Emerson HS71 VFD (resolved)

All things related to the Centroid Acorn CNC Controller

Moderator: cnckeith

Post Reply
Ken Rychlik
Posts: 383
Joined: Wed Jan 23, 2019 4:19 pm
Acorn CNC Controller: Yes
Allin1DC CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: 80F5B5B92C3A-0213236854
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No

Emerson HS71 VFD (resolved)

Post by Ken Rychlik »

I can get it into keypad mode. (It was set up with ethernet control from axyz)
I can't seem to get it into remote mode to work with 0-10v and relay switching.

I ran 26 to 22 for a on relay switch
I have tried mulitple options on the 0-10v

I think it needs to be in A1 A2 on param 5.

Resolved: For anyone having trouble do an online chat with Emerson in Canada. Several things had to be changed, but depending on your model it may be different. The phone calls to Yaskawa have been great, so I decided to try Emerson. Positive results and all is working correct.

Thanks
Attachments
unidrive-hs70_71_72-user-guide-issue-1-0478-0231-01.pdf
(11.35 MiB) Downloaded 1 time
Last edited by Ken Rychlik on Wed May 29, 2024 2:55 pm, edited 2 times in total.
Ken
Gary Campbell
Posts: 2236
Joined: Sat Nov 18, 2017 2:32 pm
Acorn CNC Controller: Yes
Plasma CNC Controller: No
AcornSix CNC Controller: Yes
Allin1DC CNC Controller: No
Hickory CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: Acorn 238
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No
Location: Bergland, MI, USA
Contact:

Re: Emerson HS71 VFD

Post by Gary Campbell »

Are you able to change vfd parameters? I have retrofit a number of AXYZ machines and they have a habit of locking out vfd changes and will not provide the password code.
GCnC Control
CNC Control & Retrofits
https://www.youtube.com/user/Islaww1/videos
Ken Rychlik
Posts: 383
Joined: Wed Jan 23, 2019 4:19 pm
Acorn CNC Controller: Yes
Allin1DC CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: 80F5B5B92C3A-0213236854
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No

Re: Emerson HS71 VFD

Post by Ken Rychlik »

Gary Campbell wrote: Sun May 26, 2024 9:14 pm Are you able to change vfd parameters? I have retrofit a number of AXYZ machines and they have a habit of locking out vfd changes and will not provide the password code.
I was able to change param 5 to keypad and it does run the spindle. I changed acel and decel and it responded.

I have spindle speed 0-10v tied to input 5 for the + and the neg of that to 3 with a jumper to 6.
The run signal I have tied to 22 and 26. It has a jumper to 31 and it needs that to run.

I am wondering if there is another parm to put it into terminal mode.

Ken
Attachments
Screenshot 2024-05-26 213715.jpg
Ken
Ken Rychlik
Posts: 383
Joined: Wed Jan 23, 2019 4:19 pm
Acorn CNC Controller: Yes
Allin1DC CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: 80F5B5B92C3A-0213236854
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No

Re: Emerson HS71 VFD

Post by Ken Rychlik »

I was able to get into advanced parameters and under 01 there was a spot that showed spindle speed percentage on A1. I touched my 9v batter to the leads for speed and it went to 87% so that is promising, At least it is understanding my 0-10v somewhere.