Testing out the ATC function after reinstalling CNC12 and got an error about a missing file during a tool change.
Turns out the standard mfunc6.mac file has the following line:
G65 "C:\cncm\system\tt_check_configuration.cnc"
This macro is a safety check to ensure a tool setter is attached and configured properly before doing a tool touch-off. However, the file wasn't installed by CNC12 5.30 for Hickory.
I've downloaded & extracted a number of Acorn report files from the forum (back to 1/2024) and the tt-check file is present under /urf/system.
All three Hickory reports I downloaded (back to early 2024) are missing the file, and in the single report where the user had an ATC their mfunc6.mac file has the entire tool check section commented out.
So... long story short... Centroid might want to take a look at the Hickory installation and if mfunc6.mac calls tt_check_configuration.cnc ensure that file is present after installation.
Hickory M6 calls missing macro
Moderator: cnckeith
-
- Posts: 50
- Joined: Sat Mar 22, 2025 5:24 pm
- Acorn CNC Controller: No
- Plasma CNC Controller: No
- AcornSix CNC Controller: No
- Allin1DC CNC Controller: No
- Hickory CNC Controller: Yes
- Oak CNC controller: No
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC12: No
- CNC11: No
- CPU10 or CPU7: No
Hickory M6 calls missing macro
(Note: Liking will "up vote" a post in the search results helping others find good information faster)
-
- PLC Expert
- Posts: 245
- Joined: Wed Jul 31, 2019 12:53 pm
- Acorn CNC Controller: Yes
- Plasma CNC Controller: No
- AcornSix CNC Controller: No
- Allin1DC CNC Controller: Yes
- Hickory CNC Controller: No
- Oak CNC controller: Yes
- CNC Control System Serial Number: none
- DC3IOB: Yes
- CNC12: Yes
- CNC11: Yes
- CPU10 or CPU7: Yes
Re: Hickory M6 calls missing macro
Hello Spumco,
Thanks for reporting this, you are correct that it does appear the hickory install does not install this file. This will be corrected for next release.
You can copy the file found in the acorn/acornsix install to the hickory install or use the one attached here in the mean time.
Thanks for reporting this, you are correct that it does appear the hickory install does not install this file. This will be corrected for next release.
You can copy the file found in the acorn/acornsix install to the hickory install or use the one attached here in the mean time.
- Attachments
-
- tt_check_configuration.cnc
- (6.54 KiB) Downloaded 52 times
When requesting support READ THIS POST first. viewtopic.php?t=1043
Please ALWAYS post a FRESH report. To make a report: https://www.youtube.com/watch?v=A36MSMilMyc.
(We pride ourselves on providing timely solid technical support but, without good information we may not be able to help and/or reply until such information is posted.)
Centroid PLC Tutorial Videos
Please ALWAYS post a FRESH report. To make a report: https://www.youtube.com/watch?v=A36MSMilMyc.
(We pride ourselves on providing timely solid technical support but, without good information we may not be able to help and/or reply until such information is posted.)
Centroid PLC Tutorial Videos
(Note: Liking will "up vote" a post in the search results helping others find good information faster)
-
- Posts: 50
- Joined: Sat Mar 22, 2025 5:24 pm
- Acorn CNC Controller: No
- Plasma CNC Controller: No
- AcornSix CNC Controller: No
- Allin1DC CNC Controller: No
- Hickory CNC Controller: Yes
- Oak CNC controller: No
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC12: No
- CNC11: No
- CPU10 or CPU7: No
Re: Hickory M6 calls missing macro
It may not be necessary to copy the file over. Looks like the Hickory version of tool check from the tool offsets page uses an alternate tool setter config check in the form of tool_offset_auto_measure.cnc. This macro accomplishes the same thing as the 'missing' Acorn file.
So it appears that there is an 'Acorn' scheme and a 'Hickory' scheme, but the current Hickory implementation has some leftover stuff from when it was copied from Acorn.
May make more sense to delete the G65 from Hickory's mfunc6.mac file. Copying the Acorn file to Hickory would essentially be using both schemes.
(Note: Liking will "up vote" a post in the search results helping others find good information faster)
-
- Posts: 50
- Joined: Sat Mar 22, 2025 5:24 pm
- Acorn CNC Controller: No
- Plasma CNC Controller: No
- AcornSix CNC Controller: No
- Allin1DC CNC Controller: No
- Hickory CNC Controller: Yes
- Oak CNC controller: No
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC12: No
- CNC11: No
- CPU10 or CPU7: No
Re: Hickory M6 calls missing macro
Unfortunately, the tt_check_config.cnc file isn't appropriate for Hickory.
