Machine Stopping Mid Program! <flaky limits and bad coms>
Malachilee
CNC Control System Serial Number: 98F07B936216-0504237156
Re: Machine Stopping Mid Program!
Post by Malachilee »
CentroidFrog wrote: Mon Sep 08, 2025 8:59 am Related reading for troubleshooting comm errors:
viewtopic.php?t=1451
Thanks for posting all of these. I did find a few settings that were not correct. However, correcting them did not help with my issue. The program still just ends abruptly, and I get notifications of limits being tripped and cleared.
-Lee
New River, AZ
So, assuming you are not actually tripping any of your limit switches with axis movement, you need to find out why Acorn sees the limit switch input tripped (open).
Most likely you have a loose connection somewhere in the limit switch / INP2 chain, so that machine vibration causes it to open momentarily. Or you could have a weak limit switch that is opening momentarily with vibration.
It is also possible, but much less likely, that RF noise from your spindle drive is causing a false signal.
Try running the same job, but with the Z axis part zero (WCS zero) set just high enough that the cutter does not actually touch the workpiece. Does it still stop with false "Limit tripped" errors?
Malachilee
It is not tripping the switches from axis movements. It was running parts all week, and then I switched to OP 2, and this started happening. I will double-check the wires and see if something came loose. As for running it without engaging the cutter, it now does it when trying to move to the tool change position at the start of the program. However, I am able to jog all axis without issues.
-Lee
New River, AZ
Malachilee
cncsnw wrote: Mon Sep 08, 2025 12:24 pm So, assuming you are not actually tripping any of your limit switches with axis movement, you need to find out why Acorn sees the limit switch input tripped (open).
Okay, I checked all the connections, and nothing seems to be loose. I was able to run the program and shake all the wires, and nothing happened. It wasn't until I thought it was working again and sat down that it stopped, just like before. I don't think it's a wire connection. I even brought up the PLC diagnostics screen and physically triggered all the limit switches to verify they were working correctly. Even on that screen, shaking the wires didn't trip the green to red.
-Lee
New River, AZ
Did you try to post the gcode without the tool preload function?
Malachilee
suntravel wrote: Mon Sep 08, 2025 4:36 pm Did you try to post the gcode without the tool preload function?
Yeah, I switched it off when posting, and it didn't fix the offset having a different number. It still shows T2 H1.
-Lee
New River, AZ
Is it possible to post the fusion file?
This is how it is if I post from fusion
(File:  1001.nc)
(T3 D=6.000 CR=0.000 - ZMIN=-20.000 - right hand tap)
N10 G90 G94 G17
N15 G21
(Material Size MinMax for CNC12 V5.40 Graphing and Run Time Graphics)
:::: X- = 0.000, X+ = 100.000
:::: Y- = 0.000, Y+ = 30.000
:::: Z- = -20.000, Z+ = 0.000
N20 G28 G91 Z0.000
N25 G90
N30
(Drill1)
N35 T3 M6
N40 S500 M3
N45 G17 G90 G94
N50 G54
N55 G0 X10.000 Y15.000
N60 G43 Z15.000 H3
N65 G0 Z5.000
N70 G98 G84 X10.000 Y15.000 Z-20.000 R5.000 P1. Q1.
N75 X50.000
N80 X90.000
N85 G80
N90 Z15.000
N95 G28 G91 Z0.000
N100 G90
N105 G28 G91 X0.000 Y0.000
N110 G90
N115 M5
N120 M30
UWe
Have you looked at your error log in your report that you posted? There's no way this machine will cut reliably.
(4)   09-05-2025 12:55:50 946 PC resending # 43162
(1)   09-05-2025 12:55:55 452 Ethernet Communication Error, See Tech Bulletin 270
(4)   09-05-2025 12:56:12 944 MPU requested resend # 9933
(4)   09-05-2025 12:56:12 946 PC resending # 43217
(4)   09-05-2025 12:56:12 946 PC resending # 43224
(4)   09-05-2025 12:56:12 944 MPU requested resend # 9934
(4)   09-05-2025 12:56:12 946 PC resending # 43251
(4)   09-05-2025 12:56:12 946 PC resending # 43263
(4)   09-05-2025 12:56:14 944 MPU requested resend # 9935
(4)   09-05-2025 12:56:14 946 PC resending # 43265
(4)   09-05-2025 12:56:15 944 MPU requested resend # 9936
(4)   09-05-2025 12:56:15 946 PC resending # 43267
(4)   09-05-2025 12:56:51 944 MPU requested resend # 9937
(4)   09-05-2025 12:56:51 946 PC resending # 43269
(4)   09-05-2025 12:57:11 944 MPU requested resend # 9938
(4)   09-05-2025 12:57:11 946 PC resending # 43272
(4)   09-05-2025 12:57:20 944 MPU requested resend # 9939
(4)   09-05-2025 12:57:20 946 PC resending # 43274
(4)   09-05-2025 12:57:52 944 MPU requested resend # 9940
(4)   09-05-2025 12:57:52 944 MPU requested resend # 9941
(4)   09-05-2025 12:57:52 946 PC resending # 43320
(4)   09-05-2025 12:57:52 946 PC resending # 43336
(4)   09-05-2025 12:58:32 944 MPU requested resend # 9942
(4)   09-05-2025 12:58:32 946 PC resending # 43338
(4)   09-05-2025 12:58:36 944 MPU requested resend # 9943
(4)   09-05-2025 12:58:36 946 PC resending # 43340
(4)   09-05-2025 12:59:12 944 MPU requested resend # 9944
(4)   09-05-2025 12:59:12 946 PC resending # 43342
(4)   09-05-2025 12:59:17 944 MPU requested resend # 9945
(4)   09-05-2025 12:59:17 946 PC resending # 43344
(4)   09-05-2025 12:59:29 944 MPU requested resend # 9946
(4)   09-05-2025 12:59:29 946 PC resending # 43346
(4)   09-05-2025 13:00:10 944 MPU requested resend # 9947
(4)   09-05-2025 13:00:10 946 PC resending # 43348
(4)   09-05-2025 13:00:36 944 MPU requested resend # 9948
(4)   09-05-2025 13:00:36 946 PC resending # 43350
(4)   09-05-2025 13:00:42 944 MPU requested resend # 9949
(4)   09-05-2025 13:00:42 946 PC resending # 43352
(4)   09-05-2025 13:00:59 944 MPU requested resend # 9950
(4)   09-05-2025 13:00:59 946 PC resending # 43354
(4)   09-05-2025 13:01:12 944 MPU requested resend # 9951
(4)   09-05-2025 13:01:12 946 PC resending # 43356
(4)   09-05-2025 13:02:01 944 MPU requested resend # 9952
(4)   09-05-2025 13:02:01 946 PC resending # 43358
(4)   09-05-2025 13:02:34 944 MPU requested resend # 9953
(4)   09-05-2025 13:02:34 946 PC resending # 43360
(4)   09-05-2025 13:02:36 944 MPU requested resend # 9954
(4)   09-05-2025 13:02:36 946 PC resending # 43363
(4)   09-05-2025 13:02:48 944 MPU requested resend # 9955
(4)   09-05-2025 13:02:48 946 PC resending # 43365
(4)   09-05-2025 13:02:48 944 MPU requested resend # 9956
(4)   09-05-2025 13:02:48 946 PC resending # 43367
(4)   09-05-2025 13:02:53 944 MPU requested resend # 9957
(4)   09-05-2025 13:02:53 946 PC resending # 43369
(4)   09-05-2025 13:03:17 944 MPU requested resend # 9958
(4)   09-05-2025 13:03:17 946 PC resending # 43371
(4)   09-05-2025 13:03:33 944 MPU requested resend # 9959
(4)   09-05-2025 13:03:33 946 PC resending # 43373
(4)   09-05-2025 13:04:13 944 MPU requested resend # 9960
(4)   09-05-2025 13:04:13 946 PC resending # 43375
(4)   09-05-2025 13:04:22 944 MPU requested resend # 9961
