Yaskawa Sigma7 400V 5.5kW+ dynamic braking
Posted: Mon Mar 03, 2025 4:17 pm
Has anyone else configured a Hickory system with 400V Sigma7 drives of 5.5kW or greater? For example, SGD7S-210D or SGD7S-260D?
If so, you may have encountered an unexpected "A.042" alarm at startup, even after initializing drive parameters to defaults.
In a departure from 200V Sigma7 drives and from any SigmaV drives, the larger 400V Sigma7 drives require an external braking resistor network for dynamic braking during emergency stops.
Note that this is entirely separate from the regenerative resistor connected to terminals B1 and B2.
The dynamic braking resistors are connected across the motor power leads, and switched with an external contactor. See section 5.3.3 in the product manual:
https://www.yaskawa.com/downloads/searc ... PS80000180
Guidance for selecting the braking resistors is minimal. Resistance values are clear enough (section 5.3.2 in the manual) but for power dissipation, the only advice is to calculate absorbed energy per emergency stop, and expected number of emergency stop events in the lifetime of the machine, and then "confirm these specifications with the manufacturer of the Resistor."
If you have been through the resistor selection process and wired a braking circuit as described in the Yaskawa product manual, I would be interested in hearing what resistors you selected, and on what basis.
If so, you may have encountered an unexpected "A.042" alarm at startup, even after initializing drive parameters to defaults.
In a departure from 200V Sigma7 drives and from any SigmaV drives, the larger 400V Sigma7 drives require an external braking resistor network for dynamic braking during emergency stops.
Note that this is entirely separate from the regenerative resistor connected to terminals B1 and B2.
The dynamic braking resistors are connected across the motor power leads, and switched with an external contactor. See section 5.3.3 in the product manual:
https://www.yaskawa.com/downloads/searc ... PS80000180
Guidance for selecting the braking resistors is minimal. Resistance values are clear enough (section 5.3.2 in the manual) but for power dissipation, the only advice is to calculate absorbed energy per emergency stop, and expected number of emergency stop events in the lifetime of the machine, and then "confirm these specifications with the manufacturer of the Resistor."
If you have been through the resistor selection process and wired a braking circuit as described in the Yaskawa product manual, I would be interested in hearing what resistors you selected, and on what basis.