F1410HS CNC Project with Acorn
Re: F1410HS CNC Project with Acorn
You should be able to use Acorn screw terminals.
DISCONNECT ENABLE AND ALARM FROM THE DRIVE (Do NOT worry about ALARM or ENABLE at this time. Leave them disconnected from the drive. As I mentioned previously, on your inputs, take out DRIVE FAULT from the input for now.)
CONNECT:
+5VDC to +PUL (+5VDC is provided on the Acorn power supply)
+5VDC to +DIR (+5VDC is provided on the Acorn Power supply)
-PUL to ST1 on Acorn Header
-DIR to DR 1 on Acorn Header
Connect your stepper motor power supply to the drive.
One drive, one motor only
When you power up Acorn, your drive and motor is the motor rotor locked or FREE (after doing the wiring suggested above)?
LorenzoRR
Post by LorenzoRR »
martyscncgarage wrote: Sat Jun 13, 2020 2:14 pm You should be able to use Acorn screw terminals.
CONNECT:
Hi,
Following that wiring with 5V from acorn PS, axle is locked. I cannot rotate it.
After that I have launched CNC12, removed Drive OK from IN5 in the wizard and motor rotates. Works fine both JOG and INCREMENTAL (x1, x10 and x100).
Why you think it does not work with ENA? What would be next steps?
Thanks very much for your help!
Lorenzo
Lorenzo
Prototyping with: EMCO CT60, Klipfeld K120 and Wabeco F1210HS
HFS Suspension
You are saying you are able to rotate the motor now with CNC 12, jog foward backward etc?
IF so:
Now to wire ENA:
+ENA to +5VDC
-ENA to Acorn Header ENA1
Only do this for now.
IF the motor does NOT now rotate when you try and jog with CNC12 jog panel, then go into Wizard ADVANCED tab and under Axis 1, IF the ENA box is checked, UNcheck it, if it is NOT checked, then CHECK it.
Shut down CNC12 , restart CNC 12 and then see if the motor Jogs with CNC12 jog panel.
LorenzoRR
Post by LorenzoRR »
martyscncgarage wrote: Sun Jun 14, 2020 3:37 pm You are saying you are able to rotate the motor now with CNC 12, jog foward backward etc?
IF so:
Now to wire ENA:
+ENA to +5VDC
Hello,
I have connected +ENA +5VCD and -ENA to terminal ENA1, and motor moves correctly in both directions.
Reminder: IN5 is not enabled as "axis 1 drive OK" in the wizard, as it was disabled in previous tests.
Should I turn it on? or maybe other tests.
Thanks!
Lorenzo
Lorenzo
HFS Suspension
LorenzoRR wrote: Mon Jun 15, 2020 8:31 am
IF so:
Now to wire ENA:
+ENA to +5VDC
Hello,
Thanks!
Lorenzo
OK
Now connect +Alarm to input 5 and -Alarm to Acorn power supply common.
Make input 5 DRIVE Alarm.
Write settings, exit CNC12 and restart CNC12
IF when you try and move the motor you can DRIVE FAULT! then go into the wizard and on Input 5 click the number 5 to change it state to RED (normally open) Write settings to save your changes. Exit CNC12 and then restart and retry.
If this works with the first drive, then wire up the second drive, set it up exactly the same as the first and test it. When second drive is done, then do the third drive.
Point is, TEST each system you work on AS YOU GO, not when you are all wired and done. Its far easier to figure out when something is not right as you go...
LorenzoRR
Post by LorenzoRR »
Will do, thanks very much Marty.
I am also fighting with the inductive sensor.
It is a NC NPN/PNP and I have to wire it as NPN.
Will also check with 1 axis first and then one by one the rest.
Lorenzo
Lorenzo
HFS Suspension
LorenzoRR wrote: Mon Jun 15, 2020 9:21 am Will do, thanks very much Marty.
Lorenzo
Never heard of a sensor that is both NPN and PNP. Provide picture, part number and link to the data sheet.
Do it right, simply get NPN NC sensors. They are not terribly expensive.
LorenzoRR
Post by LorenzoRR »
martyscncgarage wrote: Mon Jun 15, 2020 9:22 am
Lorenzo
Hi:
- picture
- data sheet:
Sensor-NC-NPN-8mm-IFM_IE5349-01_ES-ES.pdf
(181.27 KiB) Downloaded 92 times
Supplier told me that using the three wires is PNP and with two wires configuration it is NPN.
OEM is IFM from Germany; this is link from supplier here in Europe: https://www.automation24.es/sensor-indu ... 03bbskg-as
Lorenzo
HFS Suspension
LorenzoRR
Post by LorenzoRR »
Sorry, now TDS in english.
Sensor-IE5349-01_EN-GB.pdf
(178.29 KiB) Downloaded 147 times
Lorenzo
HFS Suspension
LorenzoRR wrote: Mon Jun 15, 2020 10:04 am
Lorenzo
Hi:
- picture
- data sheet: Sensor-NC-NPN-8mm-IFM_IE5349-01_ES-ES.pdf
You will have to validate that.
I doubt they will work in series like that as NPN