(4)   09-05-2025 13:04:22 946 PC resending # 43418
(4)   09-05-2025 13:04:30 944 MPU requested resend # 9962
(4)   09-05-2025 13:04:30 946 PC resending # 43420
(4)   09-05-2025 13:04:33 944 MPU requested resend # 9963
(4)   09-05-2025 13:04:33 946 PC resending # 43422
(4)   09-05-2025 13:04:55 944 MPU requested resend # 9964
(4)   09-05-2025 13:04:55 946 PC resending # 43424
(4)   09-05-2025 13:05:07 944 MPU requested resend # 9965
(4)   09-05-2025 13:05:07 946 PC resending # 43426
(4)   09-05-2025 13:05:09 944 MPU requested resend # 9966
(4)   09-05-2025 13:05:09 946 PC resending # 43430
(4)   09-05-2025 13:05:23 944 MPU requested resend # 9967
(4)   09-05-2025 13:05:23 946 PC resending # 43432
(4)   09-05-2025 13:05:42 944 MPU requested resend # 9968
(4)   09-05-2025 13:05:42 946 PC resending # 43434
(4)   09-05-2025 13:06:18 944 MPU requested resend # 9969
(4)   09-05-2025 13:06:18 946 PC resending # 43436
(4)   09-05-2025 13:06:23 944 MPU requested resend # 9970
(4)   09-05-2025 13:06:23 946 PC resending # 43438
(4)   09-05-2025 13:06:38 944 MPU requested resend # 9971
(4)   09-05-2025 13:06:38 946 PC resending # 43440
(4)   09-05-2025 13:06:44 944 MPU requested resend # 9972
(4)   09-05-2025 13:06:44 946 PC resending # 43442
(4)   09-05-2025 13:06:46 944 MPU requested resend # 9973
(4)   09-05-2025 13:06:46 946 PC resending # 43444
(4)   09-05-2025 13:06:57 944 MPU requested resend # 9974
(4)   09-05-2025 13:06:57 946 PC resending # 43446
(4)   09-05-2025 13:07:06 944 MPU requested resend # 9975
(4)   09-05-2025 13:07:06 946 PC resending # 43475
(4)   09-05-2025 13:07:06 946 PC resending # 43508
(4)   09-05-2025 13:07:24 944 MPU requested resend # 9976
(4)   09-05-2025 13:07:24 946 PC resending # 43510
(4)   09-05-2025 13:07:34 944 MPU requested resend # 9977
(4)   09-05-2025 13:07:34 946 PC resending # 43512
(4)   09-05-2025 13:07:50 944 MPU requested resend # 9978
(4)   09-05-2025 13:07:50 946 PC resending # 43514
(4)   09-05-2025 13:08:29 944 MPU requested resend # 9979
(4)   09-05-2025 13:08:29 946 PC resending # 43516
(4)   09-05-2025 13:08:34 944 MPU requested resend # 9980
(4)   09-05-2025 13:08:34 946 PC resending # 43573
(4)   09-05-2025 13:08:34 944 MPU requested resend # 9981
(4)   09-05-2025 13:08:34 946 PC resending # 43615
(4)   09-05-2025 13:08:49 944 MPU requested resend # 9982
(4)   09-05-2025 13:08:49 946 PC resending # 43617
(4)   09-05-2025 13:09:14 944 MPU requested resend # 9983
(4)   09-05-2025 13:09:14 946 PC resending # 43621
(4)   09-05-2025 13:09:39 944 MPU requested resend # 9984
(4)   09-05-2025 13:09:39 946 PC resending # 43632
(4)   09-05-2025 13:10:22 944 MPU requested resend # 9985
(4)   09-05-2025 13:10:22 946 PC resending # 43634
(4)   09-05-2025 13:10:27 944 MPU requested resend # 9986
(4)   09-05-2025 13:10:27 946 PC resending # 43636
(4)   09-05-2025 13:10:44 944 MPU requested resend # 9987
(4)   09-05-2025 13:10:44 946 PC resending # 43680
(4)   09-05-2025 13:11:32 944 MPU requested resend # 9988
(4)   09-05-2025 13:11:33 946 PC resending # 43682
(4)   09-05-2025 13:11:42 944 MPU requested resend # 9989
(4)   09-05-2025 13:11:42 946 PC resending # 43684
(4)   09-05-2025 13:11:49 944 MPU requested resend # 9990
(4)   09-05-2025 13:11:49 946 PC resending # 43686
(4)   09-05-2025 13:12:01 944 MPU requested resend # 9991
(4)   09-05-2025 13:12:01 946 PC resending # 43688
(4)   09-05-2025 13:12:30 944 MPU requested resend # 9992
(4)   09-05-2025 13:12:30 946 PC resending # 43697
(4)   09-05-2025 13:12:38 944 MPU requested resend # 9993
(4)   09-05-2025 13:12:38 946 PC resending # 43699
(4)   09-05-2025 13:12:49 944 MPU requested resend # 9994
(4)   09-05-2025 13:12:49 946 PC resending # 43701
(4)   09-05-2025 13:13:20 944 MPU requested resend # 9995
(4)   09-05-2025 13:13:20 946 PC resending # 43728
(4)   09-05-2025 13:13:20 946 PC resending # 43757
(4)   09-05-2025 13:13:29 944 MPU requested resend # 9996
(4)   09-05-2025 13:13:29 946 PC resending # 43759
(4)   09-05-2025 13:13:37 944 MPU requested resend # 9997
(4)   09-05-2025 13:13:37 946 PC resending # 43761
(4)   09-05-2025 13:13:40 944 MPU requested resend # 9998
(4)   09-05-2025 13:13:40 946 PC resending # 43763
(4)   09-05-2025 13:13:45 944 MPU requested resend # 9999
(4)   09-05-2025 13:13:45 946 PC resending # 43765
(4)   09-05-2025 13:13:53 944 MPU requested resend # 10000
(4)   09-05-2025 13:13:53 946 PC resending # 43767
(4)   09-05-2025 13:14:05 944 MPU requested resend # 10001
(4)   09-05-2025 13:14:05 946 PC resending # 43794
(4)   09-05-2025 13:14:05 946 PC resending # 43815
(4)   09-05-2025 13:14:06 944 MPU requested resend # 10002
(4)   09-05-2025 13:14:06 944 MPU requested resend # 10003
(4)   09-05-2025 13:14:06 946 PC resending # 43856
(4)   09-05-2025 13:14:06 946 PC resending # 43868
(4)   09-05-2025 13:14:20 944 MPU requested resend # 10004
(4)   09-05-2025 13:14:20 946 PC resending # 43870
(4)   09-05-2025 13:15:16 944 MPU requested resend # 10005
(4)   09-05-2025 13:15:17 946 PC resending # 43872
(4)   09-05-2025 13:15:26 944 MPU requested resend # 10006
(4)   09-05-2025 13:15:26 946 PC resending # 43899
(4)   09-05-2025 13:15:26 946 PC resending # 43923
(4)   09-05-2025 13:15:26 944 MPU requested resend # 10007
(4)   09-05-2025 13:15:26 946 PC resending # 43967
(4)   09-05-2025 13:15:30 944 MPU requested resend # 10008
(4)   09-05-2025 13:15:30 946 PC resending # 43969
(4)   09-05-2025 13:15:40 944 MPU requested resend # 10009
(4)   09-05-2025 13:15:40 946 PC resending # 43971
(4)   09-05-2025 13:16:23 944 MPU requested resend # 10010
(4)   09-05-2025 13:16:23 946 PC resending # 43973
(4)   09-05-2025 13:16:53 944 MPU requested resend # 10011
(4)   09-05-2025 13:16:53 946 PC resending # 43975
(4)   09-05-2025 13:17:03 944 MPU requested resend # 10012
(4)   09-05-2025 13:17:03 946 PC resending # 43979
(4)   09-05-2025 13:17:15 944 MPU requested resend # 10013
(4)   09-05-2025 13:17:15 946 PC resending # 43981
(4)   09-05-2025 13:17:28 944 MPU requested resend # 10014
(4)   09-05-2025 13:17:28 946 PC resending # 43983
(4)   09-05-2025 13:17:28 944 MPU requested resend # 10015
(4)   09-05-2025 13:17:28 946 PC resending # 43985
(4)   09-05-2025 13:17:35 944 MPU requested resend # 10016
(4)   09-05-2025 13:17:35 946 PC resending # 43987
(4)   09-05-2025 13:18:24 944 MPU requested resend # 10017
(4)   09-05-2025 13:18:24 946 PC resending # 43989
(4)   09-05-2025 13:18:33 944 MPU requested resend # 10018
(4)   09-05-2025 13:18:33 946 PC resending # 43991
(4)   09-05-2025 13:18:35 944 MPU requested resend # 10019
(4)   09-05-2025 13:18:35 946 PC resending # 43995
(4)   09-05-2025 13:18:38 944 MPU requested resend # 10020
(4)   09-05-2025 13:18:38 946 PC resending # 43997
(4)   09-05-2025 13:18:40 944 MPU requested resend # 10021
(4)   09-05-2025 13:18:40 946 PC resending # 43998
