Spindle Jog?
chronolite
CNC Control System Serial Number: 7804739E42DF-0925192491
Spindle Jog?
Post by chronolite »
I can't seem to find anywhere that I can enable my lathe spindle to jog. The operators want to be able to hit the jog buttons on the MPG and move the spindle slowly at some speed and rotate the wheel to spin the spindle. This particular spindle/chuck is difficult to move by hand. Can I set the Oak to recognize the spindle as a rotary axis?
chronolite
Re: Spindle Jog?
Okay, I think that this is set via P35 and P312. I will try this weekend during downtime unless someone has some more insight.
Re: Spindle Jog?
For this you have to set up the spindle as C-Axis and switch with M50/51 the C-axis mode.
chronolite
Re: Spindle Jog?
Hmm, not sure what I am doing wrong here.
So far I have:
P313 = 6
P35 = 6
I set axis 6 (it has a little S next to it) in the motor CFG to also say C
P167 = 19
I see the C axis in the DRO, but it has a huge value (not 360) and it doesn't move when I select Axis 6 on the MPG. Is there a TB or a guide or something that can help me get all this together? M50 and M51 also give an error that they're not implemented.
Re: Spindle Jog?
chronolite wrote: Thu Jan 18, 2024 2:57 pm Hmm, not sure what I am doing wrong here.
So far I have:
P313 = 6
P35 = 6
P167 = 19
post a fresh report.zip
Re: Spindle Jog?
You do not need C axis control for the kind of spindle jog you describe.
You just need a few additions to the PLC program.
I usually make a couple memory bits:
One, "SpindleEnable_M" takes the place of SpindleEnableOut in the standard spindle start/stop logic.
The other, "SpindleJog_M", is usually controlled by an Aux key or external pushbutton.
e.g.
IF Aux1Key && !SpindleEnable_M && !SV_STOP THEN (SpindleJog_M)
The output relay "SpindleEnableOut" is then controlled by SpindleEnable_M and SpindleJog_M", OR'd together:
IF SpindleEnable_M || SpindleJog_M THEN (SpindleEnableOut)
In the speed control section, I override the spindle speed command with a value from a machine parameter during spindle jogging:
; In auto mode, assuming M3 or M4 present, use given RPM from CNC11/CNC12
IF SpinAutoModeLED THEN SpinSpeedCommand_FW = SV_PC_COMMANDED_SPINDLE_SPEED
; In manual mode, assuming spindle is on, use speed scaled from CCFG max
IF !SpinAutoModeLED THEN SpinSpeedCommand_FW = CfgMaxSpeed_FW *
                                               SV_PLC_SPINDLE_KNOB / 200.0 *
                                               SpinRangeAdjust_FW
; In manual or auto, if no M3/M4 or spindle run, then use zero instead
IF !SpindleEnable_M THEN SpinSpeedCommand_FW = 0.0
IF SpindleJog_M THEN SpinSpeedCommand_FW = SV_MACHINE_PARAMETER_760
chronolite
Re: Spindle Jog?
I'll setup an AUX key and then set P760 to 10 rpm or so and this should do it. Yeah this is very good. Simple. I'll follow up after the weekend. Thank you very much.