Limit switches are tripping randomly during machine operation

All things related to the Centroid Acorn CNC Controller

Moderator: cnckeith

DICKEYBIRD
Posts: 536
Joined: Sat Jul 08, 2017 7:38 am
Acorn CNC Controller: Yes
Allin1DC CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: n/a yet
DC3IOB: No
CNC11: No
CPU10 or CPU7: No
Location: Collierville, TN USA

Re: Limit switches are tripping randomly during machine operation

Post by DICKEYBIRD »

tblough wrote: Mon Feb 04, 2019 2:38 pm Noise is extraneous voltage induced in the wires. If your switch is NO and the controller is looking for a voltage signal, a stray 1-2V spike can set it off. If the control is using a 24V NC switch, the control is seeing 24V when the is switch not made. A stray 1-2V spike just changes that from 24V to 26V - still not made. It's pretty easy for the control to notice the absence of 24V even with a few volts of noise in the system.
Tom that is the most clear & common sense explanation of the issue I've seen. Thanks for posting! I wish Amazon would introduce a "Tom the CNC Teacher" device. Alexa's smarter brother. I'd buy one in a heart beat! :lol:
Milton in Collierville, TN

"Accuracy is the sum total of your compensating mistakes."


Richards
Posts: 706
Joined: Sun Sep 16, 2018 9:01 pm
Acorn CNC Controller: Yes
Allin1DC CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No
Location: South Jordan, UT

Re: Limit switches are tripping randomly during machine operation

Post by Richards »

I'm wondering if there might be a misunderstanding of how the Acorn INPUTs work? Page 5 of the Acorn CNC Controller Specification Manual shows that external devices pull current through an opto-coupler that (internally inside the Acorn) activates a signal. If nothing is connected to that input, the LED will never turn on. Noise would have to be extreme. It would have to pull about 10mA through that LED and the duration of that noise would have to be long enough for the Acorn to pick up that false signal. Page 7 of the manual shows that a LOW signal is 0 to 5.9 volts and a HIGH signal is 19.1 volts to 26 volts. Page 7 also gives the operating current as 20mA. You can test the minimum current needed to produce a signal by using a resistor with one end tied to GROUND and the other end connected to an Input. A 1K resistor allows about 20mA to flow. 2.2K allows about 10mA to flow, and so on. (To verify the amount of current required, put a multimeter - set to read current - in series with the resistor.) With the CNC program running, push ATL-I to get to the screen that shows Inputs and Outputs, and watch the Input to which you've connected the resistor. At some point, the LED will not change state, indicating that not enough current is flowing through the LED to generate a signal.

It's always a good idea to use a shield cable with the shield tied (on one end only!) directly to chassis ground. So far, on my test bench, I have not had any noise problems with the Acorn board just using twisted pair wires.
-Mike Richards


slodat
Posts: 795
Joined: Thu Apr 12, 2018 11:16 pm
Acorn CNC Controller: Yes
Allin1DC CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC11: No
CPU10 or CPU7: No

Re: Limit switches are tripping randomly during machine operation

Post by slodat »

mick41zxr wrote: Mon Jan 28, 2019 6:48 am Check with Keith,
I think there is an issue with home/limitOk setup at moment. I had an issue where home/limit kept re-tripping on axis 1 across a variety of switch types.
Only happened in first axis. Changed setup to home all & problem went away, just used soft limits after that.
Regards,
Michael
This is the only thing I’ve changed. Just ran the exact same gcode that I had multiple limit trips in when I first started this thread. Zero issues tonight. 90+ minutes straight of cutting. I feel like this home/limitOk vs homeOk is the issue. So, that’s how I’m running.

I did notice the following tonight.. inputs 1-3 (NO homeOk for x, y, z axis) are lit green and turn red when the limit switch trips. Input 7 (probeTripped configured NC, but the switches are actually NO) is green on a fresh system startup until I actuate the probe switch, then it goes red unless the probe is tripped. It boots up latched on until it sees a state change, then it works as expected.

