OK. Had to replace a TECO N3 VFD. Went with the Automation Direct GS3 Sensorless Vector Drive. Using 0-10VDC analog input from Centroid Control
Dammed if I can figure out how to setup the min/max speed in the drive. It doesn't use minimum and maximum frequency.
Here is a link to the manual:
https://cdn.automationdirect.com/static ... m/gs3m.pdf
My minimum speed is 635rpm and maximum speed is 3800rpm on a knee mill. The motor itself is 3hp 1720RPM@60hz.
Anyone that has used and configured the speed in the GS series drives, I would appreciate some pointers.
I know these parameters come into play, but they are based on RPM instead of frequency. VFD is wired correctly and accepting the analog inputs just fine from the Centroid Control
P0.04
P6.15
P6.16
Thanks in advance for any pointers.
Marty
Setting Frequency/Speed in Automation Direct GS3 VFD
Moderator: cnckeith
-
- Community Expert
- Posts: 9958
- Joined: Tue Mar 28, 2017 12:01 pm
- Acorn CNC Controller: Yes
- Plasma CNC Controller: Yes
- AcornSix CNC Controller: Yes
- Allin1DC CNC Controller: Yes
- Hickory CNC Controller: Yes
- Oak CNC controller: No
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
- Location: Mesa, AZ
Setting Frequency/Speed in Automation Direct GS3 VFD
Reminder, for support please follow this post: viewtopic.php?f=20&t=383
We can't "SEE" what you see...
Mesa, AZ
We can't "SEE" what you see...
Mesa, AZ
(Note: Liking will "up vote" a post in the search results helping others find good information faster)
-
- Posts: 2358
- Joined: Sat Nov 18, 2017 2:32 pm
- Acorn CNC Controller: Yes
- Plasma CNC Controller: No
- AcornSix CNC Controller: Yes
- Allin1DC CNC Controller: No
- Hickory CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: Acorn 238
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
- Location: Bergland, MI, USA
- Contact:
Re: Setting Frequency/Speed in Automation Direct GS3 VFD
Marty...
Check these:
P2.06
P3.16
P6.15
Call if you need more info
Check these:
P2.06
P3.16
P6.15
Call if you need more info
GCnC Control
CNC Control & Retrofits
CNC Depot Modular ATC kits
https://www.youtube.com/user/Islaww1/videos
CNC Control & Retrofits
CNC Depot Modular ATC kits
https://www.youtube.com/user/Islaww1/videos
(Note: Liking will "up vote" a post in the search results helping others find good information faster)
-
- Community Expert
- Posts: 9958
- Joined: Tue Mar 28, 2017 12:01 pm
- Acorn CNC Controller: Yes
- Plasma CNC Controller: Yes
- AcornSix CNC Controller: Yes
- Allin1DC CNC Controller: Yes
- Hickory CNC Controller: Yes
- Oak CNC controller: No
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
- Location: Mesa, AZ
Re: Setting Frequency/Speed in Automation Direct GS3 VFD
Thanks Gary. As these ar pretty popular drives, I'd hoped we could share the programming theory here so others could benefit as well.Gary Campbell wrote: ↑Thu Apr 19, 2018 8:11 pm Marty...
Check these:
P2.06
P3.16
P6.15
Call if you need more info
This is on a Shuozuka CNC knee mill I refitted with an Acorn. The head has a Reeves drive system. I'm trying to park the drive at 1:1 and control motor speed via Acorn.
TECO N3 VFD analog connection took out 2 Acorn analog outputs and tripped faults in the Gecko G203V stepper drives. Replaced with GS3, everything works as it should. No more stepper drive faults and no more killing Acorn analog outputs. I'm done with TECO Westinghouse VFDs.
Since the machine is not here, I will have to gather what I have learned and go back.
I want to start using the AD GS drives but need to under stand how to program the low and top end speed. Spoke with their support staff and all I got was "do you really want to do that?" He wasn't very helpful at all.
Marty
Reminder, for support please follow this post: viewtopic.php?f=20&t=383
We can't "SEE" what you see...
Mesa, AZ
We can't "SEE" what you see...
