Re: Error 327 on Rapid (Z Axis Move)
Open the Wizard to see if an input has been assigned to Drive Fault.
I think the noise is the big issue.
I think the noise is the big issue.
Reminder, for support please follow this post: viewtopic.php?f=20&t=383
We can't "SEE" what you see...
Mesa, AZ
We can't "SEE" what you see...
Mesa, AZ
(Note: Liking will "up vote" a post in the search results helping others find good information faster)
-
- Posts: 759
- Joined: Thu Feb 08, 2018 7:57 am
- Acorn CNC Controller: No
- Allin1DC CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC11: No
- CPU10 or CPU7: No
Re: Error 327 on Rapid (Z Axis Move)
Ok, based on a pic of the setup, I have DriveOK, input 5, NC. I need to see how this is wired in, if at all. I assume it must but but there is no Fault wiring going to the drives, so not sure. Pity I dont have pics of the board wiring on me to check.
(Note: Liking will "up vote" a post in the search results helping others find good information faster)
-
- Community Expert
- Posts: 9953
- Joined: Tue Mar 28, 2017 12:01 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: Yes
- Oak CNC controller: No
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC12: Yes
- CNC11: Yes
- CPU10 or CPU7: Yes
- Location: Mesa, AZ
Re: Error 327 on Rapid (Z Axis Move)
Well, youll have to double check that there is no wire physically connected to Acorn input 5
If not set the input to unused. If it is there, you'll have to check your drives and if there is no fault, then whether they need NO or NC.
If the enables are wired, I have a hunch the noise is might be faulting your drives perhaps?
Reminder, for support please follow this post: viewtopic.php?f=20&t=383
We can't "SEE" what you see...
Mesa, AZ
We can't "SEE" what you see...
Mesa, AZ
(Note: Liking will "up vote" a post in the search results helping others find good information faster)
-
- Posts: 759
- Joined: Thu Feb 08, 2018 7:57 am
- Acorn CNC Controller: No
- Allin1DC CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC11: No
- CPU10 or CPU7: No
Re: Error 327 on Rapid (Z Axis Move)
Possibly. Im tempted to go into the garage to check. I'd guess that if there was no wiring, it simply woulnt work (ie, it would fault out). Specifically if its NC.martyscncgarage wrote: ↑Mon Sep 16, 2019 3:06 pmWell, youll have to double check that there is no wire physically connected to Acorn input 5
If not set the input to unused. If it is there, you'll have to check your drives and if there is no fault, then whether they need NO or NC.
If the enables are wired, I have a hunch the noise is might be faulting your drives perhaps?
(Note: Liking will "up vote" a post in the search results helping others find good information faster)
-
- Posts: 759
- Joined: Thu Feb 08, 2018 7:57 am
- Acorn CNC Controller: No
- Allin1DC CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC11: No
- CPU10 or CPU7: No
Re: Error 327 on Rapid (Z Axis Move)
Ok. Input 5 wire goes to the Spindle VFD, so its not measuring anything from the X or Z drive but the VFD. The coolant VFD is right next to it. I suspect the noise is on that wire. Ironically the spindle setup seems happy but didnt think to look at the VFD for it (assumed the wiring was to the Axis drives, not the spindle VFD).
Ill test tomorrow but I assume disconnecting the wire will work and/or shielding that wire will help.
Ill test tomorrow but I assume disconnecting the wire will work and/or shielding that wire will help.
(Note: Liking will "up vote" a post in the search results helping others find good information faster)
-
- Community Expert
- Posts: 9953
- Joined: Tue Mar 28, 2017 12:01 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: Yes
- Oak CNC controller: No
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC12: Yes
- CNC11: Yes
- CPU10 or CPU7: Yes
- Location: Mesa, AZ
Re: Error 327 on Rapid (Z Axis Move)
Too bad you didn't look at the spindle VFD to see if it was showing a fault.Chaz wrote: ↑Mon Sep 16, 2019 3:44 pm Ok. Input 5 wire goes to the Spindle VFD, so its not measuring anything from the X or Z drive but the VFD. The coolant VFD is right next to it. I suspect the noise is on that wire. Ironically the spindle setup seems happy but didnt think to look at the VFD for it (assumed the wiring was to the Axis drives, not the spindle VFD).
Ill test tomorrow but I assume disconnecting the wire will work and/or shielding that wire will help.
Also you might change that input SpindleOk instead of drive fault.
Reminder, for support please follow this post: viewtopic.php?f=20&t=383
We can't "SEE" what you see...
Mesa, AZ
We can't "SEE" what you see...
