16-2019 19:07:01 944 MPU requested resend # 34
(4) 09-16-2019 19:07:01 946 PC resending # 960
(1) 09-16-2019 19:07:30 204 Exiting CNC...Normal Exit (66)
(1) 09-16-2019 19:14:19 199 CNC Started
(1) 09-16-2019 19:14:26 CNC12 Lathe v4.18
(4) 09-16-2019 19:14:30 9033 Reset Initiated, Press Reset to Clear
(4) 09-16-2019 19:14:32 4032 Reset Cleared
(4) 09-16-2019 19:15:36 9033 Reset Initiated, Press Reset to Clear
(4) 09-16-2019 19:15:37 4032 Reset Cleared
(4) 09-16-2019 19:17:54 9031 DRIVE FAULT!
(1) 09-16-2019 19:19:04 Creating report...
The MPU REquest resend is bad ethernet packet data. Likely from NOISE.
Open your diagnostic screen (Alt+i) look at your Drive Fault input, what state is it?
I think you have a nasty VFD...
Marty
(Note: Liking will "up vote" a post in the search results helping others find good information faster)