How to reset a User-String-Variable #300 - #399?

All things related to the Centroid Acorn CNC Controller

Moderator: cnckeith

swissi
Posts: 603
Joined: Wed Aug 29, 2018 11:15 am
Acorn CNC Controller: Yes
Plasma CNC Controller: No
AcornSix CNC Controller: No
Allin1DC CNC Controller: No
Hickory CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: 985DADEB24D5-0309180716
DC3IOB: No
CNC11: No
CPU10 or CPU7: No

How to reset a User-String-Variable #300 - #399?

Post by swissi »

As the title says, I'm struggling to find a way to reset user-string-variables #300 - #399. These variables keep their value until you quit CNC12, so good practice would be to reset them when you no longer need them.

I tried the usual way #300 = "" to assign a zero-length string but CNC12 does not like that and gives an error "501 Invalid character".

The only way I found is to set the variable to #300 = " " but that assigns a single blank to the variable and messes up my output strings if the variable is not getting filled and should output a zero length string.

Does anybody know how to reset these variables without closing CNC12 and restart it?

-swissi
If you are using any Probing Device, a Rack ATC or want a more efficient Work Flow, check out CHIPS

Contact me at swissi2000@gmail.com


AcornJosh
Posts: 78
Joined: Tue Apr 17, 2018 8:58 am
Acorn CNC Controller: Yes
Plasma CNC Controller: No
AcornSix CNC Controller: No
Allin1DC CNC Controller: No
Hickory CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC11: No
CPU10 or CPU7: No

Re: How to reset a User-String-Variable #300 - #399?

Post by AcornJosh »

I assume your are trying to modify your PLC? Could you please post a report and explain what you are trying to do?


swissi
Posts: 603
Joined: Wed Aug 29, 2018 11:15 am
Acorn CNC Controller: Yes
Plasma CNC Controller: No
AcornSix CNC Controller: No
Allin1DC CNC Controller: No
Hickory CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: 985DADEB24D5-0309180716
DC3IOB: No
CNC11: No
CPU10 or CPU7: No

Re: How to reset a User-String-Variable #300 - #399?

Post by swissi »

Not trying to modify the PLC. Just trying to reset a user-string-variable back to zero-length.

Here's an example:

Code: Select all

;------------------------------------------------------------------------------
; Filename: test.cnc
; VARIABLES USED
; #301 - String Variable 1
; #302 - String Variable 2
; #303 - String Variable 3
#101 = 0  ; How many seconds a message should be displayed. 0 is indefinitely and needs to be confirmed with Cycle Start
;------------------------------------------------------------------------------

#301 = "ABCDE"
#302 = "FGHIJ"
#303 = "KLMNO"

M225 #101 "#)The combined string is: %s%s%s\n\n Press Cycle Start to continue\n" #301 #302 #303

#302 = " "
M225 #101 "#)The combined string is: %s%s%s\n\n Press Cycle Start to continue\n" #301 #302 #303

M99  ; Return to calling job/macro
The first message displays as expected:

Cap1.JPG

and the second message has that space between string 1 and string 3.

Cap2.JPG

So the question is: How to I reset variable #302 back to zero-length so it doesn't print a space between string 1 and string 3?

-swissi
If you are using any Probing Device, a Rack ATC or want a more efficient Work Flow, check out CHIPS

Contact me at swissi2000@gmail.com


DannyB
Posts: 109
Joined: Mon Jan 15, 2018 1:11 am
Acorn CNC Controller: Yes
Plasma CNC Controller: No
AcornSix CNC Controller: No
Allin1DC CNC Controller: No
Hickory CNC Controller: No
Oak CNC controller: Yes
CNC Control System Serial Number: A900712
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No

Re: How to reset a User-String-Variable #300 - #399?