Mesa, AZ
(Note: Liking will "up vote" a post in the search results helping others find good information faster)
-
- Posts: 759
- Joined: Thu Feb 08, 2018 7:57 am
- Acorn CNC Controller: No
- Allin1DC CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC11: No
- CPU10 or CPU7: No
Re: Error 327 on Rapid (Z Axis Move)
Indeed. Will try that tomorrow. Feeling a bit fluish atm, so not ideal to be out in the garage, getting colder at night.martyscncgarage wrote: ↑Mon Sep 16, 2019 3:48 pmToo bad you didn't look at the spindle VFD to see if it was showing a faultChaz wrote: ↑Mon Sep 16, 2019 3:44 pm Ok. Input 5 wire goes to the Spindle VFD, so its not measuring anything from the X or Z drive but the VFD. The coolant VFD is right next to it. I suspect the noise is on that wire. Ironically the spindle setup seems happy but didnt think to look at the VFD for it (assumed the wiring was to the Axis drives, not the spindle VFD).
Ill test tomorrow but I assume disconnecting the wire will work and/or shielding that wire will help.
(Note: Liking will "up vote" a post in the search results helping others find good information faster)
-
- Posts: 759
- Joined: Thu Feb 08, 2018 7:57 am
- Acorn CNC Controller: No
- Allin1DC CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC11: No
- CPU10 or CPU7: No
Re: Error 327 on Rapid (Z Axis Move)
I believe this is now solved.
Ran it with the VFD cabinet door open, no fault. Odd. Closed the door, fault.
Checked, VFD error was E.oU.d on the HY unit.
I then remembered that I had set the acceleration time for the VFD from 8 seconds to 3, same as the ramp down.
Anyone who runs a HY VFD knows they have no internal braking and the E.oU.d is often due to overvoltage at ramp down. The door was just luck of the draw. Set the ramp to 6 secs both ways, door closed, no error.
Ran it with the VFD cabinet door open, no fault. Odd. Closed the door, fault.
Checked, VFD error was E.oU.d on the HY unit.
I then remembered that I had set the acceleration time for the VFD from 8 seconds to 3, same as the ramp down.
Anyone who runs a HY VFD knows they have no internal braking and the E.oU.d is often due to overvoltage at ramp down. The door was just luck of the draw. Set the ramp to 6 secs both ways, door closed, no error.
(Note: Liking will "up vote" a post in the search results helping others find good information faster)
-
- Community Expert
- Posts: 9953
- Joined: Tue Mar 28, 2017 12:01 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: Yes
- Oak CNC controller: No
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC12: Yes
- CNC11: Yes
- CPU10 or CPU7: Yes
- Location: Mesa, AZ
Re: Error 327 on Rapid (Z Axis Move)
You can specify you want the braking resistor circuit added. Message Huan Yang through Amazon.Chaz wrote: ↑Tue Sep 17, 2019 2:20 pm I believe this is now solved.
Ran it with the VFD cabinet door open, no fault. Odd. Closed the door, fault.
Checked, VFD error was E.oU.d on the HY unit.
I then remembered that I had set the acceleration time for the VFD from 8 seconds to 3, same as the ramp down.
Anyone who runs a HY VFD knows they have no internal braking and the E.oU.d is often due to overvoltage at ramp down. The door was just luck of the draw. Set the ramp to 6 secs both ways, door closed, no error.
When I do use them, I use the GT series, supposedly sensorless vector drive
Reminder, for support please follow this post: viewtopic.php?f=20&t=383
We can't "SEE" what you see...
Mesa, AZ
We can't "SEE" what you see...
Mesa, AZ
(Note: Liking will "up vote" a post in the search results helping others find good information faster)
-
- Posts: 759
- Joined: Thu Feb 08, 2018 7:57 am
- Acorn CNC Controller: No
- Allin1DC CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC11: No
- CPU10 or CPU7: No
Re: Error 327 on Rapid (Z Axis Move)
Yep, the GT series is better. There are also Ecogogo drives which I now use that can do 220V input and 380V output but they are fairly expensive but worth it.martyscncgarage wrote: ↑Tue Sep 17, 2019 2:29 pmYou can specify you want the braking resistor circuit added. Message Huan Yang through Amazon.Chaz wrote: ↑Tue Sep 17, 2019 2:20 pm I believe this is now solved.
Ran it with the VFD cabinet door open, no fault. Odd. Closed the door, fault.
Checked, VFD error was E.oU.d on the HY unit.
I then remembered that I had set the acceleration time for the VFD from 8 seconds to 3, same as the ramp down.
Anyone who runs a HY VFD knows they have no internal braking and the E.oU.d is often due to overvoltage at ramp down. The door was just luck of the draw. Set the ramp to 6 secs both ways, door closed, no error.