Error 327 on Rapid (Z Axis Move)

All things related to the Centroid Acorn CNC Controller

Moderator: cnckeith

Chaz
Posts: 767
Joined: Thu Feb 08, 2018 7:57 am
Acorn CNC Controller: No
Allin1DC CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC11: No
CPU10 or CPU7: No

Error 327 on Rapid (Z Axis Move)

Post by Chaz »

New error for me, not had this before.

I'm getting an Error 327 - same place each time when trying to cut a part. I dont have the code, but ive slowed down the Axis. Ill get the code across in a bit but Report attached.

From other errors it sounds like a noise issue but not had issues before, suggestions welcome.

Thanks
Attachments
report_C8FD19C4742C-0309180722_2019-09-14_15-12-31.zip
(281 KiB) Downloaded 109 times


cnckeith
Site Admin
Posts: 8954
Joined: Wed Mar 03, 2010 4:23 pm
Acorn CNC Controller: Yes
Allin1DC CNC Controller: Yes
Oak CNC controller: Yes
CNC Control System Serial Number: none
DC3IOB: Yes
CNC11: Yes
CPU10 or CPU7: Yes
Contact:

Re: Error 327 on Rapid (Z Axis Move)

Post by cnckeith »

Hello.
the message logs contained in the report.zip file show communication issues with the CNCPC and the Acorn. Check connections both physical and software settings in Windows. Ping the Ethernet address to debug. make sure there is no Virus software installed and running to debug.

(4) 09-14-2019 15:06:54 4032 Reset Cleared
(4) 09-14-2019 15:07:06 944 MPU requested resend # 332
(4) 09-14-2019 15:07:06 946 PC resending # 1931
(4) 09-14-2019 15:10:58 944 MPU requested resend # 333
(4) 09-14-2019 15:10:58 946 PC resending # 1934
(4) 09-14-2019 15:11:00 944 MPU requested resend # 334
(4) 09-14-2019 15:11:00 946 PC resending # 1937
(4) 09-14-2019 15:11:12 944 MPU requested resend # 335
(4) 09-14-2019 15:11:12 946 PC resending # 1940
(4) 09-14-2019 15:11:22 944 MPU requested resend # 336
(4) 09-14-2019 15:11:22 946 PC resending # 1943
(4) 09-14-2019 15:12:04 944 MPU requested resend # 339
(4) 09-14-2019 15:12:04 946 PC resending # 1952
(4) 09-14-2019 15:12:04 946 PC resending # 1955
(1) 09-14-2019 15:12:31 Creating report...
Need support? READ THIS POST first. http://centroidcncforum.com/viewtopic.php?f=60&t=1043
All Acorn Documentation is located here: viewtopic.php?f=60&t=3397
Answers to common questions: viewforum.php?f=63
and here viewforum.php?f=61
Gear we use but don't sell. https://www.centroidcnc.com/centroid_di ... _gear.html


Chaz
Posts: 767
Joined: Thu Feb 08, 2018 7:57 am
Acorn CNC Controller: No
Allin1DC CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC11: No
CPU10 or CPU7: No

Re: Error 327 on Rapid (Z Axis Move)

Post by Chaz »

cnckeith wrote: Sat Sep 14, 2019 12:21 pm Hello.
the message logs contained in the report.zip file show communication issues with the CNCPC and the Acorn. Check connections both physical and software settings in Windows. Ping the Ethernet address to debug. make sure there is no Virus software installed and running to debug.

(4) 09-14-2019 15:06:54 4032 Reset Cleared
(4) 09-14-2019 15:07:06 944 MPU requested resend # 332
(4) 09-14-2019 15:07:06 946 PC resending # 1931
(4) 09-14-2019 15:10:58 944 MPU requested resend # 333
(4) 09-14-2019 15:10:58 946 PC resending # 1934
(4) 09-14-2019 15:11:00 944 MPU requested resend # 334
(4) 09-14-2019 15:11:00 946 PC resending # 1937
(4) 09-14-2019 15:11:12 944 MPU requested resend # 335
(4) 09-14-2019 15:11:12 946 PC resending # 1940
(4) 09-14-2019 15:11:22 944 MPU requested resend # 336
(4) 09-14-2019 15:11:22 946 PC resending # 1943
(4) 09-14-2019 15:12:04 944 MPU requested resend # 339
(4) 09-14-2019 15:12:04 946 PC resending # 1952
(4) 09-14-2019 15:12:04 946 PC resending # 1955
(1) 09-14-2019 15:12:31 Creating report...
Thanks, saw them in the logs. Unusual, not had issues with this setup at all before.