Post by DannyB »

Does setting them to zero (the number) work?


wellington_tregear
Posts: 15
Joined: Sat Feb 09, 2019 10:13 pm
Acorn CNC Controller: Yes
Plasma CNC Controller: No
AcornSix CNC Controller: No
Allin1DC CNC Controller: No
Hickory CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No
Location: Monroe Michigan USA

Re: How to reset a User-String-Variable #300 - #399?

Post by wellington_tregear »

swissi wrote: Thu May 09, 2019 4:51 pm Not trying to modify the PLC. Just trying to reset a user-string-variable back to zero-length.

Here's an example:

Code: Select all

;------------------------------------------------------------------------------
; Filename: test.cnc
; VARIABLES USED
; #301 - String Variable 1
; #302 - String Variable 2
; #303 - String Variable 3
#101 = 0  ; How many seconds a message should be displayed. 0 is indefinitely and needs to be confirmed with Cycle Start
;------------------------------------------------------------------------------

#301 = "ABCDE"
#302 = "FGHIJ"
#303 = "KLMNO"

M225 #101 "#)The combined string is: %s%s%s\n\n Press Cycle Start to continue\n" #301 #302 #303

#302 = " "
M225 #101 "#)The combined string is: %s%s%s\n\n Press Cycle Start to continue\n" #301 #302 #303

M99  ; Return to calling job/macro
The first message displays as expected:


Cap1.JPG


and the second message has that space between string 1 and string 3.


Cap2.JPG


So the question is: How to I reset variable #302 back to zero-length so it doesn't print a space between string 1 and string 3?

-swissi
Just don't call #302. Omit it until you want it. See the second to last line.

Code: Select all

;------------------------------------------------------------------------------
; Filename: test.cnc
; VARIABLES USED
; #301 - String Variable 1
; #302 - String Variable 2
; #303 - String Variable 3
#101 = 0  ; How many seconds a message should be displayed. 0 is indefinitely and needs to be confirmed with Cycle Start
;------------------------------------------------------------------------------

#301 = "ABCDE"
#302 = "FGHIJ"
#303 = "KLMNO"

M225 #101 "#)The combined string is: %s%s%s\n\n Press Cycle Start to continue\n" #301 #302 #303

#302 = " "
M225 #101 "#)The combined string is: %s%s\n\n Press Cycle Start to continue\n" #301 #303

M99  ; Return to calling job/macro


tblough
Community Expert
Posts: 3557
Joined: Tue Mar 22, 2016 10:03 am
Acorn CNC Controller: Yes
Plasma CNC Controller: No
AcornSix CNC Controller: No
Allin1DC CNC Controller: Yes
Hickory CNC Controller: No
Oak CNC controller: Yes
CNC Control System Serial Number: 100505
100327
102696
103432
7804732B977B-0624192192
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No
Location: Boston, MA
Contact:

Re: How to reset a User-String-Variable #300 - #399?

Post by tblough »

My guess is they are using a null (\0) as the end of string character. You could try $0, but the manual specifically states only ASCII codes 65-90 are allowed.

The only other thing I could think of is to reserve one string variable that you never use and assign that to clear your variable.

Code: Select all

;------------------------------------------------------------------------------
; Filename: test.cnc
; VARIABLES USED
; #301 - String Variable 1
; #302 - String Variable 2
; #303 - String Variable 3
; #399 - Reserved String Variable (do not use)
#101 = 0  ; How many seconds a message should be displayed. 0 is indefinitely and needs to be confirmed with Cycle Start
;------------------------------------------------------------------------------

#301 = "ABCDE"
#302 = "FGHIJ"
#303 = "KLMNO"

M225 #101 "#)The combined string is: %s%s%s\n\n Press Cycle Start to continue\n" #301 #302 #303

#302 = #399
M225 #101 "#)The combined string is: %s%s%s\n\n Press Cycle Start to continue\n" #301 #302 #303

M99  ; Return to calling job/macro
Cheers,

Tom
Confidence is the feeling you have before you fully understand the situation.
I have CDO. It's like OCD, but the letters are where they should be.


swissi
Posts: 603
Joined: Wed Aug 29, 2018 11:15 am
Acorn CNC Controller: Yes
Plasma CNC Controller: No
AcornSix CNC Controller: No
Allin1DC CNC Controller: No
Hickory CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: 985DADEB24D5-0309180716
DC3IOB: No
CNC11: No
CPU10 or CPU7: No

Re: How to reset a User-String-Variable #300 - #399?

