Allin1DC E-Stop Circuit

Posted: Fri Mar 29, 2019 3:23 pm
by Aplus
In the TB 286 it shows running both the DC + and - between the rectifier and the VM terminals on the Allin1 thru the E-Stop contactor but the print number S14746R14 only shows running the V+ thru the E-Stop contactor (CNT1).
e-stop.JPG
S14746r14.JPG

Re: Allin1DC E-Stop Circuit

Posted: Fri Mar 29, 2019 4:02 pm
by tblough
You only need one to stop the motor, but since you'll have unused circuits on the contactor, it doesn't hurt to switch both. Brushed servos act as generators when back driven, so cutting both motor leads insures that no stray voltages are floating around if something should short in the windings.

Re: Allin1DC E-Stop Circuit

Posted: Thu Apr 04, 2019 11:33 pm
by Arrow
I usually run the +VM through all 3 contacts in series. This creates more of an "air gap" and helps prevent arc across on contacts which happens when breaking circuit on higher voltage DC.

Re: Allin1DC E-Stop Circuit

Posted: Sun Apr 07, 2019 7:49 am
by martyscncgarage
Arrow wrote: Thu Apr 04, 2019 11:33 pm I usually run the +VM through all 3 contacts in series. This creates more of an "air gap" and helps prevent arc across on contacts which happens when breaking circuit on higher voltage DC.
Arrow,
What make and model Estop contactor do you like to use?
Marty