Mesa, AZ
(Note: Liking will "up vote" a post in the search results helping others find good information faster)
-
- Community Expert
- Posts: 4602
- Joined: Wed Mar 24, 2010 5:48 pm
- Acorn CNC Controller: No
- Plasma CNC Controller: No
- AcornSix CNC Controller: No
- Allin1DC CNC Controller: No
- Hickory CNC Controller: No
- Oak CNC controller: No
Re: Setting Frequency/Speed in Automation Direct GS3 VFD
In these drives (GS2 also), you imply the maximum frequency when you set the P0.xx series motor parameters.
P0.02 = Motor base frequency (usually 60Hz)
P0.03 = Motor base RPM (from nameplate, typically ca. 1760 for a 4-pole motor)
P0.04 = Motor max RPM. This is your desired maximum speed.
The drive will scale the frequency from P0.02, in proportion to P0.04/P0.03, to come up with the frequency that will give you the max speed you ask for.
P0.02 = Motor base frequency (usually 60Hz)
P0.03 = Motor base RPM (from nameplate, typically ca. 1760 for a 4-pole motor)
P0.04 = Motor max RPM. This is your desired maximum speed.
The drive will scale the frequency from P0.02, in proportion to P0.04/P0.03, to come up with the frequency that will give you the max speed you ask for.
(Note: Liking will "up vote" a post in the search results helping others find good information faster)
-
- Community Expert
- Posts: 9958
- Joined: Tue Mar 28, 2017 12:01 pm
- Acorn CNC Controller: Yes
- Plasma CNC Controller: Yes
- AcornSix CNC Controller: Yes
- Allin1DC CNC Controller: Yes
- Hickory CNC Controller: Yes
- Oak CNC controller: No
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
- Location: Mesa, AZ
Re: Setting Frequency/Speed in Automation Direct GS3 VFD
Thanks Marc.
I found the Tech bulletin http://www.centroidcnc.com/dealersuppor ... ds/203.pdf
But I am not clear on how to set the minimum RPM.
The mill has a VS head I will set at 1:1. But the mill has a minimum RPM of 635.
Marty
I found the Tech bulletin http://www.centroidcnc.com/dealersuppor ... ds/203.pdf
But I am not clear on how to set the minimum RPM.
The mill has a VS head I will set at 1:1. But the mill has a minimum RPM of 635.
Marty
Reminder, for support please follow this post: viewtopic.php?f=20&t=383
We can't "SEE" what you see...
Mesa, AZ
We can't "SEE" what you see...
Mesa, AZ
(Note: Liking will "up vote" a post in the search results helping others find good information faster)
-
- Community Expert
- Posts: 3544
- Joined: Tue Mar 22, 2016 10:03 am
- Acorn CNC Controller: Yes
- Plasma CNC Controller: No
- AcornSix CNC Controller: No
- Allin1DC CNC Controller: Yes
- Hickory CNC Controller: No
- Oak CNC controller: Yes
- CNC Control System Serial Number: 100505
100327
102696
103432
7804732B977B-0624192192 - DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
- Location: Boston, MA
- Contact:
Re: Setting Frequency/Speed in Automation Direct GS3 VFD
Marty,
Once you get the max scaling right on the VFD, set max and min RPM on the Centroid config control screen. That should take care of the low end RPM.
Once you get the max scaling right on the VFD, set max and min RPM on the Centroid config control screen. That should take care of the low end RPM.
Cheers,
Tom
Confidence is the feeling you have before you fully understand the situation.
I have CDO. It's like OCD, but the letters are where they should be.
Tom
Confidence is the feeling you have before you fully understand the situation.
I have CDO. It's like OCD, but the letters are where they should be.
(Note: Liking will "up vote" a post in the search results helping others find good information faster)
-
- Community Expert
- Posts: 9958
- Joined: Tue Mar 28, 2017 12:01 pm
- Acorn CNC Controller: Yes
- Plasma CNC Controller: Yes
- AcornSix CNC Controller: Yes
- Allin1DC CNC Controller: Yes
- Hickory CNC Controller: Yes
- Oak CNC controller: No
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
- Location: Mesa, AZ
Re: Setting Frequency/Speed in Automation Direct GS3 VFD
Thanks Tom, I got it close. The variable speed reeves drive type mechanism on the mill head complicated things a bit. There was no easy way to get to the motor shaft to read its RPM. The name plate on the motor was also virtually unreadable so that didn't help matters much.