martyscncgarage
Community Expert
Posts: 9953
Joined: Tue Mar 28, 2017 12:01 pm
Acorn CNC Controller: Yes
Allin1DC CNC Controller: Yes
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC12: Yes
CNC11: Yes
CPU10 or CPU7: Yes
Location: Mesa, AZ

Re: Error 327 on Rapid (Z Axis Move)

Post by martyscncgarage »

Chaz wrote: Sat Sep 14, 2019 2:54 pm
cnckeith wrote: Sat Sep 14, 2019 12:21 pm Hello.
the message logs contained in the report.zip file show communication issues with the CNCPC and the Acorn. Check connections both physical and software settings in Windows. Ping the Ethernet address to debug. make sure there is no Virus software installed and running to debug.

(4) 09-14-2019 15:06:54 4032 Reset Cleared
(4) 09-14-2019 15:07:06 944 MPU requested resend # 332
(4) 09-14-2019 15:07:06 946 PC resending # 1931
(4) 09-14-2019 15:10:58 944 MPU requested resend # 333
(4) 09-14-2019 15:10:58 946 PC resending # 1934
(4) 09-14-2019 15:11:00 944 MPU requested resend # 334
(4) 09-14-2019 15:11:00 946 PC resending # 1937
(4) 09-14-2019 15:11:12 944 MPU requested resend # 335
(4) 09-14-2019 15:11:12 946 PC resending # 1940
(4) 09-14-2019 15:11:22 944 MPU requested resend # 336
(4) 09-14-2019 15:11:22 946 PC resending # 1943
(4) 09-14-2019 15:12:04 944 MPU requested resend # 339
(4) 09-14-2019 15:12:04 946 PC resending # 1952
(4) 09-14-2019 15:12:04 946 PC resending # 1955
(1) 09-14-2019 15:12:31 Creating report...
Thanks, saw them in the logs. Unusual, not had issues with this setup at all before.
Make sure you are using shielded ethernet cables. Make sure PC, ethernet cable are seated very well and routed away from anything that can cause EMI
Reminder, for support please follow this post: viewtopic.php?f=20&t=383
We can't "SEE" what you see...
Mesa, AZ


Chaz
Posts: 767
Joined: Thu Feb 08, 2018 7:57 am
Acorn CNC Controller: No
Allin1DC CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC11: No
CPU10 or CPU7: No

Re: Error 327 on Rapid (Z Axis Move)

Post by Chaz »

martyscncgarage wrote: Sun Sep 15, 2019 11:32 am
Chaz wrote: Sat Sep 14, 2019 2:54 pm
cnckeith wrote: Sat Sep 14, 2019 12:21 pm Hello.
the message logs contained in the report.zip file show communication issues with the CNCPC and the Acorn. Check connections both physical and software settings in Windows. Ping the Ethernet address to debug. make sure there is no Virus software installed and running to debug.

(4) 09-14-2019 15:06:54 4032 Reset Cleared
(4) 09-14-2019 15:07:06 944 MPU requested resend # 332
(4) 09-14-2019 15:07:06 946 PC resending # 1931
(4) 09-14-2019 15:10:58 944 MPU requested resend # 333
(4) 09-14-2019 15:10:58 946 PC resending # 1934
(4) 09-14-2019 15:11:00 944 MPU requested resend # 334
(4) 09-14-2019 15:11:00 946 PC resending # 1937
(4) 09-14-2019 15:11:12 944 MPU requested resend # 335
(4) 09-14-2019 15:11:12 946 PC resending # 1940
(4) 09-14-2019 15:11:22 944 MPU requested resend # 336
(4) 09-14-2019 15:11:22 946 PC resending # 1943
(4) 09-14-2019 15:12:04 944 MPU requested resend # 339
(4) 09-14-2019 15:12:04 946 PC resending # 1952
(4) 09-14-2019 15:12:04 946 PC resending # 1955
(1) 09-14-2019 15:12:31 Creating report...
Thanks, saw them in the logs. Unusual, not had issues with this setup at all before.
Make sure you are using shielded ethernet cables. Make sure PC, ethernet cable are seated very well and routed away from anything that can cause EMI
Thanks, its using the supplied Ethernet cable and is as it was before the problem started. I did install a small VFD however to run the coolant pump but its in its own box with the Spindle VFD. Ill disconnect it and see if the problem goes away.


