My opinion, for what it's worth:
If the probe and TT share a trip input, then there should be no problem with sharing a detect input (provided the control builder provides only one plug connection).
If the probe and TT use different trip inputs, then it would be reasonable to make separate detect inputs mandatory. Otherwise, there will be situations (such as F4/Auto on the Part Setup screen) where it is unclear which device is expected to trip.
If the probe and TT share a trip input, then there should be no problem with sharing a detect input (provided the control builder provides only one plug connection).
If the probe and TT use different trip inputs, then it would be reasonable to make separate detect inputs mandatory. Otherwise, there will be situations (such as F4/Auto on the Part Setup screen) where it is unclear which device is expected to trip.
(Note: Liking will "up vote" a post in the search results helping others find good information faster)
-
- Site Admin
- Posts: 8879
- Joined: Wed Mar 03, 2010 4:23 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: Yes
- Oak CNC controller: Yes
- CNC Control System Serial Number: none
- DC3IOB: Yes
- CNC11: Yes
- CPU10 or CPU7: Yes
- Contact:
Re: CNC12 BETA v5.23 rev5 is now available for public testing
and while we are on this subject, i'd like to implement an option to run any probing cycle in a "I don't care" mode. as in "I don't care what type of touch device input trips and I don't care if the probe is a NC or NO probe" While this mode is evoked, probing cycles will trigger off of any touch device input state change that occurs during a probing cycle.cncsnw wrote: ↑Wed Jan 22, 2025 6:48 pm My opinion, for what it's worth:
If the probe and TT share a trip input, then there should be no problem with sharing a detect input (provided the control builder provides only one plug connection).
If the probe and TT use different trip inputs, then it would be reasonable to make separate detect inputs mandatory. Otherwise, there will be situations (such as F4/Auto on the Part Setup screen) where it is unclear which device is expected to trip.
Need support? READ THIS POST first. http://centroidcncforum.com/viewtopic.php?f=60&t=1043
All Acorn Documentation is located here: viewtopic.php?f=60&t=3397
Answers to common questions: viewforum.php?f=63
and here viewforum.php?f=61
Gear we use but don't sell. https://www.centroidcnc.com/centroid_di ... _gear.html
All Acorn Documentation is located here: viewtopic.php?f=60&t=3397
Answers to common questions: viewforum.php?f=63
and here viewforum.php?f=61
Gear we use but don't sell. https://www.centroidcnc.com/centroid_di ... _gear.html
(Note: Liking will "up vote" a post in the search results helping others find good information faster)
-
- Community Expert
- Posts: 2978
- Joined: Fri May 24, 2019 8:34 am
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: 7804734C6498-0401191832
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
- Location: Clearwater, FL
Re: CNC12 BETA v5.23 rev5 is now available for public testing
On my small 3x5 router with Acorn I have 3 devices sharing the same input. I have both my movable and fixed tool touch offs and my probe all on the same input labeled "ProbeTripped". The fixed one is hard wired to the input and my movable tool touch off and my probe both have the same connector on the cable and both plug into a socket on the gantry and it also run back to the same input. Only the probe closes the "ProbeDetect" input when plugged in. All devices are of course NO devices and this works great and uses a single input. I have not tried this on an AcornSix build yet as I have inputs to spare.
I'm hoping you don't change anything with Acorn that will mess this up going forward.
I like Keith's idea.....I don't care.
I'm hoping you don't change anything with Acorn that will mess this up going forward.

I like Keith's idea.....I don't care.
(Note: Liking will "up vote" a post in the search results helping others find good information faster)
Re: CNC12 BETA v5.23 rev5 is now available for public testing
You will want to think that one through pretty carefully.cnckeith wrote: ↑Wed Jan 22, 2025 9:31 pm ... while we are on this subject, i'd like to implement an option to run any probing cycle in a "I don't care" mode. as in "I don't care what type of touch device input trips and I don't care if the probe is a NC or NO probe" While this mode is evoked, probing cycles will trigger off of any touch device input state change that occurs during a probing cycle.
At first glance, it sounds fool-proof, because motion will stop no matter what device is tripped, and regardless of whether the user managed to set up their parameters correctly.
But, as you describe it, you are also eliminating the opportunity to check whether the probe is already in a tripped state before the cycle begins. In that case, your cycle is going to move the probe into the part, waiting for a state change that never comes.
A safer definition might be: don't start until all probing devices are in the not-tripped state; and move until any probing device is in the tripped state. This does require that the tripped state be properly defined for each device.
