Cant turn on Orientation on Delta C2000

All things related to Centroid Oak, Allin1DC, MPU11 and Legacy products

Moderator: cnckeith

martyscncgarage
Community Expert
Posts: 9953
Joined: Tue Mar 28, 2017 12:01 pm
Acorn CNC Controller: Yes
Allin1DC CNC Controller: Yes
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC12: Yes
CNC11: Yes
CPU10 or CPU7: Yes
Location: Mesa, AZ

Re: Cant turn on Orientation on Delta C2000

Post by martyscncgarage »

Titleiiarms wrote: Sat Nov 06, 2021 1:42 pm I think what Marty means is you have to provide the VFD Zero speed output signal back to the OAK board for the tool changer to work. Guess they dont want tools spinning around and getting unclamped :)
Correct. Oak needs to see that the ORIENT is complete before completing the tool change cycle.
When the spindle orient completes the ZERO Speed goes active.

Marty
Reminder, for support please follow this post: viewtopic.php?f=20&t=383
We can't "SEE" what you see...
Mesa, AZ


ashesman
Posts: 431
Joined: Thu Dec 03, 2020 4:54 am
Acorn CNC Controller: No
Allin1DC CNC Controller: No
Oak CNC controller: Yes
CNC Control System Serial Number: none
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No

Re: Cant turn on Orientation on Delta C2000

Post by ashesman »

Yeah, I already have a ZS wire from the old VFD. I will hook it up. My tool change is entirely custom as is not a standard tool change system so I will wait for oriented signal not ZS signal.


martyscncgarage
Community Expert
Posts: 9953
Joined: Tue Mar 28, 2017 12:01 pm
Acorn CNC Controller: Yes
Allin1DC CNC Controller: Yes
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC12: Yes
CNC11: Yes
CPU10 or CPU7: Yes
Location: Mesa, AZ

Re: Cant turn on Orientation on Delta C2000

Post by martyscncgarage »

ashesman wrote: Sat Nov 06, 2021 2:03 pm Yeah, I already have a ZS wire from the old VFD. I will hook it up. My tool change is entirely custom as is not a standard tool change system so I will wait for oriented signal not ZS signal.
So the C2000 has an oriented signal output?
That would accomplish the same thing.

Did you write the tool change PLC or did you hire it out?
Marc is one of the best.

Marty
Reminder, for support please follow this post: viewtopic.php?f=20&t=383
We can't "SEE" what you see...
Mesa, AZ


ashesman
Posts: 431
Joined: Thu Dec 03, 2020 4:54 am
Acorn CNC Controller: No
Allin1DC CNC Controller: No
Oak CNC controller: Yes
CNC Control System Serial Number: none
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No

Re: Cant turn on Orientation on Delta C2000

Post by ashesman »

The C2000 has a configurable orient complete output. Can set the tolerance and time. It also has zero speed but I dont know when zero speed would ever add any value.

I write my own PLC code. I write software for a job so it's not too much of a challenge for me.


ashesman
Posts: 431
Joined: Thu Dec 03, 2020 4:54 am
Acorn CNC Controller: No
Allin1DC CNC Controller: No
Oak CNC controller: Yes
CNC Control System Serial Number: none
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No

Re: Cant turn on Orientation on Delta C2000

Post by ashesman »

Drive is all sorted and tuned now. See the following video. 6000 RPM max, 0.35s acceleration/deceleration times. Very stiff orient positioning.



