Help Connecting a JMC Integrated Servo - RESOLVED!
Moderator: cnckeith
-
- Posts: 349
- Joined: Wed Jan 03, 2018 10:04 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: 38D2695C8301-0122180576
- DC3IOB: No
- CNC11: No
- CPU10 or CPU7: No
- Location: NW Arkansas
Help Connecting a JMC Integrated Servo - RESOLVED!
I am connecting a JMC iHSS57-36-20 integrated servo to the Acorn. The manual describes three different ways to connect the motor; common anode, common cathode, and differential signal. I think the common cathode is the proper method, is this correct for the Acorn? Here is a link to the manual.
Also, any advice on how to connect the ALM+ ALM- and PED+ PED- lines to the Acorn?
Thanks,
Clint
Also, any advice on how to connect the ALM+ ALM- and PED+ PED- lines to the Acorn?
Thanks,
Clint
Last edited by cbb1962 on Mon Feb 12, 2018 10:35 am, edited 1 time in total.
Clint in NW Arkansas
The more I learn, the more I realize I don't know...
The more I learn, the more I realize I don't know...
-
- Posts: 390
- Joined: Fri Jan 10, 2014 11:29 am
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: Yes
- Oak CNC controller: Yes
- CNC Control System Serial Number: none
- DC3IOB: Yes
- CNC12: Yes
- CNC11: Yes
- CPU10 or CPU7: Yes
- Location: Howard, PA
Re: Help Connecting a JMC Integrated Servo
Use common anode with 24V VCC. Wire to the ACORN screw terminals.
ALM+, PED+ to ACORN inputs. ALM-, PED- to ACORN COM.
ALM+, PED+ to ACORN inputs. ALM-, PED- to ACORN COM.
-
- Posts: 349
- Joined: Wed Jan 03, 2018 10:04 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: 38D2695C8301-0122180576
- DC3IOB: No
- CNC11: No
- CPU10 or CPU7: No
- Location: NW Arkansas
Re: Help Connecting a JMC Integrated Servo
Thank you!
Clint in NW Arkansas
The more I learn, the more I realize I don't know...
The more I learn, the more I realize I don't know...
-
- Posts: 349
- Joined: Wed Jan 03, 2018 10:04 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: 38D2695C8301-0122180576
- DC3IOB: No
- CNC11: No
- CPU10 or CPU7: No
- Location: NW Arkansas
Re: Help Connecting a JMC Integrated Servo
I have figured out from various connection diagrams and the configuration wizard where to connect and how to configure the ALM+ ALM-.
According to the servo manual, the PED output from the motor is the Arrive Position. I know I could assign the PED- signal to an input, but I don't see how to configure that input in the wizard that even vaguely resembles an Arrive Position. What am I missing? Is the PED signal useful/needed?
Thanks
According to the servo manual, the PED output from the motor is the Arrive Position. I know I could assign the PED- signal to an input, but I don't see how to configure that input in the wizard that even vaguely resembles an Arrive Position. What am I missing? Is the PED signal useful/needed?
Thanks
Clint in NW Arkansas
The more I learn, the more I realize I don't know...
The more I learn, the more I realize I don't know...
-
- Posts: 349
- Joined: Wed Jan 03, 2018 10:04 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: 38D2695C8301-0122180576
- DC3IOB: No
- CNC11: No
- CPU10 or CPU7: No
- Location: NW Arkansas
Re: Help Connecting a JMC Integrated Servo
@cnckeith,
Is the PED output useful for the Acorn, and how would I configure it on the Acorn?
Is the PED output useful for the Acorn, and how would I configure it on the Acorn?
Clint in NW Arkansas
The more I learn, the more I realize I don't know...
The more I learn, the more I realize I don't know...
-
- Posts: 9915
- Joined: Tue Mar 28, 2017 12:01 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: Yes
- Oak CNC controller: No
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC12: Yes
- CNC11: Yes
- CPU10 or CPU7: Yes
- Location: Mesa, AZ
Re: Help Connecting a JMC Integrated Servo
I see no useful purpose in connecting the PED output put signal to Acorn. I could see it being useful in automation on a specific machine with repetitive tasks. That output could be monitored by a PLC before performing the next step in the operation sequence.
