Hickory input loss

All things ecat Hickory CNC controller

Moderator: cnckeith

Post Reply
darin
Posts: 10
Joined: Tue Aug 06, 2024 4:42 pm
Acorn CNC Controller: No
Plasma CNC Controller: No
AcornSix CNC Controller: No
Allin1DC CNC Controller: No
Hickory CNC Controller: Yes
Oak CNC controller: No
CNC Control System Serial Number: 0008dc11121304225240147
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No

Hickory input loss

Post by darin »

all plc inputs suddenly go off and we lose Hickory coms.


darin
Posts: 10
Joined: Tue Aug 06, 2024 4:42 pm
Acorn CNC Controller: No
Plasma CNC Controller: No
AcornSix CNC Controller: No
Allin1DC CNC Controller: No
Hickory CNC Controller: Yes
Oak CNC controller: No
CNC Control System Serial Number: 0008dc11121304225240147
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No

Re: Hickory input loss

Post by darin »

I think I found the problem, I was not cycling power to the hickory after a program change.


darin
Posts: 10
Joined: Tue Aug 06, 2024 4:42 pm
Acorn CNC Controller: No
Plasma CNC Controller: No
AcornSix CNC Controller: No
Allin1DC CNC Controller: No
Hickory CNC Controller: Yes
Oak CNC controller: No
CNC Control System Serial Number: 0008dc11121304225240147
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No

Re: Hickory input loss

Post by darin »

Scratch that still having the same problem.
When the system goes down, all inputs on the plc monitoring screen go red but all inputs on the hickory board are still energized.
The Yaskawa drives for z and x go into a "aa12" fault. This does not happen right at start up but rather after the machine has been
on for awhile.


tblough
Community Expert
Posts: 3531
Joined: Tue Mar 22, 2016 10:03 am
Acorn CNC Controller: Yes
Allin1DC CNC Controller: Yes
Oak CNC controller: Yes
CNC Control System Serial Number: 100505
100327
102696
103432
7804732B977B-0624192192
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No
Location: Boston, MA
Contact:

Re: Hickory input loss

Post by tblough »

Inputs are just that - inputs. Hickory does not turn those on or off. The external devices you have connected to those inputs determine whether they are on or off.

You will probably need to provide a lot more information if you want meaningful help. Detailed photos of your machine and wiring, a video of the problem occuring, a list of components you used and the wiring diagram for your machine.
Cheers,

Tom
Confidence is the feeling you have before you fully understand the situation.
I have CDO. It's like OCD, but the letters are where they should be.


eng199
Posts: 446
Joined: Fri Jan 10, 2014 11:29 am
Acorn CNC Controller: Yes
Plasma CNC Controller: No
AcornSix CNC Controller: Yes
Allin1DC CNC Controller: Yes
Hickory CNC Controller: Yes
Oak CNC controller: Yes
CNC Control System Serial Number: none
DC3IOB: Yes
CNC12: Yes
CNC11: Yes
CPU10 or CPU7: Yes
Location: Howard, PA

Re: Hickory input loss

Post by eng199 »

I assume the drive error is A12 "EtherCAT Outputs Data Synchronization Error".
The EtherCAT chain failed 13 minutes after start.

Check the routing, condition, and type of the RJ45/Ethernet cables. Check for any coils without snubbers or high power devices switching near the time of failure. The chain from HICKORY to the drives and jog panel is having a problem (not the cable from HICKORY to PC).


darin
Posts: 10
Joined: Tue Aug 06, 2024 4:42 pm
Acorn CNC Controller: No
Plasma CNC Controller: No
AcornSix CNC Controller: No
Allin1DC CNC Controller: No
Hickory CNC Controller: Yes
Oak CNC controller: No
CNC Control System Serial Number: 0008dc11121304225240147
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No

Re: Hickory input loss

Post by darin »

The system has been up and running for several days with centroid supplied ecat cables with no changes to the routing.
The machine is idle when this happens, nothing being energized or de-energized and the x and z are not in motion.
The only coils without snubbers are the e-stop relays and that will be addressed.
The normal inputs are energized as show by the following attachment
hickory.jpg
The PLC monitor in CNC12 is falsely reporting that the inputs are de-energized as show by the following attachment
cnc12.jpg


darin
Posts: 10
Joined: Tue Aug 06, 2024 4:42 pm
Acorn CNC Controller: No
Plasma CNC Controller: No
AcornSix CNC Controller: No
Allin1DC CNC Controller: No
Hickory CNC Controller: Yes
Oak CNC controller: No
CNC Control System Serial Number: 0008dc11121304225240147
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No

Re: Hickory input loss

Post by darin »

Correct pic for Hickory board
hickory board.jpg


eng199
Posts: 446
Joined: Fri Jan 10, 2014 11:29 am
Acorn CNC Controller: Yes
Plasma CNC Controller: No
AcornSix CNC Controller: Yes
Allin1DC CNC Controller: Yes
Hickory CNC Controller: Yes
Oak CNC controller: Yes
CNC Control System Serial Number: none
DC3IOB: Yes
CNC12: Yes
CNC11: Yes
CPU10 or CPU7: Yes
Location: Howard, PA

Re: Hickory input loss

Post by eng199 »

Create a report before the error occurs, around 10 minutes after start up. This may provide additional clues about what is going on. The slaves are already down before the other report, so no information could be retrieved from them.


darin
Posts: 10
Joined: Tue Aug 06, 2024 4:42 pm
Acorn CNC Controller: No
Plasma CNC Controller: No
AcornSix CNC Controller: No
Allin1DC CNC Controller: No
Hickory CNC Controller: Yes
Oak CNC controller: No
CNC Control System Serial Number: 0008dc11121304225240147
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No

Re: Hickory input loss

Post by darin »

I temporally rerouted the Ecat cables with that being said its been up for about 20 hours with no problems.
The next issue is that this is a vertical lathe and Z axis is having trouble with inertia in a -Z move.
Can you help size a regen resistor.


Post Reply