martyscncgarage
Community Expert
Posts: 9953
Joined: Tue Mar 28, 2017 12:01 pm
Acorn CNC Controller: Yes
Allin1DC CNC Controller: Yes
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC12: Yes
CNC11: Yes
CPU10 or CPU7: Yes
Location: Mesa, AZ

Re: Error 327 on Rapid (Z Axis Move)

Post by martyscncgarage »

Might be the coolant pump vfd.
I'll be interested to know what you find
Reminder, for support please follow this post: viewtopic.php?f=20&t=383
We can't "SEE" what you see...
Mesa, AZ


Chaz
Posts: 767
Joined: Thu Feb 08, 2018 7:57 am
Acorn CNC Controller: No
Allin1DC CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC11: No
CPU10 or CPU7: No

Re: Error 327 on Rapid (Z Axis Move)

Post by Chaz »

martyscncgarage wrote: Sun Sep 15, 2019 6:39 pm Might be the coolant pump vfd.
I'll be interested to know what you find
Indeed. The VFD wasnt running at the time but its connected and powered.


Chaz
Posts: 767
Joined: Thu Feb 08, 2018 7:57 am
Acorn CNC Controller: No
Allin1DC CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC11: No
CPU10 or CPU7: No

Re: Error 327 on Rapid (Z Axis Move)

Post by Chaz »

Ok, tested again.

VFD disconnected, no problems.

VFD connected, not running, same issue.

The VFD is power from the same powersource in a cabinet adjacent to where the Acorn controller is. The only wiring going to it from Acorn is an unshielded 3 core cable, using 2 cores to switch on the VFD to run the coolant pump.

From the VFD it goes to the motor via a route nowhere near the Acorn setup.

What's interesting is that it shows:-

9031 DRIVE FAULT!
327 Fault

Yet there is no fault wiring going to the HSS86 drives, so how / why does Acorn think there is a drive fault?

New report attached.
Attachments
report_C8FD19C4742C-0309180722_2019-09-16_19-19-04.zip
(281.4 KiB) Downloaded 84 times


martyscncgarage
Community Expert
Posts: 9953
Joined: Tue Mar 28, 2017 12:01 pm
Acorn CNC Controller: Yes
Allin1DC CNC Controller: Yes
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC12: Yes
CNC11: Yes
CPU10 or CPU7: Yes
Location: Mesa, AZ

Re: Error 327 on Rapid (Z Axis Move)

Post by martyscncgarage »

Chaz wrote: Mon Sep 16, 2019 2:38 pm Ok, tested again.

VFD disconnected, no problems.

VFD connected, not running, same issue.

The VFD is power from the same powersource in a cabinet adjacent to where the Acorn controller is. The only wiring going to it from Acorn is an unshielded 3 core cable, using 2 cores to switch on the VFD to run the coolant pump.

From the VFD it goes to the motor via a route nowhere near the Acorn setup.

What's interesting is that it shows:-

9031 DRIVE FAULT!
327 Fault

Yet there is no fault wiring going to the HSS86 drives, so how / why does Acorn think there is a drive fault?

