Problem with 10v spindle control <resolved>

All things related to the Centroid Acorn CNC Controller

Moderator: cnckeith

Jim Klawon
Posts: 8
Joined: Wed Sep 20, 2023 9:08 am
Acorn CNC Controller: Yes
Plasma CNC Controller: Yes
AcornSix CNC Controller: No
Allin1DC CNC Controller: No
Hickory CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: 7804733F0ECD-1231192780
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No

Problem with 10v spindle control <resolved>

Post by Jim Klawon »

First, the symptoms. Several months ago I started having several different issues with controlling my CNC. The MPG started responding strangely. Sometimes it would work but with an unreal lag time for updating the display. Other times it would cause an axis to move in a jerking motion in both directions when using the dial to jog. I have found that restarting the computer resolves that issue for a week or so. Around the same time there were a couple instances when I would start a run and the spindle speed would just continue to ramp up until going into fault. It would run fine after stopping and restarting the program. The issue seemed to go away for several months, though the MPG issue has persisted.

Around a week ago the spindle started randomly ramping up and down during a run. Since this was different than the spindle simply ramping up and going into fault, I started with checking the VFD. I tried changing the VFD settings to allow me to control it directly from the unit and not through the VCP. It was unresponsive to direct control. Figuring that the unit was done for I replaced it with a different model.

After getting all of the connections switched to the new VFD I tried controlling it through the VCP. I turned on and ramped up the speed. The VCP buttons worked but the constant ramping up and down randomly was still an issue. The readout on the VFD was set to display frequency and was showing random increases and decreases in step with the motor speed fluctuations.

Then I decided to check the 10v supply from the Acorn board. It too was fluctuating up and down. I disconnected the spindle and ran the spindle voltage bench test. The first voltage failed having fluctuated around the 1.3v to 1.5v range instead of the 1.66v target.

I'm assuming that I'll need a new Acorn unit but I thought that I would check to see if anyone happens to be familiar with the problem and knows a way to fix it.

Thanks

Jim


Centroid188
Posts: 52
Joined: Thu Aug 10, 2017 1:55 pm
Acorn CNC Controller: Yes
Plasma CNC Controller: No
AcornSix CNC Controller: No
Allin1DC CNC Controller: Yes
Hickory CNC Controller: No
Oak CNC controller: Yes
CNC Control System Serial Number: none
DC3IOB: Yes
CNC11: Yes
CPU10 or CPU7: Yes

Re: Problem with 10v spindle control

Post by Centroid188 »

Based on you comment on the WMPG and the fact that it has spindle override, I would shut the WMPG off when conducting these tests.
It is possible the WMPG is having a problem and commanding the spindle changes.


grossmsj
Posts: 190
Joined: Fri Jan 13, 2023 8:50 am
Acorn CNC Controller: Yes
Plasma CNC Controller: No
AcornSix CNC Controller: No
Allin1DC CNC Controller: No
Hickory CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No
Location: Hopewell NJ
Contact:

Re: Problem with 10v spindle control

Post by grossmsj »

Jim Klawon wrote: Fri Jan 24, 2025 8:56 am The MPG started responding strangely. Sometimes it would work but with an unreal lag time for updating the display. Other times it would cause an axis to move in a jerking motion in both directions when using the dial to jog. I have found that restarting the computer resolves that issue.
I've also observed this behavior and reported it: https://centroidcncforum.com/viewtopic. ... 132#p93132

It still happens, quite reproducibly, when I leave my whole system on without a daily shutdown. Like you, restarting the computer (in my case a NUC) resolves that problem. Haven't seen any problems with the spindle.
-Scott


cnckeith
Site Admin
Posts: 8983
Joined: Wed Mar 03, 2010 4:23 pm
Acorn CNC Controller: Yes
Plasma CNC Controller: No
AcornSix CNC Controller: No
Allin1DC CNC Controller: Yes
Hickory CNC Controller: No
Oak CNC controller: Yes
CNC Control System Serial Number: none
DC3IOB: Yes
CNC11: Yes
CPU10 or CPU7: Yes
Contact:

Re: Problem with 10v spindle control

Post by cnckeith »

please post a fresh report.zip
Need support? READ THIS POST first. http://centroidcncforum.com/viewtopic.php?f=60&t=1043
All Acorn Documentation is located here: viewtopic.php?f=60&t=3397
Answers to common questions: viewforum.php?f=63
and here viewforum.php?f=61
Gear we use but don't sell. https://www.centroidcnc.com/centroid_di ... _gear.html


cnckeith
Site Admin
Posts: 8983
Joined: Wed Mar 03, 2010 4:23 pm
Acorn CNC Controller: Yes
Plasma CNC Controller: No
AcornSix CNC Controller: No
Allin1DC CNC Controller: Yes
Hickory CNC Controller: No
Oak CNC controller: Yes
CNC Control System Serial Number: none
DC3IOB: Yes
CNC11: Yes
CPU10 or CPU7: Yes
Contact:

Re: Problem with 10v spindle control

Post by cnckeith »

grossmsj wrote: Fri Jan 24, 2025 11:40 am
Jim Klawon wrote: Fri Jan 24, 2025 8:56 am The MPG started responding strangely. Sometimes it would work but with an unreal lag time for updating the display. Other times it would cause an axis to move in a jerking motion in both directions when using the dial to jog. I have found that restarting the computer resolves that issue.
I've also observed this behavior and reported it: https://centroidcncforum.com/viewtopic. ... 132#p93132

It still happens, quite reproducibly, when I leave my whole system on without a daily shutdown. Like you, restarting the computer (in my case a NUC) resolves that problem. Haven't seen any problems with the spindle.
hello. are you saying you can reproduce this? if so i'd like to see it, can we remote into your machine?
Need support? READ THIS POST first. http://centroidcncforum.com/viewtopic.php?f=60&t=1043
All Acorn Documentation is located here: viewtopic.php?f=60&t=3397
Answers to common questions: viewforum.php?f=63
and here viewforum.php?f=61
Gear we use but don't sell. https://www.centroidcnc.com/centroid_di ... _gear.html


grossmsj
Posts: 190
Joined: Fri Jan 13, 2023 8:50 am
Acorn CNC Controller: Yes
Plasma CNC Controller: No
AcornSix CNC Controller: No
Allin1DC CNC Controller: No
Hickory CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No
Location: Hopewell NJ
Contact:

Re: Problem with 10v spindle control

Post by grossmsj »

Yes, it will eventually occur after I've left the machine on for a few days. I just restarted it yesterday so it may be a few days.
The next time this happens I'll leave it alone and give you guys a call so you can remote into it.
It would be helpful for me if someone could PM me a phone number I could call to expedite things.
-Scott


tblough
Community Expert
Posts: 3544
Joined: Tue Mar 22, 2016 10:03 am
Acorn CNC Controller: Yes
Plasma CNC Controller: No
AcornSix CNC Controller: No
Allin1DC CNC Controller: Yes
Hickory CNC Controller: No
Oak CNC controller: Yes
CNC Control System Serial Number: 100505
100327
102696
103432
7804732B977B-0624192192
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No
Location: Boston, MA
Contact:

Re: Problem with 10v spindle control

Post by tblough »

If it happens after a few days, it sounds like Windows sleeping the USB port and not waking it back up.
Cheers,

Tom
Confidence is the feeling you have before you fully understand the situation.
I have CDO. It's like OCD, but the letters are where they should be.


cnckeith
Site Admin
Posts: 8983
Joined: Wed Mar 03, 2010 4:23 pm
Acorn CNC Controller: Yes
Plasma CNC Controller: No
AcornSix CNC Controller: No
Allin1DC CNC Controller: Yes
Hickory CNC Controller: No
Oak CNC controller: Yes
CNC Control System Serial Number: none
DC3IOB: Yes
CNC11: Yes
CPU10 or CPU7: Yes
Contact:

Re: Problem with 10v spindle control

Post by cnckeith »

tblough wrote: Fri Jan 24, 2025 5:02 pm If it happens after a few days, it sounds like Windows sleeping the USB port and not waking it back up.
yeah! that would be a good place to look, could be windows setting or a bios setting.
Need support? READ THIS POST first. http://centroidcncforum.com/viewtopic.php?f=60&t=1043
All Acorn Documentation is located here: viewtopic.php?f=60&t=3397
Answers to common questions: viewforum.php?f=63
and here viewforum.php?f=61
Gear we use but don't sell. https://www.centroidcnc.com/centroid_di ... _gear.html


Jim Klawon
Posts: 8
Joined: Wed Sep 20, 2023 9:08 am
Acorn CNC Controller: Yes
Plasma CNC Controller: Yes
AcornSix CNC Controller: No
Allin1DC CNC Controller: No
Hickory CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: 7804733F0ECD-1231192780
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No

Re: Problem with 10v spindle control

Post by Jim Klawon »

I turned off the remote control, removed the dongle, and changed the WMPG setting in the PLC to "none". I then ran the spindle bench test with the spindle disconnected. All 4 voltage readings were within the specified range. (1.66v,3.38v,6.76v,10.13v) I ran the bench test again with the VFD connected. The first reading, measured at the VFD 0-10v input was 1.0v but steady. I entered the previous values so the test would let me move forward. All of the additional measurements were really low and began fluctuating more as the voltage was increased. The final reading, which should have been close to 10.13v, fluctuated between 1.7 -3.4v. It's as if something is drawing current from the Acorn 0-10v supply. To check the VFD, I connected a 9v battery to the 0-10v input. The voltage and current were both steady while the spindle was running.


Jim Klawon
Posts: 8
Joined: Wed Sep 20, 2023 9:08 am
Acorn CNC Controller: Yes
Plasma CNC Controller: Yes
AcornSix CNC Controller: No
Allin1DC CNC Controller: No
Hickory CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: 7804733F0ECD-1231192780
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No

Re: Problem with 10v spindle control

Post by Jim Klawon »

Here's a current ZIP
Attachments
report_7804733F0ECD-1231192780_2025-01-18_20-53-29.zip
(1.8 MiB) Downloaded 1 time


Post Reply