(4)   09-05-2025 13:18:40 946 PC resending # 43999
(4)   09-05-2025 13:18:46 944 MPU requested resend # 10022
(4)   09-05-2025 13:18:46 946 PC resending # 44001
(4)   09-05-2025 13:19:48 944 MPU requested resend # 10023
(4)   09-05-2025 13:19:48 946 PC resending # 44003
(4)   09-05-2025 13:20:01 944 MPU requested resend # 10024
(4)   09-05-2025 13:20:02 946 PC resending # 44005
(4)   09-05-2025 13:20:21 944 MPU requested resend # 10025
(4)   09-05-2025 13:20:21 946 PC resending # 44007
(4)   09-05-2025 13:20:35 944 MPU requested resend # 10026
(4)   09-05-2025 13:20:35 946 PC resending # 44009
(4)   09-05-2025 13:20:39 944 MPU requested resend # 10027
(4)   09-05-2025 13:20:39 946 PC resending # 44011
(4)   09-05-2025 13:21:31 944 MPU requested resend # 10028
(4)   09-05-2025 13:21:31 946 PC resending # 44013
(4)   09-05-2025 13:21:42 944 MPU requested resend # 10029
(4)   09-05-2025 13:21:42 946 PC resending # 44015
(4)   09-05-2025 13:21:43 944 MPU requested resend # 10030
(4)   09-05-2025 13:21:43 946 PC resending # 44017
(4)   09-05-2025 13:21:48 944 MPU requested resend # 10031
(4)   09-05-2025 13:21:48 946 PC resending # 44019
(4)   09-05-2025 13:22:10 944 MPU requested resend # 10032
(4)   09-05-2025 13:22:10 946 PC resending # 44021
(4)   09-05-2025 13:22:51 944 MPU requested resend # 10033
(4)   09-05-2025 13:22:51 946 PC resending # 44048
(4)   09-05-2025 13:22:51 946 PC resending # 44081
(4)   09-05-2025 13:22:52 944 MPU requested resend # 10034
(4)   09-05-2025 13:22:52 946 PC resending # 44126
(4)   09-05-2025 13:22:52 944 MPU requested resend # 10035
(4)   09-05-2025 13:22:52 946 PC resending # 44155
(4)   09-05-2025 13:22:52 946 PC resending # 44169
(4)   09-05-2025 13:22:52 944 MPU requested resend # 10036
(4)   09-05-2025 13:22:52 946 PC resending # 44213
(4)   09-05-2025 13:23:10 944 MPU requested resend # 10037
(4)   09-05-2025 13:23:10 946 PC resending # 44215
(4)   09-05-2025 13:23:10 944 MPU requested resend # 10038
(4)   09-05-2025 13:23:10 946 PC resending # 44217
(4)   09-05-2025 13:23:34 944 MPU requested resend # 10039
(4)   09-05-2025 13:23:34 946 PC resending # 44223
(4)   09-05-2025 13:23:42 944 MPU requested resend # 10040
(4)   09-05-2025 13:23:42 946 PC resending # 44279
(4)   09-05-2025 13:23:43 944 MPU requested resend # 10041
(4)   09-05-2025 13:23:43 946 PC resending # 44281
(4)   09-05-2025 13:23:46 944 MPU requested resend # 10042
(4)   09-05-2025 13:23:47 946 PC resending # 44283
(4)   09-05-2025 13:24:04 944 MPU requested resend # 10043
(4)   09-05-2025 13:24:04 946 PC resending # 44338
(4)   09-05-2025 13:24:04 946 PC resending # 44342
(4)   09-05-2025 13:24:11 944 MPU requested resend # 10044
(4)   09-05-2025 13:24:11 946 PC resending # 44344
(4)   09-05-2025 13:24:12 944 MPU requested resend # 10045
(4)   09-05-2025 13:24:12 946 PC resending # 44346
(4)   09-05-2025 13:24:18 944 MPU requested resend # 10046
(4)   09-05-2025 13:24:18 946 PC resending # 44387
(4)   09-05-2025 13:24:27 944 MPU requested resend # 10047
(4)   09-05-2025 13:24:27 946 PC resending # 44389
(4)   09-05-2025 13:25:08 944 MPU requested resend # 10048
(4)   09-05-2025 13:25:08 946 PC resending # 44391
(4)   09-05-2025 13:25:30 944 MPU requested resend # 10049
(4)   09-05-2025 13:25:30 946 PC resending # 44416
(4)   09-05-2025 13:26:05 944 MPU requested resend # 10050
(4)   09-05-2025 13:26:05 946 PC resending # 44418
(4)   09-05-2025 13:26:17 944 MPU requested resend # 10051
(4)   09-05-2025 13:26:17 946 PC resending # 44420
(4)   09-05-2025 13:26:18 944 MPU requested resend # 10052
(4)   09-05-2025 13:26:18 946 PC resending # 44422
(4)   09-05-2025 13:26:21 944 MPU requested resend # 10053
(4)   09-05-2025 13:26:21 946 PC resending # 44427
(4)   09-05-2025 13:26:34 944 MPU requested resend # 10054
(4)   09-05-2025 13:26:34 946 PC resending # 44458
(4)   09-05-2025 13:26:36 944 MPU requested resend # 10055
(4)   09-05-2025 13:26:36 946 PC resending # 44460
(4)   09-05-2025 13:26:46 944 MPU requested resend # 10056
(4)   09-05-2025 13:26:46 946 PC resending # 44462
(4)   09-05-2025 13:27:03 944 MPU requested resend # 10057
(4)   09-05-2025 13:27:03 946 PC resending # 44521
(4)   09-05-2025 13:27:33 944 MPU requested resend # 10058
(4)   09-05-2025 13:27:33 946 PC resending # 44550
(4)   09-05-2025 13:27:33 946 PC resending # 44581
(4)   09-05-2025 13:28:24 944 MPU requested resend # 10059
(4)   09-05-2025 13:28:24 946 PC resending # 44628
(4)   09-05-2025 13:28:32 944 MPU requested resend # 10060
(4)   09-05-2025 13:28:32 946 PC resending # 44630
(4)   09-05-2025 13:28:44 944 MPU requested resend # 10061
(4)   09-05-2025 13:28:44 946 PC resending # 44637
(4)   09-05-2025 13:28:44 944 MPU requested resend # 10062
(4)   09-05-2025 13:28:44 946 PC resending # 44650
(4)   09-05-2025 13:28:53 944 MPU requested resend # 10063
(4)   09-05-2025 13:28:53 946 PC resending # 44677
(4)   09-05-2025 13:28:53 946 PC resending # 44706
(4)   09-05-2025 13:28:53 944 MPU requested resend # 10064
(4)   09-05-2025 13:28:53 946 PC resending # 44757
(4)   09-05-2025 13:29:10 944 MPU requested resend # 10065
(4)   09-05-2025 13:29:10 946 PC resending # 44759
(4)   09-05-2025 13:29:13 944 MPU requested resend # 10066
(4)   09-05-2025 13:29:13 946 PC resending # 44761
(4)   09-05-2025 13:29:23 944 MPU requested resend # 10067
(4)   09-05-2025 13:29:23 946 PC resending # 44796
(4)   09-05-2025 13:29:27 944 MPU requested resend # 10068
(4)   09-05-2025 13:29:27 946 PC resending # 44798
(4)   09-05-2025 13:29:41 944 MPU requested resend # 10069
(4)   09-05-2025 13:29:41 946 PC resending # 44806
(4)   09-05-2025 13:29:42 944 MPU requested resend # 10070
(4)   09-05-2025 13:29:42 946 PC resending # 44808
(4)   09-05-2025 13:29:50 944 MPU requested resend # 10071
(4)   09-05-2025 13:29:50 946 PC resending # 44818
(4)   09-05-2025 13:30:08 944 MPU requested resend # 10072
(4)   09-05-2025 13:30:08 946 PC resending # 44820
(4)   09-05-2025 13:30:21 944 MPU requested resend # 10073
(4)   09-05-2025 13:30:21 946 PC resending # 44821
(4)   09-05-2025 13:30:21 946 PC resending # 44822
(4)   09-05-2025 13:30:26 944 MPU requested resend # 10074
(4)   09-05-2025 13:30:26 946 PC resending # 44824
(4)   09-05-2025 13:30:56 944 MPU requested resend # 10075
(4)   09-05-2025 13:30:56 946 PC resending # 44826
(4)   09-05-2025 13:31:23 944 MPU requested resend # 10076
(4)   09-05-2025 13:31:23 946 PC resending # 44882
(4)   09-05-2025 13:31:34 944 MPU requested resend # 10077
(4)   09-05-2025 13:31:34 946 PC resending # 44884
(4)   09-05-2025 13:31:35 944 MPU requested resend # 10078
(4)   09-05-2025 13:31:35 946 PC resending # 44892
(4)   09-05-2025 13:31:50 944 MPU requested resend # 10079
(4)   09-05-2025 13:31:50 946 PC resending # 44894
(4)   09-05-2025 13:32:13 944 MPU requested resend # 10080