I’m not replacing my NO limit switches at this time..
Attachments
00D06132-C5B9-40D7-AA15-F86578515535.jpeg
96A57C7E-AC08-4621-8229-F6DE4D39815E.jpeg


martyscncgarage
Community Expert
Posts: 9956
Joined: Tue Mar 28, 2017 12:01 pm
Acorn CNC Controller: Yes
Allin1DC CNC Controller: Yes
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC12: Yes
CNC11: Yes
CPU10 or CPU7: Yes
Location: Mesa, AZ

Re: Limit switches are tripping randomly during machine operation

Post by martyscncgarage »

Screen shot of the diagnostics page please.
Do you have lines over the LED on inputs 1, 2, 3?

Marty
Reminder, for support please follow this post: viewtopic.php?f=20&t=383
We can't "SEE" what you see...
Mesa, AZ


slodat
Posts: 795
Joined: Thu Apr 12, 2018 11:16 pm
Acorn CNC Controller: Yes
Allin1DC CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC11: No
CPU10 or CPU7: No

Re: Limit switches are tripping randomly during machine operation

Post by slodat »

On power up. Input 7 is green. Line over 1-3 and 5.
Attachments
399FA29C-C9F3-44C3-BCBA-48F7BE61274C.jpeg
After tripping probe once. Input 7 off.
After tripping probe once. Input 7 off.
On power up. Input 7 on. Lines over 1-3 and 5.
On power up. Input 7 on. Lines over 1-3 and 5.


martyscncgarage
Community Expert
Posts: 9956
Joined: Tue Mar 28, 2017 12:01 pm
Acorn CNC Controller: Yes
Allin1DC CNC Controller: Yes
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC12: Yes
CNC11: Yes
CPU10 or CPU7: Yes
Location: Mesa, AZ

Re: Limit switches are tripping randomly during machine operation

Post by martyscncgarage »

Limit switch inputs have been inverted, thats why the are green (NO)
Input 7 is probe tripped. Do you have a probe on the machine?

Marty
Reminder, for support please follow this post: viewtopic.php?f=20&t=383
We can't "SEE" what you see...
Mesa, AZ


slodat
Posts: 795
Joined: Thu Apr 12, 2018 11:16 pm
Acorn CNC Controller: Yes
Allin1DC CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC11: No
CPU10 or CPU7: No

Re: Limit switches are tripping randomly during machine operation

Post by slodat »

Yes.
slodat wrote: Tue Feb 05, 2019 1:35 am Input 7 (probeTripped configured NC, but the switches are actually NO) is green on a fresh system startup until I actuate the probe switch, then it goes red unless the probe is tripped. It boots up latched on until it sees a state change, then it works as expected.


cncman172
Posts: 254
Joined: Thu Nov 02, 2017 4:07 pm
Acorn CNC Controller: Yes
Allin1DC CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: 985DAD429EE9-0926170118
DC3IOB: No
CNC11: No
CPU10 or CPU7: No
Location: Westerville, Ohio

Re: Limit switches are tripping randomly during machine operation

Post by cncman172 »

Slodat,
I have seen this same exact issue. I am using a TT (touchoff) tool post and when I first start up the indicator is wrong. I have to press the touch off post once before a do any work. That seems to toggle the software in CNC12. I first thought it was something wrong in my touch off indicator but I checked it with a meter and it worked correctly.

I was going to make a video of this and send it to Keith and the development team. Seems to do the same thing if you use input7 for a probe in your case or Input4 for the TT in my case.

Russ


martyscncgarage
Community Expert
Posts: 9956
Joined: Tue Mar 28, 2017 12:01 pm
Acorn CNC Controller: Yes
Allin1DC CNC Controller: Yes
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC12: Yes
CNC11: Yes
CPU10 or CPU7: Yes
Location: Mesa, AZ

Re: Limit switches are tripping randomly during machine operation

Post by martyscncgarage »

General Reference:
viewtopic.php?f=63&t=1023

See Keith's last post
Reminder, for support please follow this post: viewtopic.php?f=20&t=383
We can't "SEE" what you see...
Mesa, AZ


slodat
Posts: 795
Joined: Thu Apr 12, 2018 11:16 pm
Acorn CNC Controller: Yes
Allin1DC CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC11: No
CPU10 or CPU7: No

Re: Limit switches are tripping randomly during machine operation

Post by slodat »

martyscncgarage wrote: Tue Feb 05, 2019 12:40 pm General Reference:
viewtopic.php?f=63&t=1023

See Keith's last post
I have my NPN NO switches wired individually to inputs 1-3.
Last edited by slodat on Tue Feb 05, 2019 1:57 pm, edited 1 time in total.


Post Reply