Circuit Breaker Sizing
Posted: Tue Oct 09, 2018 11:02 am
I've been looking over the technical documentation for Yaskawa and I'm no less confused than when I began. They give guidelines for sizing breakers if you are only running a single drive. They then show a multiple drive configuration with single breakers for power and control but without a formula to arrive at the correct value. Their multiple drive configuration is similar to Centroid's. Their tech support then tells me that this should never be done and that they each need a breaker, even though their own documentation shows it.....
I have (4) 750 watt sigma 7 drives and I'm going to run them on single phase 240v. According to their docs, Current capacity is 8.7 amps main and 0.2 for the control. They then list 34 amps each for the main and control for inrush current. 68 amps.. Really?
Main circuit should hold for 5 sec at 3X capacity, and for 20ms at inrush. If I put one breaker on the main and one on the control for all 4 drives, what value would that be? Also is that a 1077, 508, or 489? Curve B, C, D???
Do you add them together, or do you assume that they are less demanding as they wont' all be driving at full bore simultaneously???
Also, the filter they recommend is a Japanese brand that isn't sold in the US. Has anyone used TDK brand? I'm looking at the RSEN series 20 amp.
Thanks!
I have (4) 750 watt sigma 7 drives and I'm going to run them on single phase 240v. According to their docs, Current capacity is 8.7 amps main and 0.2 for the control. They then list 34 amps each for the main and control for inrush current. 68 amps.. Really?
Main circuit should hold for 5 sec at 3X capacity, and for 20ms at inrush. If I put one breaker on the main and one on the control for all 4 drives, what value would that be? Also is that a 1077, 508, or 489? Curve B, C, D???
Do you add them together, or do you assume that they are less demanding as they wont' all be driving at full bore simultaneously???
Also, the filter they recommend is a Japanese brand that isn't sold in the US. Has anyone used TDK brand? I'm looking at the RSEN series 20 amp.