(4)   09-05-2025 13:32:13 946 PC resending # 44899
(4)   09-05-2025 13:32:41 944 MPU requested resend # 10081
(4)   09-05-2025 13:32:41 946 PC resending # 44942
(4)   09-05-2025 13:32:49 944 MPU requested resend # 10082
(4)   09-05-2025 13:32:49 946 PC resending # 44944
(4)   09-05-2025 13:33:03 944 MPU requested resend # 10083
(4)   09-05-2025 13:33:03 946 PC resending # 44946
(4)   09-05-2025 13:33:10 944 MPU requested resend # 10084
(4)   09-05-2025 13:33:10 946 PC resending # 44948
(4)   09-05-2025 13:33:11 944 MPU requested resend # 10085
(4)   09-05-2025 13:33:11 946 PC resending # 44950
(4)   09-05-2025 13:34:05 944 MPU requested resend # 10086
(4)   09-05-2025 13:34:05 946 PC resending # 44952
(4)   09-05-2025 13:34:08 944 MPU requested resend # 10087
(4)   09-05-2025 13:34:08 946 PC resending # 45012
(4)   09-05-2025 13:34:09 944 MPU requested resend # 10088
(4)   09-05-2025 13:34:09 946 PC resending # 45014
(4)   09-05-2025 13:34:10 944 MPU requested resend # 10089
(4)   09-05-2025 13:34:10 946 PC resending # 45016
(4)   09-05-2025 13:34:15 944 MPU requested resend # 10090
(4)   09-05-2025 13:34:15 946 PC resending # 45018
(4)   09-05-2025 13:34:25 944 MPU requested resend # 10091
(4)   09-05-2025 13:34:25 946 PC resending # 45020
(4)   09-05-2025 13:34:31 944 MPU requested resend # 10092
(4)   09-05-2025 13:34:31 946 PC resending # 45083
(4)   09-05-2025 13:34:34 944 MPU requested resend # 10093
(4)   09-05-2025 13:34:34 946 PC resending # 45085
(4)   09-05-2025 13:34:36 944 MPU requested resend # 10094
(4)   09-05-2025 13:34:36 946 PC resending # 45087
(4)   09-05-2025 13:34:43 944 MPU requested resend # 10095
(4)   09-05-2025 13:34:43 946 PC resending # 45089
(4)   09-05-2025 13:35:12 944 MPU requested resend # 10096
(4)   09-05-2025 13:35:12 946 PC resending # 45091
(4)   09-05-2025 13:35:24 944 MPU requested resend # 10097
(4)   09-05-2025 13:35:24 946 PC resending # 45093
(4)   09-05-2025 13:35:26 944 MPU requested resend # 10098
(4)   09-05-2025 13:35:26 946 PC resending # 45095
(4)   09-05-2025 13:35:54 944 MPU requested resend # 10099
(4)   09-05-2025 13:35:54 946 PC resending # 45105
(4)   09-05-2025 13:36:11 944 MPU requested resend # 10100
(4)   09-05-2025 13:36:11 946 PC resending # 45107
(4)   09-05-2025 13:36:15 944 MPU requested resend # 10101
(4)   09-05-2025 13:36:15 946 PC resending # 45109
(4)   09-05-2025 13:36:22 944 MPU requested resend # 10102
(4)   09-05-2025 13:36:22 946 PC resending # 45138
(4)   09-05-2025 13:36:22 946 PC resending # 45146
(4)   09-05-2025 13:36:34 944 MPU requested resend # 10103
(4)   09-05-2025 13:36:34 946 PC resending # 45148
(4)   09-05-2025 13:36:39 944 MPU requested resend # 10104
(4)   09-05-2025 13:36:39 946 PC resending # 45170
(4)   09-05-2025 13:36:45 944 MPU requested resend # 10105
(4)   09-05-2025 13:36:45 946 PC resending # 45173
(4)   09-05-2025 13:36:45 944 MPU requested resend # 10106
(4)   09-05-2025 13:36:45 946 PC resending # 45191
(4)   09-05-2025 13:36:50 944 MPU requested resend # 10107
(4)   09-05-2025 13:36:50 946 PC resending # 45236
(4)   09-05-2025 13:36:58 944 MPU requested resend # 10108
(4)   09-05-2025 13:36:58 946 PC resending # 45285
(4)   09-05-2025 13:37:20 944 MPU requested resend # 10109
(4)   09-05-2025 13:37:20 946 PC resending # 45287
(4)   09-05-2025 13:37:29 944 MPU requested resend # 10110
(4)   09-05-2025 13:37:29 946 PC resending # 45289
(4)   09-05-2025 13:37:33 944 MPU requested resend # 10111
(4)   09-05-2025 13:37:33 946 PC resending # 45342
(4)   09-05-2025 13:37:57 944 MPU requested resend # 10112
(4)   09-05-2025 13:37:58 946 PC resending # 45344
(4)   09-05-2025 13:38:03 944 MPU requested resend # 10113
(4)   09-05-2025 13:38:03 946 PC resending # 45346
(4)   09-05-2025 13:38:04 944 MPU requested resend # 10114
(4)   09-05-2025 13:38:04 946 PC resending # 45348
(4)   09-05-2025 13:38:08 944 MPU requested resend # 10115
(4)   09-05-2025 13:38:08 946 PC resending # 45350
(4)   09-05-2025 13:38:23 944 MPU requested resend # 10116
(4)   09-05-2025 13:38:23 946 PC resending # 45352
(4)   09-05-2025 13:38:48 944 MPU requested resend # 10117
(4)   09-05-2025 13:38:48 946 PC resending # 45412
(4)   09-05-2025 13:38:52 944 MPU requested resend # 10118
(4)   09-05-2025 13:38:52 946 PC resending # 45414
(4)   09-05-2025 13:39:24 944 MPU requested resend # 10119
(4)   09-05-2025 13:39:24 946 PC resending # 45416
(4)   09-05-2025 13:39:27 944 MPU requested resend # 10120
(4)   09-05-2025 13:39:27 946 PC resending # 45418
(4)   09-05-2025 13:39:54 944 MPU requested resend # 10121
(4)   09-05-2025 13:39:54 946 PC resending # 45429
(4)   09-05-2025 13:40:21 944 MPU requested resend # 10122
(4)   09-05-2025 13:40:21 946 PC resending # 45484
(4)   09-05-2025 13:40:21 946 PC resending # 45486
(4)   09-05-2025 13:40:22 944 MPU requested resend # 10123
(4)   09-05-2025 13:40:22 946 PC resending # 45488
(4)   09-05-2025 13:40:24 944 MPU requested resend # 10124
(4)   09-05-2025 13:40:24 946 PC resending # 45490
(4)   09-05-2025 13:40:29 944 MPU requested resend # 10125
(4)   09-05-2025 13:40:29 946 PC resending # 45492
(4)   09-05-2025 13:40:31 944 MPU requested resend # 10126
(4)   09-05-2025 13:40:31 946 PC resending # 45494
(4)   09-05-2025 13:40:34 944 MPU requested resend # 10127
(4)   09-05-2025 13:40:34 946 PC resending # 45496
(4)   09-05-2025 13:40:42 944 MPU requested resend # 10128
(4)   09-05-2025 13:40:43 946 PC resending # 45498
(4)   09-05-2025 13:40:54 944 MPU requested resend # 10129
(4)   09-05-2025 13:40:54 946 PC resending # 45500
(4)   09-05-2025 13:41:03 944 MPU requested resend # 10130
(4)   09-05-2025 13:41:03 946 PC resending # 45528
(4)   09-05-2025 13:41:14 944 MPU requested resend # 10131
(4)   09-05-2025 13:41:15 946 PC resending # 45530
(4)   09-05-2025 13:41:44 944 MPU requested resend # 10132
(4)   09-05-2025 13:41:44 946 PC resending # 45532
(4)   09-05-2025 13:41:45 944 MPU requested resend # 10133
(4)   09-05-2025 13:41:45 946 PC resending # 45561
(4)   09-05-2025 13:41:45 946 PC resending # 45589
(4)   09-05-2025 13:41:45 946 PC resending # 45595
(4)   09-05-2025 13:41:47 944 MPU requested resend # 10134
(4)   09-05-2025 13:41:47 946 PC resending # 45597
(4)   09-05-2025 13:42:15 944 MPU requested resend # 10135
(4)   09-05-2025 13:42:15 946 PC resending # 45599
(4)   09-05-2025 13:42:17 944 MPU requested resend # 10136
(4)   09-05-2025 13:42:17 946 PC resending # 45601
(4)   09-05-2025 13:43:05 944 MPU requested resend # 10137
(4)   09-05-2025 13:43:05 946 PC resending # 45603
(4)   09-05-2025 13:43:53 944 MPU requested resend # 10138
(4)   09-05-2025 13:43:53 946 PC resending # 45605
(4)   09-05-2025 13:44:08 944 MPU requested resend # 10139
(4)   09-05-2025 13:44:08 946 PC resending # 45607
(4)   09-05-2025 13:44:14 944 MPU requested resend # 10140
