Spindle fault remove probe from spindle

Posted: Thu Dec 21, 2023 4:13 pm
by DrLocke
Upgrading from v4.82 to v5.06. v4.82 has worked fine for months. Got v5.06 running X,Y,Z and TT-1 and KC-3 probe appear to work. Spindle will not start because of subject error. Have removed probe from wizard and still same error. I'm guessing I need to change a parameter but can't find a reference. This appears to be my final hurdle. Latest Report attached. (prior to removal of probe in wizard.)

Re: Spindle fault remove probe from spindle

Posted: Thu Dec 21, 2023 4:29 pm
by dpascucci_support
Your report claims that the tool in the spindle is T10, which is the probe. Is the tool listed in the status bar in the top-right: T10H10?

Re: Spindle fault remove probe from spindle

Posted: Thu Dec 21, 2023 6:18 pm
by DrLocke
It was when I first attempted to start the spindle and I then changed it to tool #1 but that didn't solve the issue.

Re: Spindle fault remove probe from spindle

Posted: Thu Dec 21, 2023 6:47 pm
by cnckeith
DrLocke wrote: Thu Dec 21, 2023 6:18 pm It was when I first attempted to start the spindle and I then changed it to tool #1 but that didn't solve the issue.
sounds like the probe detect signal has been inverted?

Re: Spindle fault remove probe from spindle

Posted: Thu Dec 21, 2023 6:48 pm
by cnckeith
12-21-2023 0:25:44 9030 SPINDLE FAULT!
(4) 12-21-2023 0:25:44 9033 Reset Initiated, Press Reset to Clear
(4) 12-21-2023 9:00:30 9030 SPINDLE FAULT!
(4) 12-21-2023 9:00:30 4032 Reset Cleared
(4) 12-21-2023 9:00:32 9030 SPINDLE FAULT!
(1) 12-21-2023 9:01:01 204 Exiting CNC...Normal Exit (66)
(1) 12-21-2023 9:01:32 199 CNC Started
(1) 12-21-2023 9:01:40 CNC12 Acorn Mill v5.06
(4) 12-21-2023 9:01:40 9033 Reset Initiated, Press Reset to Clear
(4) 12-21-2023 9:01:46 4032 Reset Cleared
(1) 12-21-2023 9:02:23 407 Z+ limit (#50036) tripped
(1) 12-21-2023 9:02:26 407 Y- limit (#50035) tripped
(1) 12-21-2023 9:02:29 407 X+ limit (#50033) tripped
(1) 12-21-2023 9:17:28 204 Exiting CNC...Normal Exit (66)
(1) 12-21-2023 10:14:44 199 CNC Started
(1) 12-21-2023 10:14:51 CNC12 Acorn Mill v5.06
(4) 12-21-2023 10:14:51 9033 Reset Initiated, Press Reset to Clear
(4) 12-21-2023 10:15:00 4032 Reset Cleared
(1) 12-21-2023 10:15:17 407 Z+ limit (#50036) tripped
(1) 12-21-2023 10:15:19 407 Y- limit (#50035) tripped
(1) 12-21-2023 10:15:21 407 X+ limit (#50033) tripped
(1) 12-21-2023 10:16:45 407 Z+ limit (#50036) tripped
(1) 12-21-2023 10:37:11 8075 WARNING: TOOL TOUCH OFF TRIPPED
(1) 12-21-2023 10:37:12 9077 Tool Touch Off Cleared
(1) 12-21-2023 10:40:51 303 Paused...
(1) 12-21-2023 10:40:52 307 Operator abort: job cancelled
(4) 12-21-2023 10:40:52 8075 WARNING: TOOL TOUCH OFF TRIPPED
(4) 12-21-2023 10:40:52 9077 Tool Touch Off Cleared
(4) 12-21-2023 10:41:26 8075 WARNING: TOOL TOUCH OFF TRIPPED
(4) 12-21-2023 10:41:32 9077 Tool Touch Off Cleared
(4) 12-21-2023 10:41:47 9045 Drawbar Clamped
(4) 12-21-2023 10:43:54 9044 Drawbar Released
(1) 12-21-2023 10:44:30 407 Z+ limit (#50036) tripped
(1) 12-21-2023 10:45:22 407 Z+ limit (#50036) tripped
(1) 12-21-2023 10:45:27 407 Z+ limit (#50036) tripped
(1) 12-21-2023 10:46:38 918 Probe unable to detect surface
(4) 12-21-2023 10:47:23 9045 Drawbar Clamped
(4) 12-21-2023 11:12:28 9044 Drawbar Released
(1) 12-21-2023 11:14:40 907 X axis travel exceeded
(1) 12-21-2023 11:18:49 407 Z+ limit (#50036) tripped
(1) 12-21-2023 11:20:18 407 Z+ limit (#50036) tripped
(1) 12-21-2023 11:20:23 407 Z+ limit (#50036) tripped
(1) 12-21-2023 11:20:28 407 Z+ limit (#50036) tripped
(4) 12-21-2023 11:23:41 9045 Drawbar Clamped
(4) 12-21-2023 11:26:34 9044 Drawbar Released
(1) 12-21-2023 11:30:41 8040 WARNING: PROBE TRIPPED
(1) 12-21-2023 11:33:13 9042 Probe Cleared
(4) 12-21-2023 11:33:20 907 Z axis travel exceeded
(4) 12-21-2023 11:33:20 907 Z axis travel exceeded
(4) 12-21-2023 11:33:20 907 Z axis travel exceeded
(4) 12-21-2023 11:33:47 9045 Drawbar Clamped
(4) 12-21-2023 11:33:48 8040 WARNING: PROBE TRIPPED
(4) 12-21-2023 11:33:48 9042 Probe Cleared
(1) 12-21-2023 11:36:45 Creating report...

Re: Spindle fault remove probe from spindle

Posted: Thu Dec 21, 2023 7:32 pm
by DrLocke
Posted a new report that shows the fault as most recent action.
Added probe back into the wizard.
Tried inverting the Probe Detect and no change, still faults when attempting to start spindle.

Re: Spindle fault remove probe from spindle

Posted: Fri Dec 22, 2023 10:56 am
by dpascucci_support
In the wizard, what are the settings for "inhibit spindle when detect is on" for both your probe and tt?

Re: Spindle fault remove probe from spindle

Posted: Fri Dec 22, 2023 11:08 am
by suntravel
dpascucci_support wrote: Fri Dec 22, 2023 10:56 am In the wizard, what are the settings for "inhibit spindle when detect is on" for both your probe and tt?
I have both set to yes, this is no problem to run the spindle if probe detect or tripped is not on.

Uwe

Re: Spindle fault remove probe from spindle

Posted: Fri Dec 22, 2023 11:55 am
by dpascucci_support
suntravel wrote: Fri Dec 22, 2023 11:08 am
I have both set to yes, this is no problem to run the spindle if probe detect or tripped is not on.

Uwe
Right, but if the TT is set to inhibit the spindle while detect is on, it will trip the same fault "Remove probe from spindle" even though the issue lies in the TT being connected.

Re: Spindle fault remove probe from spindle

Posted: Fri Dec 22, 2023 12:40 pm
by DrLocke
Thank you, thank you, thank you. Changed TT to NOT inhibit and looking good!
Merry Christmas!