i want to connect my integrated jmc servos motor`s which operate like a simple stepper motor/drive with an Step(+/-),Direction(+/-) and an Enable(+/-) Signal. Which Drive Type should i use in the Acorn Wizard?

this is the connection diagramm but i don`t want to use/connect the PED and ALM.
Bildschirmfoto 2022-01-05 um 19.54.35.png

best regards
Andy

Re: JMC integrated Servo - which Drive Type?

Posted: Wed Jan 05, 2022 3:07 pm
by CNCMaryland
Interested to know this as well. My new machine that is on the way will be running these. (I would run the Alarm however).

Re: JMC integrated Servo - which Drive Type?

Posted: Wed Jan 05, 2022 4:32 pm
by Andygraphy
great! :)

yes i think i connect the alarm too. I found this about wiring the alarm on JMC`s (in german):

but it seems simple:
Bildschirmfoto 2022-01-05 um 21.29.27.png
Bildschirmfoto 2022-01-05 um 21.29.04.png
Alarm reset via a relay (output) would be simple and sweet.

Re: JMC integrated Servo - which Drive Type?

Posted: Wed Jan 05, 2022 4:43 pm
by CNCMaryland
Not to get us too far away from the correct answer, there are other schematics posted that have similar drives and hookup. Those all use the Step Dir Enable, and Alarm. I will DM you the one I am talking about so you can at least look at it.

Re: JMC integrated Servo - which Drive Type?

Posted: Wed Jan 05, 2022 5:00 pm
by cnckeith
these motor/drives are interesting taking a look at them now.

Re: JMC integrated Servo - which Drive Type?

Posted: Wed Jan 05, 2022 6:22 pm
by ShawnM
Those motors are 5v logic and should be hooked to the DB25 via a breakout board. Wire them like a generic Leadshine following diagram S14976. If you get no movement then you can wire up the enable lines and try again. I don't know if they are enabled by default or not. Post the drive model number and a link to the manual if you want more help.

Re: JMC integrated Servo - which Drive Type?

Posted: Wed Jan 05, 2022 8:06 pm
by suntravel
JMC iHSV are 4.4-24V Pul/Dir/Ena and 8mA max on ALM Ped so you should use 1kOhm 5V or 4.7kOhm 24V for ALM and Ped

Try to get them with newest software Version 604

Regards

Uwe

Re: JMC integrated Servo - which Drive Type?

Posted: Tue Jan 11, 2022 10:47 am
by Andygraphy
Hi Uwe,

yes you`re right, instead of the information from the video the max for the PED and ALM is not 25mA, its 8mA! .. So the internal resistor of 1.2kOhm on the Input side is not enough and must be added with an second resistor. I Will choose an 2kOhm resistor to get an total of 3.2kOhm and an max of 7.5mA :)
JMC datasheet:
Bildschirmfoto 2022-01-11 um 16.07.20.png

this is my wiring diagramm for a lathe, based on the shematics S15034.R2:
Bildschirmfoto 2022-01-11 um 15.41.13.png
cheers
Andy

Re: JMC integrated Servo - which Drive Type?

Posted: Tue Jan 11, 2022 1:34 pm
by cnckeith
untested draft schematic for this motor/drive combo.
JMC_MOTOR-DRAFT.pdf
(841.02 KiB) Downloaded 118 times

Re: JMC integrated Servo - which Drive Type?

Posted: Tue Jan 11, 2022 2:07 pm
by Andygraphy
cnckeith wrote: Tue Jan 11, 2022 1:34 pm untested draft schematic for this motor/drive combo.

JMC_MOTOR-DRAFT.pdf
also a good idea... but 1 major failure and the question why using the DB25 connector for Step and direction instead of the screw terminals like the enable signal!?

the failure are hidden in the +5V of the Alarm... at 5V you need a resistor before the relay board with an minimum of 625Ohm... so i would take an 1kOhm resistor for being safe. ;)