(4)   09-05-2025 13:44:14 946 PC resending # 45609
(4)   09-05-2025 13:44:18 944 MPU requested resend # 10141
(4)   09-05-2025 13:44:18 946 PC resending # 45611
(4)   09-05-2025 13:44:35 944 MPU requested resend # 10142
(4)   09-05-2025 13:44:35 946 PC resending # 45613
(4)   09-05-2025 13:44:40 944 MPU requested resend # 10143
(4)   09-05-2025 13:44:40 946 PC resending # 45615
(4)   09-05-2025 13:44:41 944 MPU requested resend # 10144
(4)   09-05-2025 13:44:41 946 PC resending # 45617
(4)   09-05-2025 13:44:49 944 MPU requested resend # 10145
(4)   09-05-2025 13:44:49 946 PC resending # 45619
(4)   09-05-2025 13:45:00 944 MPU requested resend # 10146
(4)   09-05-2025 13:45:01 946 PC resending # 45621
(4)   09-05-2025 13:45:52 944 MPU requested resend # 10147
(4)   09-05-2025 13:45:52 946 PC resending # 45623
(4)   09-05-2025 13:45:53 944 MPU requested resend # 10148
(4)   09-05-2025 13:45:54 946 PC resending # 45625
(4)   09-05-2025 13:46:20 944 MPU requested resend # 10149
(4)   09-05-2025 13:46:20 946 PC resending # 45627
(4)   09-05-2025 13:47:01 944 MPU requested resend # 10150
(4)   09-05-2025 13:47:01 946 PC resending # 45629
(4)   09-05-2025 13:47:11 944 MPU requested resend # 10151
(4)   09-05-2025 13:47:11 946 PC resending # 45631
(4)   09-05-2025 13:48:21 944 MPU requested resend # 10152
(4)   09-05-2025 13:48:21 946 PC resending # 45633
(4)   09-05-2025 13:48:44 944 MPU requested resend # 10153
(4)   09-05-2025 13:48:44 946 PC resending # 45635
(4)   09-05-2025 13:48:57 944 MPU requested resend # 10154
(4)   09-05-2025 13:48:57 946 PC resending # 45637
(4)   09-05-2025 13:49:13 944 MPU requested resend # 10155
(4)   09-05-2025 13:49:13 946 PC resending # 45648
(4)   09-05-2025 13:49:14 944 MPU requested resend # 10156
(4)   09-05-2025 13:49:14 946 PC resending # 45677
(4)   09-05-2025 13:49:14 946 PC resending # 45697
(4)   09-05-2025 13:49:14 944 MPU requested resend # 10157
(4)   09-05-2025 13:49:14 946 PC resending # 45699
(4)   09-05-2025 13:49:33 944 MPU requested resend # 10158
(4)   09-05-2025 13:49:33 946 PC resending # 45701
(4)   09-05-2025 13:49:42 944 MPU requested resend # 10159
(4)   09-05-2025 13:49:42 946 PC resending # 45716
(4)   09-05-2025 13:49:42 944 MPU requested resend # 10160
(4)   09-05-2025 13:49:42 946 PC resending # 45761
(4)   09-05-2025 13:49:42 944 MPU requested resend # 10161
(4)   09-05-2025 13:49:42 946 PC resending # 45777
(4)   09-05-2025 13:50:09 944 MPU requested resend # 10162
(4)   09-05-2025 13:50:09 946 PC resending # 45779
(4)   09-05-2025 13:50:40 944 MPU requested resend # 10163
(4)   09-05-2025 13:50:40 946 PC resending # 45784
(4)   09-05-2025 13:51:34 944 MPU requested resend # 10164
(4)   09-05-2025 13:51:34 946 PC resending # 45786
(4)   09-05-2025 13:51:34 944 MPU requested resend # 10165
(4)   09-05-2025 13:51:34 946 PC resending # 45788
(4)   09-05-2025 13:51:39 944 MPU requested resend # 10166
(4)   09-05-2025 13:51:39 946 PC resending # 45790
(4)   09-05-2025 13:51:58 944 MPU requested resend # 10167
(4)   09-05-2025 13:51:58 946 PC resending # 45792
(4)   09-05-2025 13:52:20 944 MPU requested resend # 10168
(4)   09-05-2025 13:52:20 946 PC resending # 45794
(4)   09-05-2025 13:52:40 944 MPU requested resend # 10169
(4)   09-05-2025 13:52:40 946 PC resending # 45825
(4)   09-05-2025 13:52:40 944 MPU requested resend # 10170
(4)   09-05-2025 13:52:40 946 PC resending # 45830
(4)   09-05-2025 13:52:57 944 MPU requested resend # 10171
(4)   09-05-2025 13:52:57 946 PC resending # 45832
(4)   09-05-2025 13:54:24 944 MPU requested resend # 10172
(4)   09-05-2025 13:54:24 946 PC resending # 45834
(4)   09-05-2025 13:55:40 944 MPU requested resend # 10173
(4)   09-05-2025 13:55:40 946 PC resending # 45836
(4)   09-05-2025 13:56:24 944 MPU requested resend # 10174
(4)   09-05-2025 13:56:24 946 PC resending # 45838
(4)   09-05-2025 13:56:54 944 MPU requested resend # 10175
(4)   09-05-2025 13:56:54 946 PC resending # 45898
(4)   09-05-2025 13:58:06 944 MPU requested resend # 10176
(4)   09-05-2025 13:58:06 946 PC resending # 45902
(4)   09-05-2025 13:58:10 944 MPU requested resend # 10177
(4)   09-05-2025 13:58:10 946 PC resending # 45904
(4)   09-05-2025 13:58:44 944 MPU requested resend # 10178
(4)   09-05-2025 13:58:44 946 PC resending # 45906
(4)   09-05-2025 13:59:16 944 MPU requested resend # 10179
(4)   09-05-2025 13:59:16 946 PC resending # 45908
(4)   09-05-2025 13:59:30 944 MPU requested resend # 10180
(4)   09-05-2025 13:59:30 946 PC resending # 45910
(4)   09-05-2025 13:59:49 944 MPU requested resend # 10181
(4)   09-05-2025 13:59:49 946 PC resending # 45915
(4)   09-05-2025 14:00:23 944 MPU requested resend # 10182
(4)   09-05-2025 14:00:23 946 PC resending # 45937
(4)   09-05-2025 14:00:23 944 MPU requested resend # 10183
(4)   09-05-2025 14:00:23 946 PC resending # 45964
(4)   09-05-2025 14:00:23 946 PC resending # 45989
(4)   09-05-2025 14:00:32 944 MPU requested resend # 10184
(4)   09-05-2025 14:00:33 946 PC resending # 45991
(4)   09-05-2025 14:00:34 944 MPU requested resend # 10185
(4)   09-05-2025 14:00:34 946 PC resending # 45993
(4)   09-05-2025 14:01:01 944 MPU requested resend # 10186
(4)   09-05-2025 14:01:01 946 PC resending # 45995
(4)   09-05-2025 14:01:11 944 MPU requested resend # 10187
(4)   09-05-2025 14:01:11 946 PC resending # 45997
(4)   09-05-2025 14:01:16 944 MPU requested resend # 10188
(4)   09-05-2025 14:01:16 946 PC resending # 45999
(4)   09-05-2025 14:01:18 944 MPU requested resend # 10189
(4)   09-05-2025 14:01:18 946 PC resending # 46001
(4)   09-05-2025 14:01:43 944 MPU requested resend # 10190
(4)   09-05-2025 14:01:43 946 PC resending # 46003
(4)   09-05-2025 14:02:04 944 MPU requested resend # 10191
(4)   09-05-2025 14:02:05 946 PC resending # 46005
(4)   09-05-2025 14:02:28 944 MPU requested resend # 10192
(4)   09-05-2025 14:02:28 946 PC resending # 46007
(4)   09-05-2025 14:02:36 944 MPU requested resend # 10193
(4)   09-05-2025 14:02:36 946 PC resending # 46009
(4)   09-05-2025 14:02:59 944 MPU requested resend # 10194
(4)   09-05-2025 14:02:59 946 PC resending # 46011
(4)   09-05-2025 14:03:14 944 MPU requested resend # 10195
(4)   09-05-2025 14:03:14 946 PC resending # 46013
(4)   09-05-2025 14:03:19 944 MPU requested resend # 10196
(4)   09-05-2025 14:03:20 946 PC resending # 46015
(4)   09-05-2025 14:03:57 944 MPU requested resend # 10197
(4)   09-05-2025 14:03:57 946 PC resending # 46017
(4)   09-05-2025 14:04:34 944 MPU requested resend # 10198
(4)   09-05-2025 14:04:34 946 PC resending # 46019
(4)   09-05-2025 14:04:38 944 MPU requested resend # 10199
(4)   09-05-2025 14:04:38 946 PC resending # 46021
(4)   09-05-2025 14:04:44 944 MPU requested resend # 10200
(4)   09-05-2025 14:04:44 946 PC resending # 46023
(4)   09-05-2025 14:05:03 944 MPU requested resend # 10201