I will try remember to put up a parameter file from the VFD in case anyone else tries to get a servo motor running nicely on one.


ashesman
Posts: 431
Joined: Thu Dec 03, 2020 4:54 am
Acorn CNC Controller: No
Allin1DC CNC Controller: No
Oak CNC controller: Yes
CNC Control System Serial Number: none
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No

Re: Cant turn on Orientation on Delta C2000

Post by ashesman »

Delta C2000 parameter file attached for setup of the VFD for an AC servo motor spindle (Panasonic 1.5kW with 2500 pulse incremental encoder and commutation UVW signals). Requires UVW encoder board. Setup suits the default Oak configuration. Uses -10 to +10V for speed and direction. Also has emergency stop and external fault set up. External fault is used for brake resistor overheat, or disable if not required. A brake resistor is required to stop the spindle fast from high speed. Increase deceleration time if not using a brake resistor. Emergency stop should be connected to Estop. In my case it is wired in parallel to the Oaks EStop DI, but I added an optocoupler isolator (a relay would do) to separate the power domains. Orientation is configured and tuned for fast response. If I remember I will also upload a wiring diagram so match the configuration file.
Attachments
Delta C2000 Spindle Drive Parameters.CSV
(149.25 KiB) Downloaded 89 times


martyscncgarage
Community Expert
Posts: 9953
Joined: Tue Mar 28, 2017 12:01 pm
Acorn CNC Controller: Yes
Allin1DC CNC Controller: Yes
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC12: Yes
CNC11: Yes
CPU10 or CPU7: Yes
Location: Mesa, AZ

Re: Cant turn on Orientation on Delta C2000

Post by martyscncgarage »

ashesman wrote: Fri Dec 03, 2021 2:54 pm Delta C2000 parameter file attached for setup of the VFD for an AC servo motor spindle (Panasonic 1.5kW with 2500 pulse incremental encoder and commutation UVW signals). Requires UVW encoder board. Setup suits the default Oak configuration. Uses -10 to +10V for speed and direction. Also has emergency stop and external fault set up. External fault is used for brake resistor overheat, or disable if not required. A brake resistor is required to stop the spindle fast from high speed. Increase deceleration time if not using a brake resistor. Emergency stop should be connected to Estop. In my case it is wired in parallel to the Oaks EStop DI, but I added an optocoupler isolator (a relay would do) to separate the power domains. Orientation is configured and tuned for fast response. If I remember I will also upload a wiring diagram so match the configuration file.
Thank you!
A schematic would be helpful.
May help get someone pointed in the right direction in the future.
Centroid recently published this document: https://www.centroidcnc.com/dealersuppo ... ds/316.pdf
Marty
Reminder, for support please follow this post: viewtopic.php?f=20&t=383
We can't "SEE" what you see...
Mesa, AZ


ashesman
Posts: 431
Joined: Thu Dec 03, 2020 4:54 am
Acorn CNC Controller: No
Allin1DC CNC Controller: No
Oak CNC controller: Yes
CNC Control System Serial Number: none
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No

Re: Cant turn on Orientation on Delta C2000

Post by ashesman »

Wiring diagram attached. Excuse my hand drawing...
20211205_160059[1].jpg


martyscncgarage
Community Expert
Posts: 9953
Joined: Tue Mar 28, 2017 12:01 pm
Acorn CNC Controller: Yes
Allin1DC CNC Controller: Yes
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC12: Yes
CNC11: Yes
CPU10 or CPU7: Yes
Location: Mesa, AZ

Re: Cant turn on Orientation on Delta C2000

Post by martyscncgarage »

PDF
Attachments
C2000 Connection.pdf
(796.42 KiB) Downloaded 93 times
Reminder, for support please follow this post: viewtopic.php?f=20&t=383
We can't "SEE" what you see...
Mesa, AZ


cncsnw
Community Expert
Posts: 4589
Joined: Wed Mar 24, 2010 5:48 pm

Re: Cant turn on Orientation on Delta C2000

Post by cncsnw »

I probably would not wire the VFD's 24V supply to H2 on the Oak.

Even though that supply to Oak shares the H2 header with the spindle analog output and input, it is not actually related to the spindle interface at all.

The 24VDC supply you connect to H2 is used for the servo drive I/O, on the four axis headers. I usually wire the 24V from PS1 (the RQ-65D underneath the Oak unit) to H2 for axis servo drive sequencing.


Post Reply