Separate Input Power Supply

Post by FKreider »

I looked in the Acorn manual and also did some searching here on the board but haven't seen this question addressed.

Is it OK if I provide +24VDC from a separate power supply to the input H4 terminal? (the common would also be separate).

I have Acorn powered by the included Meanwell power supply and plan on only letting it provide main power to Acorn.

The reason being is that this is a retrofit application where a 24VDC power supply along with the limit switches, homing switches, etc. are already wired to DIN rail terminal strips and are already setup to "sink" the input to 0VDC COM. If I'm able to leave these terminal strips wired as they are it will save a lot of time vs. rewiring everything.


Gary Campbell
Posts: 2353
Joined: Sat Nov 18, 2017 2:32 pm
Acorn CNC Controller: Yes
Plasma CNC Controller: No
AcornSix CNC Controller: Yes
Allin1DC CNC Controller: No
Hickory CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: Acorn 238
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No
Location: Bergland, MI, USA
Contact:

Re: Separate Input Power Supply

Post by Gary Campbell »

Yes, it's not a bad idea to use multiple power supplies, but you must connect the commons together.
GCnC Control
CNC Control & Retrofits
CNC Depot Modular ATC kits
https://www.youtube.com/user/Islaww1/videos


FKreider
Posts: 33
Joined: Wed Mar 27, 2019 10:53 pm
Acorn CNC Controller: Yes
Allin1DC CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No

Re: Separate Input Power Supply

Post by FKreider »

oh really? The commons from the two different 24V power supplies should be tied together?

I figured that was not a good thing and could cause ground loops.


Coolidge62
Posts: 82
Joined: Mon Jan 20, 2025 10:01 pm
Acorn CNC Controller: No
Plasma CNC Controller: No
AcornSix CNC Controller: No
Allin1DC CNC Controller: No
Hickory CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC12: No
CNC11: No
CPU10 or CPU7: No

Re: Separate Input Power Supply

Post by Coolidge62 »

Think of grounds like a large river, with creeks and streams flowing into the main channel, then flowing downstream until it empties into the sea at your main panel ground. Ideally the big amp stuff is downstream from the small stuff.