The file was written for Acorn and all of the probe input check lines are restricted to inputs 1-16. Hickory has up to 32 inputs. Because my TT-4 is on input 32, I got an error message when the tool touchoff started.
To work with Hickory I edited the file and replaced all instances of "16" with "32", which also covered the plc input lines (50032).
Might want to have a Hickory-specific version for 5.40.
The file was written for Acorn and all of the probe input check lines are restricted to inputs 1-16. Hickory has up to 32 inputs. Because my TT-4 is on input 32, I got an error message when the tool touchoff started.
To work with Hickory I edited the file and replaced all instances of "16" with "32", which also covered the plc input lines (50032).
Might want to have a Hickory-specific version for 5.40.
(Note: Liking will "up vote" a post in the search results helping others find good information faster)
-
- Community Expert
- Posts: 3832
- Joined: Thu Sep 23, 2021 3:49 pm
- Acorn CNC Controller: Yes
- Plasma CNC Controller: No
- AcornSix CNC Controller: No
- Allin1DC CNC Controller: No
- Hickory CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: 6433DB0446C1-08115074
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
- Location: Germany
Re: Hickory M6 calls missing macro
On Acorn6 the tt_check_config.cnc is installed but not used IMHO.
It looks like a leftover from V4.99, maybe for users with old custom M6 macros.
From V5.18 and up the functionality is built in tool_offset_auto_measure.cnc
I also suggest to update only Hickory's mfunc6.mac
Uwe
It looks like a leftover from V4.99, maybe for users with old custom M6 macros.
From V5.18 and up the functionality is built in tool_offset_auto_measure.cnc
I also suggest to update only Hickory's mfunc6.mac
Uwe
(Note: Liking will "up vote" a post in the search results helping others find good information faster)
-
- PLC Expert
- Posts: 245
- Joined: Wed Jul 31, 2019 12:53 pm
- Acorn CNC Controller: Yes
- Plasma CNC Controller: No
- AcornSix CNC Controller: No
- Allin1DC CNC Controller: Yes
- Hickory CNC Controller: No
- Oak CNC controller: Yes
- CNC Control System Serial Number: none
- DC3IOB: Yes
- CNC12: Yes
- CNC11: Yes
- CPU10 or CPU7: Yes
Re: Hickory M6 calls missing macro
Yeah honestly i forgot about that part of the macro, Thanks for pointing it out. The modification to 32 will do for now. I think its time for me to re-think that macro, the range check makes sense for Acorn, but not the other boards.spumco wrote: ↑Thu Aug 21, 2025 9:33 pm Unfortunately, the tt_check_config.cnc file isn't appropriate for Hickory.
The file was written for Acorn and all of the probe input check lines are restricted to inputs 1-16. Hickory has up to 32 inputs. Because my TT-4 is on input 32, I got an error message when the tool touchoff started.
To work with Hickory I edited the file and replaced all instances of "16" with "32", which also covered the plc input lines (50032).
Might want to have a Hickory-specific version for 5.40.
When requesting support READ THIS POST first. viewtopic.php?t=1043
Please ALWAYS post a FRESH report. To make a report: https://www.youtube.com/watch?v=A36MSMilMyc.
(We pride ourselves on providing timely solid technical support but, without good information we may not be able to help and/or reply until such information is posted.)
Centroid PLC Tutorial Videos
Please ALWAYS post a FRESH report. To make a report: https://www.youtube.com/watch?v=A36MSMilMyc.
(We pride ourselves on providing timely solid technical support but, without good information we may not be able to help and/or reply until such information is posted.)
Centroid PLC Tutorial Videos
(Note: Liking will "up vote" a post in the search results helping others find good information faster)
-
- Community Expert
- Posts: 3832
- Joined: Thu Sep 23, 2021 3:49 pm
- Acorn CNC Controller: Yes
- Plasma CNC Controller: No
- AcornSix CNC Controller: No
- Allin1DC CNC Controller: No
- Hickory CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: 6433DB0446C1-08115074
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
- Location: Germany
Re: Hickory M6 calls missing macro
I would restrict it to 8 on Acorn because the Ether 1616 is too slow to use for a probe or TT and with one you have 8+16 inputs.Allin1Chris wrote: ↑Fri Aug 22, 2025 9:56 amYeah honestly i forgot about that part of the macro, Thanks for pointing it out. The modification to 32 will do for now. I think its time for me to re-think that macro, the range check makes sense for Acorn, but not the other boards.spumco wrote: ↑Thu Aug 21, 2025 9:33 pm Unfortunately, the tt_check_config.cnc file isn't appropriate for Hickory.
The file was written for Acorn and all of the probe input check lines are restricted to inputs 1-16. Hickory has up to 32 inputs. Because my TT-4 is on input 32, I got an error message when the tool touchoff started.