ohmic test not reading

Posted: Sun Jul 31, 2022 11:07 am
by AtomicAsian
I’m still setting up and wanted to test the ohmic
wired to T in and input 9.
Alt i “diagnostics” 9 won’t light up when i move Z down to touch material.
the plasma is not connected yet. waiting on interface cable.
I ohm out tip to other end of wire to check for breakage. All good there.
what am I missing.

Re: ohmic test not reading

Posted: Sun Jul 31, 2022 11:12 am
by AtomicAsian
EEC9311D-D6F0-43D7-B716-8469F74FD52F.jpeg

Re: ohmic test not reading

Posted: Mon Aug 01, 2022 12:18 pm
by Joey
The material clamp needs connected and pin 6 of the Hypertherm CNC communication pins needs to be connected. The Torch touch runs from the "T in" connection on the TX Board through the material clamp and then back to the TX via the positive of the Divided voltage pins from the Hypertherm. Pin 6 is the positive of the Divided voltage and has continuity to the material clamp. Hope that helps.

Re: ohmic test not reading

Posted: Mon Aug 01, 2022 10:35 pm
by AtomicAsian
Thank you