From some documentation I found:
"In-position Signal: OC output signal, activated when actual motor position reaches to target
position. This port can sink or source MAX 20mA current at 24V. By default, the impedance
between PED+ and PED- is high in normal operation and changed to low when the target
position is reached. The active impedance of in-position signal can be software configurable"
Reminder, for support please follow this post: viewtopic.php?f=20&t=383
We can't "SEE" what you see...
Mesa, AZ
We can't "SEE" what you see...
Mesa, AZ
-
- Posts: 349
- Joined: Wed Jan 03, 2018 10:04 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: 38D2695C8301-0122180576
- DC3IOB: No
- CNC11: No
- CPU10 or CPU7: No
- Location: NW Arkansas
Re: Help Connecting a JMC Integrated Servo
Thank you, Marty!
Clint in NW Arkansas
The more I learn, the more I realize I don't know...
The more I learn, the more I realize I don't know...
-
- Posts: 349
- Joined: Wed Jan 03, 2018 10:04 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: 38D2695C8301-0122180576
- DC3IOB: No
- CNC11: No
- CPU10 or CPU7: No
- Location: NW Arkansas
Re: Help Connecting a JMC Integrated Servo
I'm having trouble getting the motor to spin. I have watched the video series about bench testing a motor and configuring the wizard several times. I have connected everything according to the videos.
I have connected:
Motor PUL- to Acorn ST1
Motor DIR- to Acorn DR1
Motor ENA- to Acorn EN1
Motor PUL+, DIR+, and ENA+ to Acorn COM (the one beside EN1)
I have power to the motor, the shaft can't be turned by hand. I have configured the wizard only Axis 1 is enabled.
What am I missing?
I have connected:
Motor PUL- to Acorn ST1
Motor DIR- to Acorn DR1
Motor ENA- to Acorn EN1
Motor PUL+, DIR+, and ENA+ to Acorn COM (the one beside EN1)
I have power to the motor, the shaft can't be turned by hand. I have configured the wizard only Axis 1 is enabled.
What am I missing?
Clint in NW Arkansas
The more I learn, the more I realize I don't know...
The more I learn, the more I realize I don't know...
-
- Posts: 9915
- Joined: Tue Mar 28, 2017 12:01 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: Yes
- Oak CNC controller: No
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC12: Yes
- CNC11: Yes
- CPU10 or CPU7: Yes
- Location: Mesa, AZ
Re: Help Connecting a JMC Integrated Servo
According to the schematic, you are supposed to connect a +5vdc OR +24vdc power supply to the drive's step/dir/ena + terminals. See eng199s comment above.
So no to Acorn common, yes to Connecting to Acorn +24vdc
Marty
So no to Acorn common, yes to Connecting to Acorn +24vdc
Marty
Reminder, for support please follow this post: viewtopic.php?f=20&t=383
We can't "SEE" what you see...
Mesa, AZ
We can't "SEE" what you see...
Mesa, AZ
-
- Posts: 349
- Joined: Wed Jan 03, 2018 10:04 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: 38D2695C8301-0122180576
- DC3IOB: No
- CNC11: No
- CPU10 or CPU7: No
- Location: NW Arkansas
Re: Help Connecting a JMC Integrated Servo
Marty,
I connected to Acorn +24VDC, when I try to jog the X - I get an alarm light on the motor. It goes away when the e-stop is reset. According to the manual, this means the current too high or too low, however, it is within tolerance.
I connected to Acorn +24VDC, when I try to jog the X - I get an alarm light on the motor. It goes away when the e-stop is reset. According to the manual, this means the current too high or too low, however, it is within tolerance.
11.2 Power on red alarm light on
- Please check the motor feedback signal and if the motor is connected
with the drive.
- The stepper servo drive is over voltage or under voltage. Please
lower or increase the input voltage
Clint in NW Arkansas