New report attached.
Chaz
Open your Report, then go down and file the file URF.ZIP. Open it and look at the MSG_LOG. TXT
You will see a bunch of this:
(1) 09-14-2019 15:12:37 Saved report to C:\Users\User\Documents\report_C8FD19C4742C-0309180722_2019-09-14_15-12-31.zip
(1) 09-14-2019 15:12:46 204 Exiting CNC...Normal Exit (66)
(1) 09-16-2019 19:00:43 199 CNC Started
(4) 09-16-2019 19:00:48 944 MPU requested resend # 20
(4) 09-16-2019 19:00:48 946 PC resending # 911
(1) 09-16-2019 19:00:51 CNC12 Lathe v4.18
(4) 09-16-2019 19:00:54 9033 Reset Initiated, Press Reset to Clear
(4) 09-16-2019 19:01:05 4032 Reset Cleared
(4) 09-16-2019 19:01:10 944 MPU requested resend # 21
(4) 09-16-2019 19:01:10 946 PC resending # 913
(4) 09-16-2019 19:01:10 944 MPU requested resend # 22
(4) 09-16-2019 19:01:10 946 PC resending # 915
(4) 09-16-2019 19:01:10 944 MPU requested resend # 23
(4) 09-16-2019 19:01:10 946 PC resending # 917
(4) 09-16-2019 19:01:10 946 PC resending # 918
(4) 09-16-2019 19:01:21 9033 Reset Initiated, Press Reset to Clear
(4) 09-16-2019 19:01:21 944 MPU requested resend # 24
(4) 09-16-2019 19:01:21 946 PC resending # 929
(4) 09-16-2019 19:01:22 4032 Reset Cleared
(4) 09-16-2019 19:01:28 944 MPU requested resend # 25
(4) 09-16-2019 19:01:28 946 PC resending # 932
(4) 09-16-2019 19:03:00 944 MPU requested resend # 26
(4) 09-16-2019 19:03:00 946 PC resending # 938
(4) 09-16-2019 19:03:41 944 MPU requested resend # 27
(4) 09-16-2019 19:03:41 946 PC resending # 943
(4) 09-16-2019 19:03:58 944 MPU requested resend # 28
(4) 09-16-2019 19:03:58 946 PC resending # 946
(4) 09-16-2019 19:04:00 944 MPU requested resend # 29
(4) 09-16-2019 19:04:00 946 PC resending # 948
(4) 09-16-2019 19:04:03 944 MPU requested resend # 30
(4) 09-16-2019 19:04:03 946 PC resending # 951
(4) 09-16-2019 19:06:32 944 MPU requested resend # 31
(4) 09-16-2019 19:06:32 946 PC resending # 953
(4) 09-16-2019 19:06:58 944 MPU requested resend # 32
(4) 09-16-2019 19:06:58 946 PC resending # 956
(4) 09-16-2019 19:07:00 944 MPU requested resend # 33
(4) 09-16-2019 19:07:00 946 PC resending # 958
(4) 09-16-2019 19:07:01 944 MPU requested resend # 34
(4) 09-16-2019 19:07:01 946 PC resending # 960
(1) 09-16-2019 19:07:30 204 Exiting CNC...Normal Exit (66)
(1) 09-16-2019 19:14:19 199 CNC Started
(1) 09-16-2019 19:14:26 CNC12 Lathe v4.18
(4) 09-16-2019 19:14:30 9033 Reset Initiated, Press Reset to Clear
(4) 09-16-2019 19:14:32 4032 Reset Cleared
(4) 09-16-2019 19:15:36 9033 Reset Initiated, Press Reset to Clear
(4) 09-16-2019 19:15:37 4032 Reset Cleared
(4) 09-16-2019 19:17:54 9031 DRIVE FAULT!
(1) 09-16-2019 19:19:04 Creating report...


The MPU REquest resend is bad ethernet packet data. Likely from NOISE.
Open your diagnostic screen (Alt+i) look at your Drive Fault input, what state is it?

I think you have a nasty VFD...

What is "3 core cable"?

I would use the digital inputs on the VFD to turn your pump on and off, not power up and down the VFD if that's what you are doing....


Marty
Reminder, for support please follow this post: viewtopic.php?f=20&t=383
We can't "SEE" what you see...
Mesa, AZ


Chaz
Posts: 767
Joined: Thu Feb 08, 2018 7:57 am
Acorn CNC Controller: No
Allin1DC CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC11: No
CPU10 or CPU7: No

Re: Error 327 on Rapid (Z Axis Move)

Post by Chaz »

martyscncgarage wrote: Mon Sep 16, 2019 2:55 pm
Chaz wrote: Mon Sep 16, 2019 2:38 pm Ok, tested again.

VFD disconnected, no problems.

VFD connected, not running, same issue.

The VFD is power from the same powersource in a cabinet adjacent to where the Acorn controller is. The only wiring going to it from Acorn is an unshielded 3 core cable, using 2 cores to switch on the VFD to run the coolant pump.

From the VFD it goes to the motor via a route nowhere near the Acorn setup.

What's interesting is that it shows:-

9031 DRIVE FAULT!
327 Fault

Yet there is no fault wiring going to the HSS86 drives, so how / why does Acorn think there is a drive fault?

