AcornSix Enable
Posted: Tue May 30, 2023 5:06 pm
by kman1967
Acorn Six enable output on H13 and H14...
1. Is it only 5V or capable of 24V as well
2. Is it sinking or sourcing?
Re: AcornSix Enable
Posted: Tue May 30, 2023 5:19 pm
by kman1967
Update...
Page 40 of the AcornSix Install Manual rev12 shows +5v to the enable + and the enable - going to the H13 and H14 connectors.
but diagram for a Leadshine CS-D1008 show the enable out from the Acorn going to the enb+ on the drive and enable - on the drive going to grnd.
Re: AcornSix Enable
Posted: Tue May 30, 2023 5:53 pm
page 40 also says. "An example of drive wiring is below. Please consult your schematic for drive specific wiring."
so use.
https://www.centroidcnc.com/dealersuppo ... 147.r2.pdf
Re: AcornSix Enable
Posted: Tue May 30, 2023 8:45 pm
by kman1967
Not sure how the output can be sourcing and sinking, but OK, I'll wire like that and see what happens.
Re: AcornSix Enable
Posted: Wed May 31, 2023 12:45 pm
by Centroid_Tech2
See page 81 of the AcornSix install manual for a description of the outputs.
Headers H13 and H14 are 5V logic outputs (High = +5VDC , Low= 0V/GND).
Headers H1, H2, and H3 are open collector outputs (sinking).
Re: AcornSix Enable
Posted: Wed May 31, 2023 3:52 pm
by kman1967
Thanks, completely missed that.
Re: AcornSix Enable
Posted: Wed May 31, 2023 5:42 pm
by ShawnM
kman1967 wrote: ↑Wed May 31, 2023 3:52 pm
No worries, most everyone does.