Anilam Crusader series M converting to Allin1DC

All things related to Centroid Oak, Allin1DC, MPU11 and Legacy products

Moderator: cnckeith

Robert Meacham
Posts: 31
Joined: Tue Jan 28, 2025 1:41 pm
Acorn CNC Controller: No
Plasma CNC Controller: No
AcornSix CNC Controller: No
Allin1DC CNC Controller: Yes
Hickory CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: A901522
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No

Re: Anilam Crusader series M converting to Allin1DC

Post by Robert Meacham »

Okay I think I've got the Transformer, cap, contactor, power supply, and limit switches figured out and wired in. Now we're back to the spindle controls. I'm assuming the board on the bottom left is going away. The line input is coming in in the top right corner. Next it goes through a rotary disconnect switch then through the large fuses and up to the relays in the top left and middle. I'm thinking the relays in the very top left are for forward and reverse? Does this all sound correct so far? I'm thinking that the centroid control could run those forward and reverse relays correct?



Robert Meacham
Posts: 31
Joined: Tue Jan 28, 2025 1:41 pm
Acorn CNC Controller: No
Plasma CNC Controller: No
AcornSix CNC Controller: No
Allin1DC CNC Controller: Yes
Hickory CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: A901522
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No

Re: Anilam Crusader series M converting to Allin1DC

Post by Robert Meacham »

Next question, thinking about the encoders, i think this is a tach in the ends of my servos, i don't think i will need those right? I'd like to remove them to make room for encoder wiring.


centroid467
Posts: 824
Joined: Thu Apr 14, 2022 2:46 pm
Acorn CNC Controller: No
Allin1DC CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC12: No
CNC11: No
CPU10 or CPU7: No

Re: Anilam Crusader series M converting to Allin1DC

Post by centroid467 »

Do you have the original schematics for this system? Otherwise, you'd have to trace wires to determine where the contactors (3 big relays up top) go. It looks like the spindle speed control was mechanical so it makes sense for there to be some contactors for forward/reverse running. I'd also expect at least one for the axis servos.


You probably would not need that board with relays unless the relays on ALLIN1DC cannot handle the loads. In that case, using the ALLIN1DC relays to control beefier external relays is the way to go.

Yep, those are the brushes and commutator for the tachometer. ALLIN1DC does not use tachometers and so that is probably where the encoders should be mounted.


cncsnw
Community Expert
Posts: 4589
Joined: Wed Mar 24, 2010 5:48 pm

Re: Anilam Crusader series M converting to Allin1DC

Post by cncsnw »

Yes, the things in the top left are a reversing contactor assembly, with an overload relay (collectively called a "reversing starter").

Yes, you can control them from the Centroid control for spindle forward/reverse/off. You will not, of course, have programmable speed control.


Robert Meacham
Posts: 31
Joined: Tue Jan 28, 2025 1:41 pm
Acorn CNC Controller: No
Plasma CNC Controller: No
AcornSix CNC Controller: No
Allin1DC CNC Controller: Yes
Hickory CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: A901522
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No

Re: Anilam Crusader series M converting to Allin1DC

Post by Robert Meacham »



Here's a diagram I made of the forward and reverse relays. Looks like it's controlled by 110 volt AC circuit with some safety auxiliary contacts to prevent both relays from being on at the same time. What's the best way to control this with the all-in-one?


Robert Meacham
Posts: 31
Joined: Tue Jan 28, 2025 1:41 pm
Acorn CNC Controller: No
Plasma CNC Controller: No
AcornSix CNC Controller: No
Allin1DC CNC Controller: Yes
Hickory CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: A901522
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No

Re: Anilam Crusader series M converting to Allin1DC

Post by Robert Meacham »



Here's what I'm thinking if I can find two 24 volt DC controlled relay to apply the 110 volts to the main spindle relays. Does this look reasonable?


cncsnw
Community Expert
Posts: 4589
Joined: Wed Mar 24, 2010 5:48 pm

Re: Anilam Crusader series M converting to Allin1DC

Post by cncsnw »

I would just wire the 120VAC for the contactor coils through the OUT7 and OUT8 relays on the Allin1DC. I believe they are rated for up to 250VAC, and the current draw of the contactor coils is minimal.

It is generally not necessary to use a relay to control a relay to control a relay.


Robert Meacham
Posts: 31
Joined: Tue Jan 28, 2025 1:41 pm
Acorn CNC Controller: No
Plasma CNC Controller: No
AcornSix CNC Controller: No
Allin1DC CNC Controller: Yes
Hickory CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: A901522
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No

Re: Anilam Crusader series M converting to Allin1DC

Post by Robert Meacham »


So just go something like this? I'd assume I'd want to use the 110 volt off the tb1 and the common off the tb1 correct,


tblough
Community Expert
Posts: 3540
Joined: Tue Mar 22, 2016 10:03 am
Acorn CNC Controller: Yes
Allin1DC CNC Controller: Yes
Oak CNC controller: Yes
CNC Control System Serial Number: 100505
100327
102696
103432
7804732B977B-0624192192
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No
Location: Boston, MA
Contact:

Re: Anilam Crusader series M converting to Allin1DC

Post by tblough »

Don't forget snubbers across the relay coils!
Cheers,

Tom
Confidence is the feeling you have before you fully understand the situation.
I have CDO. It's like OCD, but the letters are where they should be.


Robert Meacham
Posts: 31
Joined: Tue Jan 28, 2025 1:41 pm
Acorn CNC Controller: No
Plasma CNC Controller: No
AcornSix CNC Controller: No
Allin1DC CNC Controller: Yes
Hickory CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: A901522
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No

Re: Anilam Crusader series M converting to Allin1DC

Post by Robert Meacham »

tblough wrote: Thu Jan 30, 2025 9:26 pm Don't forget snubbers across the relay coils!
That's not something I'm familiar with, what is it? ( I'm guessing something to do with voltage Spike when the coil unloads) where do I get it? and where should I put it?


Post Reply