Post by swissi »

Thanks guys for all the suggestions but none of them seems to work. Even assigning one string variable to another generates a "501 Invalid character" error.

I hope nobody will argue that resetting a variable is an essential and basic function in any programming language. Especially so when the variables are global and will only be reset when the program is exited.

So my guess is that the fact that CNC12 generates an error when trying to set a string variable = "" was an oversight of the programmer who wrote the "check string for legal character" function.

Centroid can you please fix that?

-swissi
If you are using any Probing Device, a Rack ATC or want a more efficient Work Flow, check out CHIPS

Contact me at swissi2000@gmail.com


Muzzer
Posts: 816
Joined: Mon Feb 19, 2018 2:52 pm
Acorn CNC Controller: Yes
Plasma CNC Controller: No
AcornSix CNC Controller: No
Allin1DC CNC Controller: No
Hickory CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: 38D269594F9C-0110180512
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No
Location: UK
Contact:

Re: How to reset a User-String-Variable #300 - #399?

Post by Muzzer »

That's damned annoying. I think this arises partly because macro variables are initially "null" ie they don't even have a zero or any other value when initialised. So if you can't ascribe a null value to them without power cycling, there is no way around it. I guess you would need to be able to set the variables to ASCII value 0 which is the null character.


cnckeith
Site Admin
Posts: 9067
Joined: Wed Mar 03, 2010 4:23 pm
Acorn CNC Controller: Yes
Plasma CNC Controller: No
AcornSix CNC Controller: No
Allin1DC CNC Controller: Yes
Hickory CNC Controller: No
Oak CNC controller: Yes
CNC Control System Serial Number: none
DC3IOB: Yes
CNC11: Yes
CPU10 or CPU7: Yes
Contact:

Re: How to reset a User-String-Variable #300 - #399?

Post by cnckeith »

Muzzer wrote: Sun May 12, 2019 1:22 pm That's damned annoying. I think this arises partly because macro variables are initially "null" ie they don't even have a zero or any other value when initialised. So if you can't ascribe a null value to them without power cycling, there is no way around it. I guess you would need to be able to set the variables to ASCII value 0 which is the null character.
please tell me the goal of project? we are trying to understand your application for this..thanks..
Need support? READ THIS POST first. http://centroidcncforum.com/viewtopic.php?f=60&t=1043
All Acorn Documentation is located here: viewtopic.php?f=60&t=3397
Answers to common questions: viewforum.php?f=63

Gear we use but don't sell. https://www.centroidcnc.com/centroid_di ... _gear.html


tblough
Community Expert
Posts: 3557
Joined: Tue Mar 22, 2016 10:03 am
Acorn CNC Controller: Yes
Plasma CNC Controller: No
AcornSix CNC Controller: No
Allin1DC CNC Controller: Yes
Hickory CNC Controller: No
Oak CNC controller: Yes
CNC Control System Serial Number: 100505
100327
102696
103432
7804732B977B-0624192192
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No
Location: Boston, MA
Contact:

Re: How to reset a User-String-Variable #300 - #399?

Post by tblough »

Keith,

It looks like swissi is just trying to apply good programming practice to his macro files. Since string variables are global and only cleared on restart of the machine, he wants to clear them after he is done using them so that the next macro to use the variable (if it happens before the machine is restarted) does not potentially get bad data. Unlike the numerical variables, there currently is not a way to set a string variable to it's initial "empty" state.
Cheers,

Tom
Confidence is the feeling you have before you fully understand the situation.
I have CDO. It's like OCD, but the letters are where they should be.


Post Reply