DMM DYN4 Spindle Set-up - receiving 1V at power up - voltage drift (solved)

All things related to the Centroid Acorn CNC Controller

Moderator: cnckeith

slodat
Posts: 795
Joined: Thu Apr 12, 2018 11:16 pm
Acorn CNC Controller: Yes
Plasma CNC Controller: No
AcornSix CNC Controller: No
Allin1DC CNC Controller: No
Hickory CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC11: No
CPU10 or CPU7: No

Re: DMM DYN4 Spindle Set-up - receiving -1V at power up

Post by slodat »

You could power down the motor power to the spindle DYN4 with a contactor that is controlled by the FWD output of Acorn. As long as the logic is separately powered, seems like it would be a way to get an enable.. Also the DYN4 does have an enable input.. could that be switched with the FWD output of Acorn?


Nick4Maker
Posts: 33
Joined: Fri Jan 12, 2018 12:34 am
Acorn CNC Controller: Yes
Plasma CNC Controller: No
AcornSix CNC Controller: No
Allin1DC CNC Controller: No
Hickory CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: 38D26959B3D8-0103180444
DC3IOB: No
CNC11: No
CPU10 or CPU7: No

Re: DMM DYN4 Spindle Set-up - receiving -1V at power up

Post by Nick4Maker »

Slodat,

I like your idea of "Also the DYN4 does have an enable input.. could that be switched with the FWD output of Acorn?" its pin 15 on the DMM.

With a contactor, I'm not crazy about the idea to turn the servo drive on & off every time the spindle stops.

Here is my course of action. If one does not work, go to the next one.
1) Try FWD output of Acorn to DYN4 enable input pin 15. I need to run this by the DMM people and see if resistor is need and run in between +24V and DIR+. Or see if they have any other suggestions
2) Diode. Couple people suggested this. I need to find out what is the amperage that is coming from the 0-10V output.
3) Relay configuration
4) Punt and by a machine center. :D

Thanks to all for the input, much appreciated.

Nick


Nick4Maker
Posts: 33
Joined: Fri Jan 12, 2018 12:34 am
Acorn CNC Controller: Yes
Plasma CNC Controller: No
AcornSix CNC Controller: No
Allin1DC CNC Controller: No
Hickory CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: 38D26959B3D8-0103180444
DC3IOB: No
CNC11: No
CPU10 or CPU7: No

Re: DMM DYN4 Spindle Set-up - receiving 1V at power up - voltage drift (Solved)

Post by Nick4Maker »

I happy to report the problem has been solved.
- Thanks to all the posted.
- Special thanks to Marty & Slodat for pointing me in the right direction.
- Special thanks to DMM for following up with the suggestion and creating a drawing, which is attached.

FYI, DMM direction for this optional set-up:

Use the DMMDRV program to check the Enable Active Low check box, then power cycle the drive, now the drive is Disabled when powered so it will not rotate with any analog input voltage.

- Connect FWD output to Enable input per attached diagram.
- When FWD command is given, it enables the drive and drive starts analog speed operation

This is the reason I chose Centroid and DMM, for tough weeks like this and the support that was given.

Nick
Attachments
DYN4AcornSpindle_R3.pdf
(64.07 KiB) Downloaded 132 times


rangerboy347
Posts: 66
Joined: Fri Aug 17, 2018 11:04 pm
Acorn CNC Controller: Yes
Plasma CNC Controller: No
AcornSix CNC Controller: No
Allin1DC CNC Controller: No
Hickory CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: 38d2693c4f62-0725181074
DC3IOB: No
CNC11: No
CPU10 or CPU7: No

Re: DMM DYN4 Spindle Set-up - receiving 1V at power up - voltage drift (solved)

Post by rangerboy347 »

are you using to relay board or just oc5? do you have a pic?
joe


martyscncgarage
Community Expert
Posts: 9958
Joined: Tue Mar 28, 2017 12:01 pm
Acorn CNC Controller: Yes
Plasma CNC Controller: Yes
AcornSix CNC Controller: Yes
Allin1DC CNC Controller: Yes
Hickory CNC Controller: Yes
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No
Location: Mesa, AZ

Re: DMM DYN4 Spindle Set-up - receiving 1V at power up - voltage drift (solved)

