Post by Chas »

Hi, hopefully just a simple fix but i have a slight problem . I am just finishing off wiring up acorn to replace Mach3 which i used for a number of years but i cannot get the no fault out relay connected to the main contactor to change state when the E stop button is pressed. I have it wired as shown in the acorn schematic for the no fault out but the led on the relay board remains red when the E stop is pressed yet the led on the diagnostics screen for that output does change colour when the E stop is pressed as it should.According to the info the relay assigned to "no fault out" should change state when the E stop is pressed but it doesn't. Acorn sees the E stop btw and acknowledges it on screen so i think that bit is fine. Probably something simple i've forgotten to do but i can't see it right now.
Thanks
Charlie


centroid467
Posts: 821
Joined: Thu Apr 14, 2022 2:46 pm
Acorn CNC Controller: No
Allin1DC CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC12: No
CNC11: No
CPU10 or CPU7: No

Re: No fault out problem with the relay board

Post by centroid467 »

Could you please post a report and some pictures of your wiring?


CentroidFrog
Tech Support
Posts: 128
Joined: Wed Jan 29, 2025 9:39 am
Acorn CNC Controller: No
Plasma CNC Controller: No
AcornSix CNC Controller: No
Allin1DC CNC Controller: No
Hickory CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No

Re: No fault out problem with the relay board

Post by CentroidFrog »

Want to post your own question?
Check this out first: http://centroidcncforum.com/viewtopic.php?f=60&t=1043
Acorn CNC tech tips: viewforum.php?f=63


ShawnM
Community Expert
Posts: 3026
Joined: Fri May 24, 2019 8:34 am
Acorn CNC Controller: Yes
Allin1DC CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: 7804734C6498-0401191832
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No
Location: Clearwater, FL

Re: No fault out problem with the relay board

Post by ShawnM »

Chas wrote: Sun Mar 16, 2025 6:58 am Hi, hopefully just a simple fix but i have a slight problem . I am just finishing off wiring up acorn to replace Mach3 which i used for a number of years but i cannot get the no fault out relay connected to the main contactor to change state when the E stop button is pressed. I have it wired as shown in the acorn schematic for the no fault out but the led on the relay board remains red when the E stop is pressed yet the led on the diagnostics screen for that output does change colour when the E stop is pressed as it should.According to the info the relay assigned to "no fault out" should change state when the E stop is pressed but it doesn't. Acorn sees the E stop btw and acknowledges it on screen so i think that bit is fine. Probably something simple i've forgotten to do but i can't see it right now.
Thanks
Charlie
When the Acorn is working as it should (no errors or faults) the LED on the relay board relay for "no fault out" output should be green and latched. If you press e-stop for whatever reason EVERYTHING stops and the LED for the relay will go red.

Please give us a schematic diagram number so we can see which schematic you are referring to. There are too many to guess.

And post a current report.


Chas
Posts: 57
Joined: Fri Jan 25, 2019 2:25 pm
Acorn CNC Controller: Yes
Allin1DC CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No

Re: No fault out problem with the relay board

Post by Chas »

Hi guys, problem solved. I have a Rev 2 Acorn board which has 2 onboard relay outputs. I was assuming using the wizard that all numbered relays would be on the external relay board but that isn't so. Number one and two correspond to the relays on the Acorn board itself. Relays 3-8 correspond to the relays on the relay board but how you access relays 1 & 2 on the relay board through the wizard i'm still not sure as there are only 8 outputs shown on the wizard. Once i checked all the relays and realised my mistake then rewired the contactor connections to one of the relays on the Acorn board itself everything now works as it should. Be interested to know if relays 1 & 2 on the relay board can be used when using an early acorn board.
Many thanks
Charlie


cnckeith
Site Admin
Posts: 8942
Joined: Wed Mar 03, 2010 4:23 pm
Acorn CNC Controller: Yes
Allin1DC CNC Controller: Yes
Oak CNC controller: Yes
CNC Control System Serial Number: none
DC3IOB: Yes
CNC11: Yes
CPU10 or CPU7: Yes
Contact:

Re: No fault out problem with the relay board

Post by cnckeith »

thanks for reporting back.
Need support? READ THIS POST first. http://centroidcncforum.com/viewtopic.php?f=60&t=1043
All Acorn Documentation is located here: viewtopic.php?f=60&t=3397
Answers to common questions: viewforum.php?f=63
and here viewforum.php?f=61
Gear we use but don't sell. https://www.centroidcnc.com/centroid_di ... _gear.html


Post Reply