CNC 10 Mill v2.68 M400 (Non-Windows)
Re: commanded spindle speed, Oak CNC12
That is actually a bit puzzling.
First, this is not a CNC10 Mill system with v2.68 (Non-Windows). It is a CNC12 Mill system with v4.20 (Windows).
Second, he does not have a spindle encoder configured (P78 = 0), so the speed displayed in the status window should be the commanded speed reported by the PLC program, via SV_PLC_SPINDLE_SPEED.
Generally, that would be the commanded speed (CNC 'S' code) provided the override is at 100%, the S code was not less than minimum, and the S code was not more than maximum. He has a minimum speed of 0, a maximum of 2800. In high gear, any speed from 0 to 2800 should be reported back running as commanded. He does have a low gear configured, so if INP13 is closed, then the maximum possible speed would be 350. But even in low gear, then, any speed from 0 to 350 should be reported running as commanded.
ruirosa: Press Alt-i for the PLC Diagnostic screen. Press F12 to page right until you reach the page that has "FW" variables at the bottom (the numbers, displayed below the four rows of dots). Watch the value next to FW06 on that display while you try "M3 S100", "M3 S200", "M3 S300" and so on.
What values do you see for FW06? Are they the commanded speed (S code)? Or are they the 80% speed that you see in the status window?
Re: CNC 10 Mill v2.68 M400 (Non-Windows)
Hello
I inserted the comand M3s200.
And took some screen pictures.
The FW6 value shown is the correct. 200 (pic3).
The spindle max. speed is set to 3000 rpm (pic2) i do not understand how the system is assuming max spindle speed 2800.
Maybe the all rpm diference is due that fact.
Where is possible to change the max. spindle speed to to 3000 rpm?
Regards
Rui
Regards
Rui
The report you uploaded had the max spindle speed set to 2800:
The report also states you do not have a spindle encoder attached.
That is why it is important to create a new report whenever you make changes. We do not know what changes you have made and can only go on the information based in the report.
Configuration file
CNC12 Virtual v. 4.200 setup file for MPU11 serial number 0008DC111213-08032009
DRO display units: Millimeters
Machine units: Millimeters
Max spindle (high range): 2800.0
Min spindle (high range): 0.0
Machine home at pwrup: Ref Mark-HS
PLC type: Standard
Jog Panel type Virtual
Jog panel required: No
Remote Drive & Directory:
Fourth axis level offset 0
Fifth axis level offset 0
P35 = 0.00000 - Spindle Axis 1-8, 0 = disabled
Hello
Herewith I am sending a new report made some moments ago.
Regards
Rui
Regards
Rui
- report_0008DC111213-0803200997_2023-02-23_13-20-44.zip
- (585.53 KiB) Downloaded 4 times
You have an encoder connected to input 5 with a counts per rev of 8000. Unfortunately, the encoder data sheet you linked to earlier does not list 8000 cpr as a valid choice. I suspect your encoder is actually 8192 cpr.
Since the encoder we listed had a delivery time of 6 monts, we decide to use an omron diferential with 2000 lines
that make 8000 cpr.
I also measured the spindle rpm with a laser rotation mesure psitol and in fact there is a 20% rpm diference betwen the mdi comand a nd the real rpm.
Regards
Rui
that make 8000 cpr.
Regards
Rui
I don't know of any Omron big bore encoders, so I assume your encoder is now belted to the spindle. If it is belted at 1:1 to the spindle, then you need to adjust your VFD so it spins at the correct speed using the spindle calibration procedure previously posted.
Yes the encoder is belted to the spindle axis 1:1.
I already made the calibration procedur, measuring the analog output voltages at the spindle outputs.
I will repeat the calibration process and then give a feedback.
Regards
Rui
Regards
Rui
If the actual speed you measure with a tachometer is the same as the speed in the status window (which is now based on the encoder, in your newer report) then the encoder is set up correctly.
A command of 200 RPM out of a presumed maximum of 3000 would be 1/15 of maximum speed. If this results in 163 RPM, then spindle drive's maximum speed is 15 x 163 = 2445 RPM.
You should change the "Max spindle (high range)" speed on the Control Configuration screen to 2445.
If you want to make it go faster, you need to reprogram your spindle drive for a higher maximum speed first, then adjust the number on the Control Configuration screen to match.