Post by martyscncgarage »

rangerboy347 wrote: Sun May 26, 2019 2:31 pm are you using to relay board or just oc5? do you have a pic?
joe
Always use a relay board. It has dry contacts.
Any special drive from DMM needs to be specified at time of order. They don't automatically have the firmware in them for spindle operation.
Reminder, for support please follow this post: viewtopic.php?f=20&t=383
We can't "SEE" what you see...
Mesa, AZ


rangerboy347
Posts: 66
Joined: Fri Aug 17, 2018 11:04 pm
Acorn CNC Controller: Yes
Plasma CNC Controller: No
AcornSix CNC Controller: No
Allin1DC CNC Controller: No
Hickory CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: 38d2693c4f62-0725181074
DC3IOB: No
CNC11: No
CPU10 or CPU7: No

Re: DMM DYN4 Spindle Set-up - receiving 1V at power up - voltage drift (solved)

Post by rangerboy347 »

got it working thanks Marty now just to get the chuck to line up with commanded speed.


martyscncgarage
Community Expert
Posts: 9958
Joined: Tue Mar 28, 2017 12:01 pm
Acorn CNC Controller: Yes
Plasma CNC Controller: Yes
AcornSix CNC Controller: Yes
Allin1DC CNC Controller: Yes
Hickory CNC Controller: Yes
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No
Location: Mesa, AZ

Re: DMM DYN4 Spindle Set-up - receiving 1V at power up - voltage drift (solved)

Post by martyscncgarage »

rangerboy347 wrote: Sun May 26, 2019 6:49 pm got it working thanks Marty now just to get the chuck to line up with commanded speed.
Will be a little trickier. Are you running Dyn4 on 120vac or 240vac?
It is my understanding that Dyn4 will max out at 3000rpm @120vac and about 5.5krpm at 240vac

I believe you have to use the DMMDRV software to establish the max RPM when you supply 10vdc.

I'll he testing this soon, but not likely before I leave on vacation.

Keep us posted on your progress...
Marty
Reminder, for support please follow this post: viewtopic.php?f=20&t=383
We can't "SEE" what you see...
Mesa, AZ


rangerboy347
Posts: 66
Joined: Fri Aug 17, 2018 11:04 pm
Acorn CNC Controller: Yes
Plasma CNC Controller: No
AcornSix CNC Controller: No
Allin1DC CNC Controller: No
Hickory CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: 38d2693c4f62-0725181074
DC3IOB: No
CNC11: No
CPU10 or CPU7: No

Re: DMM DYN4 Spindle Set-up - receiving 1V at power up - voltage drift (solved)

Post by rangerboy347 »

dyn4 on 240vac and yes 3000 is max for the 1.8kw and at 2000 rpm its crazy fast lol. one thing i was wondering is there a way to ramp up and down the speed cause its instant full speed and slows same way pretty violent seams stressful on belt. I have the chuck running commanded speed by setting the max speed in cnc 12 basically fooling it but my worry is will this effect thread cutting and taping? or will it be ok, because the encoder shows the speed of the servo drive witch is different then the chuck speed.
joe


rangerboy347
Posts: 66
Joined: Fri Aug 17, 2018 11:04 pm
Acorn CNC Controller: Yes
Plasma CNC Controller: No
AcornSix CNC Controller: No
Allin1DC CNC Controller: No
Hickory CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: 38d2693c4f62-0725181074
DC3IOB: No
CNC11: No
CPU10 or CPU7: No

Re: DMM DYN4 Spindle Set-up - receiving 1V at power up - voltage drift (solved)

Post by rangerboy347 »

this may help
Attachments
dmm.PNG


Nick4Maker
Posts: 33
Joined: Fri Jan 12, 2018 12:34 am
Acorn CNC Controller: Yes
Plasma CNC Controller: No
AcornSix CNC Controller: No
Allin1DC CNC Controller: No
Hickory CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: 38D26959B3D8-0103180444
DC3IOB: No
CNC11: No
CPU10 or CPU7: No

Re: DMM DYN4 Spindle Set-up - receiving 1V at power up - voltage drift (solved)

Post by Nick4Maker »

Hey guys just an update,

I added the new relay board and the drifting started come back. I even tried a diode, it only made the spindle rotate faster.

So here is the solution that worked and its proving to be solid solution so far, using the new relay board from Centroid:
Relay 4 - Spindle FWD
Relay 5 - Spindle Reverse
Relay 6 - Spindle Release Brake

Therefore, I'm using Relay-6 to control Analog out 0-10V pin13. No drift, till Centroid activates Spindle Brake Release.

I ended up putting an auxiliary panel, the things that experience teaches us. Here is a picture:
Attachments
20190521_233254.jpg


Post Reply