(4)   09-05-2025 14:05:03 946 PC resending # 46025
(4)   09-05-2025 14:05:08 944 MPU requested resend # 10202
(4)   09-05-2025 14:05:08 946 PC resending # 46027
(4)   09-05-2025 14:05:13 944 MPU requested resend # 10203
(4)   09-05-2025 14:05:13 946 PC resending # 46029
(4)   09-05-2025 14:05:35 944 MPU requested resend # 10204
(4)   09-05-2025 14:05:35 946 PC resending # 46031
(4)   09-05-2025 14:06:09 944 MPU requested resend # 10205
(4)   09-05-2025 14:06:09 946 PC resending # 46033
(4)   09-05-2025 14:06:10 944 MPU requested resend # 10206
(4)   09-05-2025 14:06:10 946 PC resending # 46035
(4)   09-05-2025 14:07:30 944 MPU requested resend # 10207
(4)   09-05-2025 14:07:30 946 PC resending # 46037
(4)   09-05-2025 14:08:29 944 MPU requested resend # 10208
(4)   09-05-2025 14:08:29 946 PC resending # 46039
(4)   09-05-2025 14:08:31 944 MPU requested resend # 10209
(4)   09-05-2025 14:08:31 946 PC resending # 46041
(4)   09-05-2025 14:08:32 944 MPU requested resend # 10210
(4)   09-05-2025 14:08:32 946 PC resending # 46043
(4)   09-05-2025 14:08:56 944 MPU requested resend # 10211
(4)   09-05-2025 14:08:56 946 PC resending # 46045
(4)   09-05-2025 14:10:05 944 MPU requested resend # 10212
(4)   09-05-2025 14:10:05 946 PC resending # 46047
(4)   09-05-2025 14:10:10 944 MPU requested resend # 10213
(4)   09-05-2025 14:10:10 946 PC resending # 46049
(4)   09-05-2025 14:10:28 944 MPU requested resend # 10214
(4)   09-05-2025 14:10:28 946 PC resending # 46051
(4)   09-05-2025 14:10:53 944 MPU requested resend # 10215
(4)   09-05-2025 14:10:53 946 PC resending # 46053
(4)   09-05-2025 14:11:24 944 MPU requested resend # 10216
(4)   09-05-2025 14:11:24 946 PC resending # 46055
(4)   09-05-2025 14:11:30 944 MPU requested resend # 10217
(4)   09-05-2025 14:11:30 946 PC resending # 46057
(4)   09-05-2025 14:11:48 944 MPU requested resend # 10218
(4)   09-05-2025 14:11:48 946 PC resending # 46059
(4)   09-05-2025 14:11:56 944 MPU requested resend # 10219
(4)   09-05-2025 14:11:56 946 PC resending # 46061
(4)   09-05-2025 14:12:07 944 MPU requested resend # 10220
(4)   09-05-2025 14:12:07 946 PC resending # 46063
(1)   09-05-2025 14:12:09 452 Ethernet Communication Error, See Tech Bulletin 270
(4)   09-05-2025 14:12:09 944 MPU requested resend # 10221
(4)   09-05-2025 14:12:09 946 PC resending # 46064
(4)   09-05-2025 14:12:09 946 PC resending # 46065
(4)   09-05-2025 14:12:11 944 MPU requested resend # 10222
(4)   09-05-2025 14:12:11 946 PC resending # 46067
(1)   09-05-2025 14:12:14 452 Ethernet Communication Error, See Tech Bulletin 270
(4)   09-05-2025 14:12:14 944 MPU requested resend # 10223
(4)   09-05-2025 14:12:15 946 PC resending # 46069
(4)   09-05-2025 14:12:25 944 MPU requested resend # 10224
(4)   09-05-2025 14:12:25 946 PC resending # 46102
(4)   09-05-2025 14:12:25 946 PC resending # 46124
(4)   09-05-2025 14:12:25 944 MPU requested resend # 10225
(4)   09-05-2025 14:12:25 946 PC resending # 46153
(4)   09-05-2025 14:12:25 946 PC resending # 46171
(4)   09-05-2025 14:12:25 944 MPU requested resend # 10226
(4)   09-05-2025 14:12:25 946 PC resending # 46200
(4)   09-05-2025 14:12:25 946 PC resending # 46230
(4)   09-05-2025 14:12:25 946 PC resending # 46233
(4)   09-05-2025 14:12:59 944 MPU requested resend # 10227
(4)   09-05-2025 14:12:59 946 PC resending # 46235
(4)   09-05-2025 14:13:06 944 MPU requested resend # 10228
(4)   09-05-2025 14:13:06 946 PC resending # 46237
(4)   09-05-2025 14:13:13 944 MPU requested resend # 10229
(4)   09-05-2025 14:13:13 946 PC resending # 46239
(4)   09-05-2025 14:13:14 944 MPU requested resend # 10230
(4)   09-05-2025 14:13:14 946 PC resending # 46241
(4)   09-05-2025 14:13:30 944 MPU requested resend # 10231
(4)   09-05-2025 14:13:30 946 PC resending # 46243
(4)   09-05-2025 14:13:38 944 MPU requested resend # 10232
(4)   09-05-2025 14:13:38 946 PC resending # 46245
(4)   09-05-2025 14:14:11 944 MPU requested resend # 10233
(4)   09-05-2025 14:14:11 946 PC resending # 46247
(4)   09-05-2025 14:15:32 944 MPU requested resend # 10234
(4)   09-05-2025 14:15:32 946 PC resending # 46263
(4)   09-05-2025 14:16:17 944 MPU requested resend # 10235
(4)   09-05-2025 14:16:18 946 PC resending # 46265
(4)   09-05-2025 14:16:22 944 MPU requested resend # 10236
(4)   09-05-2025 14:16:22 946 PC resending # 46267
(4)   09-05-2025 14:16:26 944 MPU requested resend # 10237
(4)   09-05-2025 14:16:26 946 PC resending # 46269
(4)   09-05-2025 14:17:07 944 MPU requested resend # 10238
(4)   09-05-2025 14:17:07 946 PC resending # 46271
(4)   09-05-2025 14:18:01 944 MPU requested resend # 10239
(4)   09-05-2025 14:18:01 946 PC resending # 46273
(4)   09-05-2025 14:18:17 944 MPU requested resend # 10240
(4)   09-05-2025 14:18:17 946 PC resending # 46275
(4)   09-05-2025 14:19:08 944 MPU requested resend # 10241
(4)   09-05-2025 14:19:08 946 PC resending # 46277
(4)   09-05-2025 14:19:17 944 MPU requested resend # 10242
(4)   09-05-2025 14:19:17 946 PC resending # 46279
(4)   09-05-2025 14:20:16 944 MPU requested resend # 10243
(4)   09-05-2025 14:20:16 946 PC resending # 46281
(1)   09-05-2025 14:20:17 407 X+ limit (#50002) tripped
(1)   09-05-2025 14:20:17 407 Y+ limit (#50002) tripped
(1)   09-05-2025 14:20:17 407 Z+ limit (#50002) tripped
(1)   09-05-2025 14:20:21 407 X+ limit (#50002) tripped
(1)   09-05-2025 14:20:21 407 Y+ limit (#50002) tripped
(1)   09-05-2025 14:20:21 407 Z+ limit (#50002) tripped
(1)   09-05-2025 14:20:38 452 Ethernet Communication Error, CNCPC to controller. See Tech Bulletin 270, "How to Solve Communication Errors"
(4)   09-05-2025 14:21:03 9039 Software Exited, Cycle E-Stop/Reset to Continue
(1)   09-05-2025 14:21:12 490 Reset Initiated, Press Reset to Clear
(4)   09-05-2025 14:22:00 944 MPU requested resend # 10244
(4)   09-05-2025 14:22:00 946 PC resending # 46283
(4)   09-05-2025 14:22:13 944 MPU requested resend # 10245
(4)   09-05-2025 14:22:13 946 PC resending # 46285
(1)   09-05-2025 14:22:16 452 Ethernet Communication Error, See Tech Bulletin 270
(4)   09-05-2025 14:22:22 944 MPU requested resend # 10246
(4)   09-05-2025 14:22:22 946 PC resending # 46287
(4)   09-05-2025 14:22:26 944 MPU requested resend # 10247
(4)   09-05-2025 14:22:26 946 PC resending # 46289
(4)   09-05-2025 14:22:29 944 MPU requested resend # 10248
(4)   09-05-2025 14:22:29 946 PC resending # 46291
(4)   09-05-2025 14:22:30 944 MPU requested resend # 10249
(4)   09-05-2025 14:22:30 946 PC resending # 46293
(4)   09-05-2025 14:22:35 944 MPU requested resend # 10250
(4)   09-05-2025 14:22:35 946 PC resending # 46295
(4)   09-05-2025 14:22:38 944 MPU requested resend # 10251
(4)   09-05-2025 14:22:38 946 PC resending # 46297
(1)   09-05-2025 14:22:47 452 Ethernet Communication Error, See Tech Bulletin 270
(4)   09-05-2025 14:22:49 944 MPU requested resend # 10252