(Note: Liking will "up vote" a post in the search results helping others find good information faster)
Re: CNC12 BETA v5.23 rev5 is now available for public testing
Another note on v5.23 beta rev5:
The Utility menu text still says "... support is avalible".
The Utility menu text still says "... support is avalible".
(Note: Liking will "up vote" a post in the search results helping others find good information faster)
-
- Site Admin
- Posts: 8879
- Joined: Wed Mar 03, 2010 4:23 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: Yes
- Oak CNC controller: Yes
- CNC Control System Serial Number: none
- DC3IOB: Yes
- CNC11: Yes
- CPU10 or CPU7: Yes
- Contact:
Re: CNC12 BETA v5.23 rev5 is now available for public testing
ah! we fixed that..its back
Need support? READ THIS POST first. http://centroidcncforum.com/viewtopic.php?f=60&t=1043
All Acorn Documentation is located here: viewtopic.php?f=60&t=3397
Answers to common questions: viewforum.php?f=63
and here viewforum.php?f=61
Gear we use but don't sell. https://www.centroidcnc.com/centroid_di ... _gear.html
All Acorn Documentation is located here: viewtopic.php?f=60&t=3397
Answers to common questions: viewforum.php?f=63
and here viewforum.php?f=61
Gear we use but don't sell. https://www.centroidcnc.com/centroid_di ... _gear.html
(Note: Liking will "up vote" a post in the search results helping others find good information faster)
Re: CNC12 v5.24 will soon be available for testing.
Release notes state:
Since the report*.txt file is supposed to be human-readable, I recommend using input and output numbers that count from 1, not from 0. In the above example, "Ax1_MinusLimitOk" was defined to be INP1, and "Ax2_PlusLimitOk" was defined to be INP4.
I also recommend using the native names: "INP1", "INP2", "OUT1", "OUT2". Writing it out as, for example "Output 2" promotes further confusion for Wizard users who already are not clear on the difference between OUT2 and OUTPUT2.
An example report*.txt file contains:17. Added PLC IO to the Report Summary
Code: Select all
PLC IO
Ax1_MinusLimitOk Input 0
Ax1_PlusLimitOk Input 1
Ax2_MinusLimitOk Input 2
Ax2_PlusLimitOk Input 3
... and so on
I also recommend using the native names: "INP1", "INP2", "OUT1", "OUT2". Writing it out as, for example "Output 2" promotes further confusion for Wizard users who already are not clear on the difference between OUT2 and OUTPUT2.
(Note: Liking will "up vote" a post in the search results helping others find good information faster)
-
- Site Admin
- Posts: 8879
- Joined: Wed Mar 03, 2010 4:23 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: Yes
- Oak CNC controller: Yes
- CNC Control System Serial Number: none
- DC3IOB: Yes
- CNC11: Yes
- CPU10 or CPU7: Yes
- Contact:
Re: CNC12 v5.24 will soon be available for testing.
thanks, i put this on the v5.30 list.cncsnw wrote: ↑Thu Jan 23, 2025 6:57 pm Release notes state:An example report*.txt file contains:17. Added PLC IO to the Report SummarySince the report*.txt file is supposed to be human-readable, I recommend using input and output numbers that count from 1, not from 0. In the above example, "Ax1_MinusLimitOk" was defined to be INP1, and "Ax2_PlusLimitOk" was defined to be INP4.Code: Select all
PLC IO Ax1_MinusLimitOk Input 0 Ax1_PlusLimitOk Input 1 Ax2_MinusLimitOk Input 2 Ax2_PlusLimitOk Input 3 ... and so on
I also recommend using the native names: "INP1", "INP2", "OUT1", "OUT2". Writing it out as, for example "Output 2" promotes further confusion for Wizard users who already are not clear on the difference between OUT2 and OUTPUT2.
thought i was going to have a v5.24 RC out this evening but it will be tomorrow.