New report attached.
Chaz
Open your Report, then go down and file the file URF.ZIP. Open it and look at the MSG_LOG. TXT
You will see a bunch of this:
(1) 09-14-2019 15:12:37 Saved report to C:\Users\User\Documents\report_C8FD19C4742C-0309180722_2019-09-14_15-12-31.zip
(1) 09-14-2019 15:12:46 204 Exiting CNC...Normal Exit (66)
(1) 09-16-2019 19:00:43 199 CNC Started
(4) 09-16-2019 19:00:48 944 MPU requested resend # 20
(4) 09-16-2019 19:00:48 946 PC resending # 911
(1) 09-16-2019 19:00:51 CNC12 Lathe v4.18
(4) 09-16-2019 19:00:54 9033 Reset Initiated, Press Reset to Clear
(4) 09-16-2019 19:01:05 4032 Reset Cleared
(4) 09-16-2019 19:01:10 944 MPU requested resend # 21
(4) 09-16-2019 19:01:10 946 PC resending # 913
(4) 09-16-2019 19:01:10 944 MPU requested resend # 22
(4) 09-16-2019 19:01:10 946 PC resending # 915
(4) 09-16-2019 19:01:10 944 MPU requested resend # 23
(4) 09-16-2019 19:01:10 946 PC resending # 917
(4) 09-16-2019 19:01:10 946 PC resending # 918
(4) 09-16-2019 19:01:21 9033 Reset Initiated, Press Reset to Clear
(4) 09-16-2019 19:01:21 944 MPU requested resend # 24
(4) 09-16-2019 19:01:21 946 PC resending # 929
(4) 09-16-2019 19:01:22 4032 Reset Cleared
(4) 09-16-2019 19:01:28 944 MPU requested resend # 25
(4) 09-16-2019 19:01:28 946 PC resending # 932
(4) 09-16-2019 19:03:00 944 MPU requested resend # 26
(4) 09-16-2019 19:03:00 946 PC resending # 938
(4) 09-16-2019 19:03:41 944 MPU requested resend # 27
(4) 09-16-2019 19:03:41 946 PC resending # 943
(4) 09-16-2019 19:03:58 944 MPU requested resend # 28
(4) 09-16-2019 19:03:58 946 PC resending # 946
(4) 09-16-2019 19:04:00 944 MPU requested resend # 29
(4) 09-16-2019 19:04:00 946 PC resending # 948
(4) 09-16-2019 19:04:03 944 MPU requested resend # 30
(4) 09-16-2019 19:04:03 946 PC resending # 951
(4) 09-16-2019 19:06:32 944 MPU requested resend # 31
(4) 09-16-2019 19:06:32 946 PC resending # 953
(4) 09-16-2019 19:06:58 944 MPU requested resend # 32
(4) 09-16-2019 19:06:58 946 PC resending # 956
(4) 09-16-2019 19:07:00 944 MPU requested resend # 33
(4) 09-16-2019 19:07:00 946 PC resending # 958
(4) 09-16-2019 19:07:01 944 MPU requested resend # 34
(4) 09-16-2019 19:07:01 946 PC resending # 960
(1) 09-16-2019 19:07:30 204 Exiting CNC...Normal Exit (66)
(1) 09-16-2019 19:14:19 199 CNC Started
(1) 09-16-2019 19:14:26 CNC12 Lathe v4.18
(4) 09-16-2019 19:14:30 9033 Reset Initiated, Press Reset to Clear
(4) 09-16-2019 19:14:32 4032 Reset Cleared
(4) 09-16-2019 19:15:36 9033 Reset Initiated, Press Reset to Clear
(4) 09-16-2019 19:15:37 4032 Reset Cleared
(4) 09-16-2019 19:17:54 9031 DRIVE FAULT!
(1) 09-16-2019 19:19:04 Creating report...


The MPU REquest resend is bad ethernet packet data. Likely from NOISE.
Open your diagnostic screen (Alt+i) look at your Drive Fault input, what state is it?

I think you have a nasty VFD...

Marty
Thanks, saw those messages in the logs too. I dont believe I have anything connected to the input for drive fault. Need to check, the machine was retrofitted by another forum member here. Ive got some screenshots (Ive closed up the garage for now), so wont head back in tonight.


Post Reply