take a look at TB300
http://www.centroidcnc.com/cnc_techbulletin.html
that should get you going.
M Code control of Aux Contacts Output 9
Re: M Code control of Aux Contacts Output 9
TB300 does not have any information about that.The manual talks about output 8 & 9 but how do you map to an M Code?
You have to change the PLC program.
The request flow is generally like this:
1) Custom M function macro files "mfuncxx.mac" uses M94 and M95 to turn a request bit on and off.
2) The PLC program sees that M function request bit, combines it with any other relevant logic, and uses that to turn an output on or off.
The request bit number (the number which follows M94 or M95) does not necessarily have to be the same as the associated CNC M function, but your program will be a little easier to understand if you do it that way.
Neither the request bit number nor the associated CNC M functions need to match the number of the output to be controlled.
Suppose you want to use M71 to turn on OUT9, and M72 to turn it off, and there are no limitations or interlocks associated with it.
Then you might choose request bit #71. You do not need to use another request bit for turning off. In simple cases like this, the second M function just turns off the request that was set by the first one.
So your mfunc71.mac file might read:
; M71 - Turn on OUT9
M94/71
; M72 - Turn off OUT9
M95/71
M71Out IS OUT9
M71 IS SV_M94_M95_71
IF M71 THEN (M71Out)
I have been searching the system for the connection between AUX3 and Output 9 but have not found anything
Every place the manual talks about AUX3 and or 9 has nothing
This is where I have been stumped
I figured that if I could see the current configuration it would help me understand how to program
If you post a report, then we can look in your PLC program source file.