Are you using the contactor as an Estop Contactor?
You will want a contactor with DC voltage contact ratings. I would run both the DC- and the DC+ across a contact.
Eaton Moeller DIL or XTC series contactors are good, Schneider Telemecanique LC1DT series, etc....
20Amp contact rating would be fine.
Just remember to look at the coil voltage you intend to use. I would recommend 24VDC....
Hope that helps
Marty
Reminder, for support please follow this post: viewtopic.php?f=20&t=383
We can't "SEE" what you see...
Mesa, AZ
(Note: Liking will "up vote" a post in the search results helping others find good information faster)
tuffduck wrote: ↑Wed Apr 14, 2021 9:49 pm
I would like to use this as an estop contactor to shut down the spindle and steppers but leave acorn running, so that I can resume a program. Thanks
Look at the Acorn SYSTEM schematic in the Acorn Schematic set. It shows what you are wanting to accomplish