Re: Faraday tape/ copper tape for EMI shielding encoder cable
Posted: Sun Jul 03, 2022 12:09 pm
For my encoders I have only solderd the shielding from the original cable to the DB9 metal part. Works fine.
Uwe
Uwe
Having worked for a building automation company for almost 20 years we tried the ground issue both ways! If both ends of the wire hook to a until with the same ground potential, then grounding both ends is OK. However, we found that anything that had separate power circuits never had 0 ground potential between the two points.tblough wrote: ↑Sun Jul 03, 2022 11:16 am Connecting one end or both of the shield borders on religion for some. Crusades and jihads have been waged on this topic and a gathering of 10 experts will get three different majority decisions.
Personally, I connect the shield at the end where the signal originates for control signals (I.e. currents that are affected by noise) and both ends of power leads (I.e. noise generators). Your mileage may vary.
However, as previously mentioned an ounce of prevention is worth a pound of cure. Find the cause of the interference and fix that.
Single point ground is the best way! (All ground wires to one grounding point or buss bar) Just make sure the backplane has a post with no paint, or use a bare spot, because the paint itself presents itself as a capacitor and changes the ground potential.