Need support? READ THIS POST first. http://centroidcncforum.com/viewtopic.php?f=60&t=1043
All Acorn Documentation is located here: viewtopic.php?f=60&t=3397
Answers to common questions: viewforum.php?f=63
and here viewforum.php?f=61
Gear we use but don't sell. https://www.centroidcnc.com/centroid_di ... _gear.html
All Acorn Documentation is located here: viewtopic.php?f=60&t=3397
Answers to common questions: viewforum.php?f=63
and here viewforum.php?f=61
Gear we use but don't sell. https://www.centroidcnc.com/centroid_di ... _gear.html
(Note: Liking will "up vote" a post in the search results helping others find good information faster)
-
- Site Admin
- Posts: 8879
- Joined: Wed Mar 03, 2010 4:23 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: Yes
- Oak CNC controller: Yes
- CNC Control System Serial Number: none
- DC3IOB: Yes
- CNC11: Yes
- CPU10 or CPU7: Yes
- Contact:
Re: CNC12 v5.24 will soon be available for testing.
ok! turns out andrew made the improvements to the i/o reporting in the report.txt file and its in v5.24 rc4cnckeith wrote: ↑Thu Jan 23, 2025 7:19 pmthanks, will do.cncsnw wrote: ↑Thu Jan 23, 2025 6:57 pm Release notes state:An example report*.txt file contains:17. Added PLC IO to the Report SummarySince the report*.txt file is supposed to be human-readable, I recommend using input and output numbers that count from 1, not from 0. In the above example, "Ax1_MinusLimitOk" was defined to be INP1, and "Ax2_PlusLimitOk" was defined to be INP4.Code: Select all
PLC IO Ax1_MinusLimitOk Input 0 Ax1_PlusLimitOk Input 1 Ax2_MinusLimitOk Input 2 Ax2_PlusLimitOk Input 3 ... and so on
I also recommend using the native names: "INP1", "INP2", "OUT1", "OUT2". Writing it out as, for example "Output 2" promotes further confusion for Wizard users who already are not clear on the difference between OUT2 and OUTPUT2.
thought i was going to have a v5.24 RC out this evening but it will be tomorrow.
here is the download link. www.centroidcnc.com/centroid_diy/downlo ... taller.zip
thanks in advance for your testing efforts, bug reporting, and suggestions.
Need support? READ THIS POST first. http://centroidcncforum.com/viewtopic.php?f=60&t=1043
All Acorn Documentation is located here: viewtopic.php?f=60&t=3397
Answers to common questions: viewforum.php?f=63
and here viewforum.php?f=61
Gear we use but don't sell. https://www.centroidcnc.com/centroid_di ... _gear.html
All Acorn Documentation is located here: viewtopic.php?f=60&t=3397
Answers to common questions: viewforum.php?f=63
and here viewforum.php?f=61
Gear we use but don't sell. https://www.centroidcnc.com/centroid_di ... _gear.html
(Note: Liking will "up vote" a post in the search results helping others find good information faster)
-
- Posts: 30
- Joined: Thu Apr 07, 2022 5:34 pm
- Acorn CNC Controller: Yes
- Plasma CNC Controller: No
- AcornSix CNC Controller: No
- Allin1DC CNC Controller: No
- Hickory CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: E062347948F9-0324225805
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: Yes
- Location: Jacksonville Florida
Re: CNC12 v5.24 RC4 is now available for testing
For some apparent reason, the link doesn't work for me. When I click on it a window will flash but nothing happens.cnckeith wrote: ↑Wed Jan 15, 2025 6:44 pm fyi.. CNC12 v5.24 RC4 (RC = release candidate = no beta count down timer) is available for testing.
http://www.centroidcnc.com/centroid_diy/downloads/centroid_cnc12_download/centroid_cnc12_v5.24_rc4_installer.zip
CNC12 v5.24 RC DRAFT release notes are here:
www.centroidcnc.com/centroid_diy/downlo ... _notes.pdf

Blue Elephant 1318-4th axis Rotary, 6hp Spindle with Richauto B58 DSP controller converted to Centroid Acorn, Shopbot Desktop 2418 with 1.25hp HSD Spindle
Epilog Helix 50 watt C02 laser 18"x 24" work area
Graphtec FC8000-30" Vinyl cutter/Plotter
Software: Vectric Aspire 12.0v; Rhinoceros 8 with RhinoCAM 2018; Deskproto 8.0v; Autodesk Artcam Premium 2018; CorelDraw 2020; FlexiSign Pro 10.5v
Epilog Helix 50 watt C02 laser 18"x 24" work area
Graphtec FC8000-30" Vinyl cutter/Plotter
Software: Vectric Aspire 12.0v; Rhinoceros 8 with RhinoCAM 2018; Deskproto 8.0v; Autodesk Artcam Premium 2018; CorelDraw 2020; FlexiSign Pro 10.5v
(Note: Liking will "up vote" a post in the search results helping others find good information faster)