(4)   09-05-2025 14:22:49 946 PC resending # 46299
(4)   09-05-2025 14:22:52 944 MPU requested resend # 10253
(4)   09-05-2025 14:22:52 946 PC resending # 46328
(4)   09-05-2025 14:23:29 944 MPU requested resend # 10254
(4)   09-05-2025 14:23:29 946 PC resending # 46330
(4)   09-05-2025 14:23:37 944 MPU requested resend # 10255
(4)   09-05-2025 14:23:37 946 PC resending # 46332
(4)   09-05-2025 14:23:40 944 MPU requested resend # 10256
(4)   09-05-2025 14:23:40 946 PC resending # 46334
(4)   09-05-2025 14:23:53 944 MPU requested resend # 10257
(4)   09-05-2025 14:23:53 946 PC resending # 46335
(4)   09-05-2025 14:23:53 946 PC resending # 46336
(4)   09-05-2025 14:23:59 944 MPU requested resend # 10258
(4)   09-05-2025 14:23:59 946 PC resending # 46338
(4)   09-05-2025 14:24:08 944 MPU requested resend # 10259
(4)   09-05-2025 14:24:08 946 PC resending # 46340
(4)   09-05-2025 14:25:04 944 MPU requested resend # 10260
(4)   09-05-2025 14:25:04 946 PC resending # 46342
(4)   09-05-2025 14:25:17 944 MPU requested resend # 10261
(4)   09-05-2025 14:25:17 946 PC resending # 46344
(4)   09-05-2025 14:25:30 944 MPU requested resend # 10262
(4)   09-05-2025 14:25:30 946 PC resending # 46346
(1)   09-05-2025 14:25:49 407 X+ limit (#50002) tripped
(1)   09-05-2025 14:25:49 407 Y+ limit (#50002) tripped
(1)   09-05-2025 14:25:49 407 Z+ limit (#50002) tripped
(4)   09-05-2025 14:25:57 944 MPU requested resend # 10263
(4)   09-05-2025 14:25:57 946 PC resending # 46348
(4)   09-05-2025 14:26:19 944 MPU requested resend # 10264
(4)   09-05-2025 14:26:19 946 PC resending # 46350
(4)   09-05-2025 14:26:21 944 MPU requested resend # 10265
(4)   09-05-2025 14:26:22 946 PC resending # 46352
(4)   09-05-2025 14:26:53 944 MPU requested resend # 10266
(4)   09-05-2025 14:26:53 946 PC resending # 46354
(4)   09-05-2025 14:26:57 944 MPU requested resend # 10267
(4)   09-05-2025 14:26:57 946 PC resending # 46356
(1)   09-05-2025 14:27:01 407 X+ limit (#50002) tripped
(1)   09-05-2025 14:27:01 407 Y+ limit (#50002) tripped
(1)   09-05-2025 14:27:01 407 Z+ limit (#50002) tripped
(1)   09-05-2025 14:27:02 407 X+ limit (#50002) tripped
(1)   09-05-2025 14:27:02 407 Y+ limit (#50002) tripped
(1)   09-05-2025 14:27:02 407 Z+ limit (#50002) tripped
(1)   09-05-2025 14:27:03 407 X+ limit (#50002) tripped
(1)   09-05-2025 14:27:03 407 Y+ limit (#50002) tripped
(1)   09-05-2025 14:27:03 407 Z+ limit (#50002) tripped
(1)   09-05-2025 14:27:04 407 X+ limit (#50002) tripped
(1)   09-05-2025 14:27:04 407 Y+ limit (#50002) tripped
(1)   09-05-2025 14:27:04 407 Z+ limit (#50002) tripped
(1)   09-05-2025 14:27:05 407 X+ limit (#50002) tripped
(1)   09-05-2025 14:27:05 407 Y+ limit (#50002) tripped
(1)   09-05-2025 14:27:05 407 Z+ limit (#50002) tripped
(1)   09-05-2025 14:27:07 407 X+ limit (#50002) tripped
(1)   09-05-2025 14:27:07 407 Y+ limit (#50002) tripped
(1)   09-05-2025 14:27:07 407 Z+ limit (#50002) tripped
(1)   09-05-2025 14:27:08 452 Ethernet Communication Error, See Tech Bulletin 270
(1)   09-05-2025 14:27:08 407 X+ limit (#50002) tripped
(1)   09-05-2025 14:27:08 407 Y+ limit (#50002) tripped
(1)   09-05-2025 14:27:08 407 Z+ limit (#50002) tripped
(1)   09-05-2025 14:27:13 452 Ethernet Communication Error, See Tech Bulletin 270
(1)   09-05-2025 14:27:14 407 X+ limit (#50002) tripped
(1)   09-05-2025 14:27:14 407 Y+ limit (#50002) tripped
(1)   09-05-2025 14:27:14 407 Z+ limit (#50002) tripped
(1)   09-05-2025 14:27:15 407 X+ limit (#50002) tripped
(1)   09-05-2025 14:27:15 407 Y+ limit (#50002) tripped
(1)   09-05-2025 14:27:15 407 Z+ limit (#50002) tripped
(4)   09-05-2025 14:27:16 944 MPU requested resend # 10268
(4)   09-05-2025 14:27:17 946 PC resending # 46358
(1)   09-05-2025 14:27:25 407 X+ limit (#50002) tripped
(1)   09-05-2025 14:27:25 407 Y+ limit (#50002) tripped
(1)   09-05-2025 14:27:25 407 Z+ limit (#50002) tripped
(1)   09-05-2025 14:27:26 407 X+ limit (#50002) tripped
(1)   09-05-2025 14:27:26 407 Y+ limit (#50002) tripped
(1)   09-05-2025 14:27:26 407 Z+ limit (#50002) tripped
(4)   09-05-2025 14:27:58 944 MPU requested resend # 10269
(4)   09-05-2025 14:27:58 946 PC resending # 46360
(4)   09-05-2025 14:27:59 944 MPU requested resend # 10270
(4)   09-05-2025 14:27:59 946 PC resending # 46362
(1)   09-05-2025 14:28:05 407 X+ limit (#50002) tripped
(1)   09-05-2025 14:28:05 407 Y+ limit (#50002) tripped
(1)   09-05-2025 14:28:05 407 Z+ limit (#50002) tripped
(1)   09-05-2025 14:28:06 407 X+ limit (#50002) tripped
(1)   09-05-2025 14:28:06 407 Y+ limit (#50002) tripped
(1)   09-05-2025 14:28:06 407 Z+ limit (#50002) tripped
(4)   09-05-2025 14:28:06 944 MPU requested resend # 10271
(4)   09-05-2025 14:28:07 946 PC resending # 46364
(1)   09-05-2025 14:28:07 407 X+ limit (#50002) tripped
(1)   09-05-2025 14:28:07 407 Y+ limit (#50002) tripped
(1)   09-05-2025 14:28:07 407 Z+ limit (#50002) tripped
(4)   09-05-2025 14:28:11 944 MPU requested resend # 10272
(4)   09-05-2025 14:28:11 946 PC resending # 46366
(4)   09-05-2025 14:28:11 944 MPU requested resend # 10273
(4)   09-05-2025 14:28:11 946 PC resending # 46368
(1)   09-05-2025 14:28:46 452 Ethernet Communication Error, CNCPC to controller. See Tech Bulletin 270, "How to Solve Communication Errors"
(4)   09-05-2025 14:29:37 9039 Software Exited, Cycle E-Stop/Reset to Continue
(1)   09-05-2025 14:29:45 490 Reset Initiated, Press Reset to Clear
(1)   09-05-2025 14:29:48 452 Ethernet Communication Error, See Tech Bulletin 270
(4)   09-05-2025 14:29:52 944 MPU requested resend # 10274
(4)   09-05-2025 14:29:52 946 PC resending # 46370
(4)   09-05-2025 14:30:17 944 MPU requested resend # 10275
(4)   09-05-2025 14:30:17 946 PC resending # 46372
(4)   09-05-2025 14:30:46 944 MPU requested resend # 10276
(4)   09-05-2025 14:30:46 946 PC resending # 46375
(4)   09-05-2025 14:31:13 944 MPU requested resend # 10277
(4)   09-05-2025 14:31:13 946 PC resending # 46377
(4)   09-05-2025 14:31:38 944 MPU requested resend # 10278
(4)   09-05-2025 14:31:38 946 PC resending # 46379
(4)   09-05-2025 14:32:29 944 MPU requested resend # 10279
(4)   09-05-2025 14:32:29 946 PC resending # 46381
(4)   09-05-2025 14:32:42 944 MPU requested resend # 10280
(4)   09-05-2025 14:32:42 946 PC resending # 46382
(4)   09-05-2025 14:32:42 946 PC resending # 46383
(4)   09-05-2025 14:33:13 944 MPU requested resend # 10281
(4)   09-05-2025 14:33:13 946 PC resending # 46385
(4)   09-05-2025 14:33:45 944 MPU requested resend # 10282
(4)   09-05-2025 14:33:45 946 PC resending # 46387
(4)   09-05-2025 14:33:50 944 MPU requested resend # 10283
(4)   09-05-2025 14:33:50 946 PC resending # 46389
(4)   09-05-2025 14:34:05 944 MPU requested resend # 10284
(4)   09-05-2025 14:34:05 946 PC resending # 46391
(4)   09-05-2025 14:34:14 944 MPU requested resend # 10285
(4)   09-05-2025 14:34:15 946 PC resending # 46393
