Page 1 of 2

TB270 and TB309(Rev4) Comm error <resolved>

Posted: Fri Aug 25, 2023 4:19 pm
by chief_hacker
Hello,
I am experiencing 425 communication errors.

I have followed tech bulletin 270
1) Bench test complete
2) New Windows 11 operating system - I followed the two youtube videos in bulletin 270 and double checked all settings outlined as per TB309 (Rev4)
2023-08-25 13_57_19-Centroid.png
2023-08-25 14_00_18-Centroid.png
- Power options and sleep setting adjusted per instructions
- Clock settings adjusted per instructions

- Turn off energy efficient option - NA - Option not available
Screenshot 2023-08-25 140818.png
3) Not using bulkhead connector
4) Tested two different shielded ethernet cables 1) supplied with acorn and 2) user supplied shielded cable - Ethernet cable >6" away from all power / drive cables
5) Not using USB ethernet adapter
6) Ethernet adapter drivers up to date
Screenshot 2023-08-25 140859.png
7) No antivirus installed
2023-08-25 14_10_28-Centroid.png
8) Windows firewall turned off
2023-08-25 14_10_45-Centroid -.png
9) Bios power saving feature - Not sure - Where do I look?
10) No other network devices active - Wireless turned off
11) Tested two different cables
12) Wireless turned off
13) Don't believe other programs are attempting to update - suggestions on how to check?
14) DC power supply dedicated to Acorn
-Stress Test results
2023-08-25 14_10_58-Centroid -.png
-CPU and computer specs
2023-08-25 14_11_16-Centroid -.png
2023-08-25 14_11_31-Centroid -.png
Thoughts on what I can try next?

Thank you,
Matthew

Re: TB270 and TB309(Rev4) Comm error unresolved

Posted: Fri Aug 25, 2023 4:32 pm
by ShawnM
That's all great info Matthew but you forgot to attach a current report from the machine, we need to see that also. Snap a pic of the control cabinet also or better yet start a google photo album to keep your pics all in one place and share a link here. Are you using shielded wires where needed?

Re: TB270 and TB309(Rev4) Comm error unresolved

Posted: Fri Aug 25, 2023 4:39 pm
by chief_hacker
Thanks for the reminder on the machine report.
Attached
Control cabinet photo - Attached

VFD cable is not shielded - VFD not active during stress test.

Re: TB270 and TB309(Rev4) Comm error unresolved

Posted: Fri Aug 25, 2023 6:25 pm
by cnckeith

Re: TB270 and TB309(Rev4) Comm error unresolved

Posted: Fri Aug 25, 2023 7:00 pm
by chief_hacker
Look at that!
2023-08-25 16_58_18-CNC12 Lathe.png
Changing the ethernet adapter to 100Mbps half duplex fix the issue.

Can I request this be added to TB309?

Thank you all!

Re: TB270 and TB309(Rev4) Comm error unresolved

Posted: Sun Aug 27, 2023 9:26 pm
by BDRetz
So glad I found this thread. Spent a couple hours today chasing wires and windows settings for a 425 comm error. Speed and duplex setting fixed mine as well.

Thank you all for this great resource.

Re: TB270 and TB309(Rev4) Comm error unresolved

Posted: Mon Aug 28, 2023 5:47 pm
by cnckeith
The Centroid CNC PC Configurator is now available in beta.

https://centroidcncforum.com/viewtopic.php?f=67&t=9157

Re: TB270 and TB309(Rev4) Comm error unresolved

Posted: Sat Feb 17, 2024 2:43 pm
by phazertwo
Chief_hacker you are a life saver!

I have been fighting com issues since I updated CNC12 last month... so frustrating!

I agree that this should be added to the COM issues tech bulletin.

PZ

Re: TB270 and TB309(Rev4) Comm error unresolved

Posted: Sat Feb 17, 2024 2:50 pm
by suntravel
phazertwo wrote: Sat Feb 17, 2024 2:43 pm Chief_hacker you are a life saver!

I have been fighting com issues since I updated CNC12 last month... so frustrating!

I agree that this should be added to the COM issues tech bulletin.

PZ
Did you read the current version?

Uwe

Re: TB270 and TB309(Rev4) Comm error unresolved

Posted: Sat Feb 17, 2024 10:26 pm
by ShawnM
phazertwo wrote: Sat Feb 17, 2024 2:43 pm Chief_hacker you are a life saver!

I have been fighting com issues since I updated CNC12 last month... so frustrating!

I agree that this should be added to the COM issues tech bulletin.

PZ
As Uwe stated, it's all in Rev12 page 5.