325 Limit Error? <resolved>
Re: 325 Limit Error?
RGSparber wrote: Sun Dec 19, 2021 11:46 am ........The VFD is optically connected to the breakout board which connects to the parallel port.
What, what? The VFD connects to the Acorn directly for the 0-10v signal and also to the relay board for various connections. The VDF does not connect to a breakout board or the parallel port. Pics would be very helpful to see what's goin on here.
RGSparber
CNC Control System Serial Number: 38D269533454-0111180523
Post by RGSparber »
martyscncgarage wrote: Sun Dec 19, 2021 12:00 pm Rick,
Could you please just post a current picture of your control cabinet showing Acorn here.
So you disconnected your home sensors and the fault still occurred? What is still connected to the inputs and outputs of Acorn?
Could you please also post a current fresh report.
What kind of drives are you using? Connected to DB25 (5V logic drives) or the Acorn header terminals, 24V logic drives.
My Acorn is in one box and the rest of my electronics is in a separate box. They are connected together with the parallel port cable.
Yes, I disconnected all three home sensors plus their 24V and COM connections and still got the fault. At the moment, only the parallel port cable is connected.
I am using DQ542MA motor drivers which connect to a breakout board that connects to the DB25. There is optical isolation in the driver inputs but not in the break out board. Technically, this BOB has optos, but they tied both the input and outputs to board ground. Close but no cigar.
Thanks for your help.
Rick
report_38D269533454-0111180523_2021-12-19_10-16-17.zip
(667.2 KiB) Downloaded 52 times
I would remove that opto board you have on the end of the DB25. Acorn takes care of this.
Since there are 5 inputs on the DB25, you can have something coming back on the DB25
Replace with a standard DB25 breakout board like this:
Avanexpress DB25 Breakout Connector D-sub Breakout 25 Pin Connector Female with Nut (Pack of 2)
by Twinkle Bay
Learn more: https://www.amazon.com/dp/B074387N6B/re ... TGYXW7YXFV
You were using the breakout board for the home switch inputs as well?
You should wire them directly to Acorn.
As you should also wire the VFD through a relay board on that old Acorn board like this one: https://www.mdfly.com/products/6-channe ... g-npn.html
Unplug that DB25 cable and run your program and see if you have anymore faults.
I think you are overcomplicating things using that breakout board. There is NO need for it.
Also, you still have probe tripped messages in your log file (F7 Utility, F9 Logs, F1 Errors)
YOU DID DISCONNECT AND REMOVE IT FROM THE INPUTS CORRECT?
(1) 12-19-2021 8:36:15 CNC12 Acorn Mill v4.64
(4) 12-19-2021 8:36:16 9033 Reset Initiated, Press Reset to Clear
(4) 12-19-2021 8:37:06 8040 WARNING: PROBE TRIPPED
(1) 12-19-2021 8:37:55 Tool change: T1 1/4" end mill
(4) 12-19-2021 8:44:42 9033 Reset Initiated, Press Reset to Clear
(4) 12-19-2021 8:44:42 8040 WARNING: PROBE TRIPPED
(1) 12-19-2021 8:45:04 Tool change: T1 1/4" end mill
(1) 12-19-2021 8:45:06 303 Paused...
(4) 12-19-2021 9:12:53 9033 Reset Initiated, Press Reset to Clear
(4) 12-19-2021 9:12:54 8040 WARNING: PROBE TRIPPED
(1) 12-19-2021 9:13:43 Exiting CNC and shutting down machine (68)
(1) 12-19-2021 10:15:54 199 CNC Started
(1) 12-19-2021 10:16:01 CNC12 Acorn Mill v4.64
(4) 12-19-2021 10:16:01 9033 Reset Initiated, Press Reset to Clear
(1) 12-19-2021 10:16:17 Creating report...
Updated Acorn documentation including an installation manual can be found here:
RGSparber
Post by RGSparber »
martyscncgarage wrote: Sun Dec 19, 2021 1:22 pm I would remove that opto board you have on the end of the DB25. Acorn takes care of this.
by Twinkle Bay
Unplug that DB25 cable and run your program and see if you have any more faults.
The BOB was left over from when I ran Mach3. One attraction to using the Acorn was that I could just plug this hardware into it without modifying my existing hardware. I agree that the board doesn't do much except physically terminate the DB25, but do you think it might be the root cause of my problem? On a new build, I certainly would not use it.
My home sensors connected directly to my Acorn until this morning, when I disconnected them to see if they could be the root cause.
I'm not controlling my VFD from CNC12 although I do have an optically isolated path to the Forward/Run input. Subsequent to this design, I have found that the VFD also optically isolates its inputs. I can disconnect this cable if you think it might be the problem.
Recall that with the spindle not running but the VFD powered on, I do not get any faults.
Rick
Use the relay board I suggested for your outputs, then use the dry to control your VFD inputs. You may wire the Spindle Analog output from Acorn directly the 0-10VDC analog input on the VFD. Acorn supplies this analog signal. Do away with the Mach BOB. Use the inexpensive DB25 breakout board to connect your stepper drives. Its years proven and it works.
Gary Campbell
Post by Gary Campbell »
Did you assume that, or did you read it here? Very few if any knowledgeable guys would steer you in that direction
Gary Campbell wrote: Sun Dec 19, 2021 2:00 pm
Gary, he has one of the older Acorn boards. We were saying unplug from A parallel port and plug into Acorn. It still holds true to a certain extent, however, my hunch is that old breakout board maybe causing his problem.
If he unplugs his DB25 cable and reruns his program(bench test) and there no more problem, then that could point to that old break out board causing it.
RGSparber
Post by RGSparber »
Marty,
The Avanexpress DB25 Breakout Connectors should arrive tomorrow. Unfortunately, house guests arrive at the same time so it might be a few days before I can make the change.
Since I have no plans to control my VFD from CNC12, I'll just remove the existing circuit. Without this functionality, is there still a need to buy the relay board?
Update: I cut the cable from the VFD to the BOB at the BOB end and ran the program. I got the fault in under 2 minutes. Too bad, that sure would have been a nice fix.
Rick