(4)   09-05-2025 14:34:50 944 MPU requested resend # 10286
(4)   09-05-2025 14:34:50 946 PC resending # 46395
(4)   09-05-2025 14:34:53 944 MPU requested resend # 10287
(4)   09-05-2025 14:34:53 946 PC resending # 46397
(4)   09-05-2025 14:35:09 944 MPU requested resend # 10288
(4)   09-05-2025 14:35:09 946 PC resending # 46399
(4)   09-05-2025 14:35:19 944 MPU requested resend # 10289
(4)   09-05-2025 14:35:19 946 PC resending # 46401
(4)   09-05-2025 14:35:26 944 MPU requested resend # 10290
(4)   09-05-2025 14:35:26 946 PC resending # 46403
(4)   09-05-2025 14:35:30 944 MPU requested resend # 10291
(4)   09-05-2025 14:35:30 946 PC resending # 46405
(1)   09-05-2025 14:36:27 452 Ethernet Communication Error, See Tech Bulletin 270
(4)   09-05-2025 14:36:30 944 MPU requested resend # 10292
(4)   09-05-2025 14:36:30 946 PC resending # 46415
(4)   09-05-2025 14:36:30 944 MPU requested resend # 10293
(4)   09-05-2025 14:36:30 946 PC resending # 46424
(4)   09-05-2025 14:36:31 944 MPU requested resend # 10294
(4)   09-05-2025 14:36:31 946 PC resending # 46480
(4)   09-05-2025 14:36:31 944 MPU requested resend # 10295
(4)   09-05-2025 14:36:31 946 PC resending # 46509
(4)   09-05-2025 14:36:31 946 PC resending # 46538
(4)   09-05-2025 14:36:31 944 MPU requested resend # 10296
(4)   09-05-2025 14:36:31 946 PC resending # 46565
(4)   09-05-2025 14:36:31 946 PC resending # 46599
(4)   09-05-2025 14:36:31 944 MPU requested resend # 10297
(4)   09-05-2025 14:36:31 946 PC resending # 46650
(4)   09-05-2025 14:36:31 944 MPU requested resend # 10298
(4)   09-05-2025 14:36:31 946 PC resending # 46679
(4)   09-05-2025 14:36:31 946 PC resending # 46694
(4)   09-05-2025 14:36:31 944 MPU requested resend # 10299
(4)   09-05-2025 14:36:31 946 PC resending # 46723
(4)   09-05-2025 14:36:31 946 PC resending # 46751
(4)   09-05-2025 14:36:32 944 MPU requested resend # 10300
(4)   09-05-2025 14:36:32 946 PC resending # 46778
(4)   09-05-2025 14:36:32 946 PC resending # 46793
(4)   09-05-2025 14:36:32 944 MPU requested resend # 10301
(4)   09-05-2025 14:36:32 946 PC resending # 46852
(4)   09-05-2025 14:36:32 944 MPU requested resend # 10302
(4)   09-05-2025 14:36:32 946 PC resending # 46910
(4)   09-05-2025 14:36:32 944 MPU requested resend # 10303
(4)   09-05-2025 14:36:32 946 PC resending # 46939
(4)   09-05-2025 14:36:32 946 PC resending # 46961
(4)   09-05-2025 14:36:32 944 MPU requested resend # 10304
(4)   09-05-2025 14:36:32 946 PC resending # 46988
(4)   09-05-2025 14:36:32 946 PC resending # 47018
(4)   09-05-2025 14:36:32 944 MPU requested resend # 10305
(4)   09-05-2025 14:36:32 946 PC resending # 47058
(4)   09-05-2025 14:36:33 944 MPU requested resend # 10306
(4)   09-05-2025 14:36:33 946 PC resending # 47085
(4)   09-05-2025 14:36:33 946 PC resending # 47115
(4)   09-05-2025 14:36:33 944 MPU requested resend # 10307
(4)   09-05-2025 14:36:33 946 PC resending # 47174
(4)   09-05-2025 14:36:33 946 PC resending # 47177
(4)   09-05-2025 14:36:33 944 MPU requested resend # 10308
(4)   09-05-2025 14:36:33 946 PC resending # 47206
(4)   09-05-2025 14:36:33 946 PC resending # 47238
(4)   09-05-2025 14:36:33 944 MPU requested resend # 10309
(4)   09-05-2025 14:36:33 946 PC resending # 47267
(4)   09-05-2025 14:36:33 946 PC resending # 47284
(4)   09-05-2025 14:36:33 944 MPU requested resend # 10310
(4)   09-05-2025 14:36:33 946 PC resending # 47311
(4)   09-05-2025 14:36:33 946 PC resending # 47339
(4)   09-05-2025 14:36:33 946 PC resending # 47344
(4)   09-05-2025 14:36:33 944 MPU requested resend # 10311
(4)   09-05-2025 14:36:33 946 PC resending # 47371
(4)   09-05-2025 14:36:33 946 PC resending # 47383
(4)   09-05-2025 14:36:33 944 MPU requested resend # 10312
(4)   09-05-2025 14:36:33 946 PC resending # 47410
(4)   09-05-2025 14:36:33 946 PC resending # 47435
(4)   09-05-2025 14:36:33 944 MPU requested resend # 10313
(4)   09-05-2025 14:36:33 946 PC resending # 47464
(4)   09-05-2025 14:36:33 946 PC resending # 47494
(4)   09-05-2025 14:36:34 944 MPU requested resend # 10314
(4)   09-05-2025 14:36:34 946 PC resending # 47496
(4)   09-05-2025 14:36:38 944 MPU requested resend # 10315
(4)   09-05-2025 14:36:38 946 PC resending # 47498
(1)   09-05-2025 14:37:45 490 Reset Initiated, Press Reset to Clear
(1)   09-05-2025 14:37:50 204 Exiting CNC...Normal Exit (66)
(1)   09-05-2025 14:42:56 199 CNC Started
(1)   09-05-2025 14:43:02 CNC12 Acorn Mill v5.30
(1)   09-05-2025 14:43:02 490 Reset Initiated, Press Reset to Clear
(1)   09-05-2025 14:44:03 490 Reset Initiated, Press Reset to Clear
(1)   09-05-2025 14:44:27 490 Reset Initiated, Press Reset to Clear
(1)   09-05-2025 14:45:12 490 Reset Initiated, Press Reset to Clear
(4)   09-05-2025 14:48:50 8040 WARNING: PROBE TRIPPED
(4)   09-05-2025 14:48:50 4042 Probe Cleared
(4)   09-05-2025 14:48:52 5067 FAST_JOG_SELECTED
(4)   09-05-2025 14:49:37 8040 WARNING: PROBE TRIPPED
(4)   09-05-2025 14:49:37 4042 Probe Cleared
(4)   09-05-2025 14:49:43 8040 WARNING: PROBE TRIPPED
(4)   09-05-2025 14:49:43 4042 Probe Cleared
(4)   09-05-2025 14:49:44 8040 WARNING: PROBE TRIPPED
(4)   09-05-2025 14:49:45 4042 Probe Cleared
(4)   09-05-2025 14:50:16 8040 WARNING: PROBE TRIPPED
(4)   09-05-2025 14:50:17 4042 Probe Cleared
(4)   09-05-2025 14:50:18 8040 WARNING: PROBE TRIPPED
(4)   09-05-2025 14:50:18 4042 Probe Cleared
(4)   09-05-2025 14:50:46 5067 FAST_JOG_SELECTED
(4)   09-05-2025 14:51:15 8040 WARNING: PROBE TRIPPED
(4)   09-05-2025 14:51:15 4042 Probe Cleared
(4)   09-05-2025 14:51:20 8040 WARNING: PROBE TRIPPED
(4)   09-05-2025 14:51:21 4042 Probe Cleared
(4)   09-05-2025 14:51:22 8040 WARNING: PROBE TRIPPED
(4)   09-05-2025 14:51:22 4042 Probe Cleared
(4)   09-05-2025 14:51:47 8040 WARNING: PROBE TRIPPED
(4)   09-05-2025 14:51:48 4042 Probe Cleared
(4)   09-05-2025 14:51:49 8040 WARNING: PROBE TRIPPED
(4)   09-05-2025 14:51:50 4042 Probe Cleared
(4)   09-05-2025 14:52:08 5067 FAST_JOG_SELECTED
(4)   09-05-2025 15:02:32 5068 SLOW_JOG_SELECTED
(4)   09-05-2025 15:03:23 5067 FAST_JOG_SELECTED
(1)   09-05-2025 15:06:25 407 X+ limit (#50002) tripped
(1)   09-05-2025 15:06:25 407 Y+ limit (#50002) tripped
(1)   09-05-2025 15:06:25 407 Z+ limit (#50002) tripped
(1)   09-05-2025 15:06:39 490 Reset Initiated, Press Reset to Clear
(4)   09-05-2025 15:06:48 907 Z axis travel exceeded
(1)   09-05-2025 15:08:14 Creating report...
(1)   09-05-2025 15:08:19 Saved report to C:\cncm\ncfiles\report_E062346B501D-0430248204_2025-09-05_15-08-14.zip
(1)   09-05-2025 15:21:26 Creating report...
Malachilee wrote: Mon Sep 08, 2025 11:25 am
sounds like you got a flaky limit switch/wiring or power supply
post a fresh report.zip so we can see if all the com errors are cleared up. shawn is right this setup has massive com issues, solve that first, then look a all the limits you have wired.