I/O mapping for M94/95

All things related to the Centroid Acorn CNC Controller

Moderator: cnckeith

Post Reply
kman1967
Posts: 108
Joined: Wed Feb 16, 2022 2:09 pm
Acorn CNC Controller: Yes
Allin1DC CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No

I/O mapping for M94/95

Post by kman1967 »

Wondering if there is a document available that lists the I/O mapping for M94/95. I would like to force some inputs on the Ether1616 card in a macro.


suntravel
Community Expert
Posts: 3651
Joined: Thu Sep 23, 2021 3:49 pm
Acorn CNC Controller: Yes
Allin1DC CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: 6433DB0446C1-08115074
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No
Location: Germany

Re: I/O mapping for M94/95

Post by suntravel »

M94/1 Output 1
M94/2 Output 2

....

Uwe


cncsnw
Community Expert
Posts: 4592
Joined: Wed Mar 24, 2010 5:48 pm

Re: I/O mapping for M94/95

Post by cncsnw »

No.

M94/1 sends request #1 to the PLC program. What physical PLC output it affects, if any, depends entirely on PLC logic.

In the case of Acorn controls, the PLC logic in turn depends on your Wizard output selections.

The outputs on the first Ether1616 board are OUT33 - OUT48.

There are no M94/M95 request numbers that specifically turn, say, OUT33 on or off.

If you do not want to do any of your own PLC programming, then you are limited to what the Acorn wizard provides.

You could assign the name "OUTPUT1" (which is not the same thing as OUT1, the first output on the Acorn board) to OUT33. If you do that, then you could use M94/61 or the provided M61 macro to turn it on, and M95/61 or the provided M81 macro to turn it off.

Regarding Uwe's examples:
M94/1 turns on request #1, which in all standard PLC programs is the M3 run-spindle-forward request.
M94/2 turns on request #2, which in all standard PLC programs is the M4 run-spindle-reverse request.
Whether either of those codes turns an output relay on or off depends on whether and where you have assigned SpindleEnableOut, SpindleDirectionOut, SpindleFwd, or SpindleRev; and also depends on whether the rest of the PLC logic would allow the spindle to be started with an auto mode request.


suntravel
Community Expert
Posts: 3651
Joined: Thu Sep 23, 2021 3:49 pm
Acorn CNC Controller: Yes
Allin1DC CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: 6433DB0446C1-08115074
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No
Location: Germany

Re: I/O mapping for M94/95

Post by suntravel »

current M94 assignment of you setup is in the PLC,

Here an example

Code: Select all

;------------------------------------------------------------------------------
; M functions - The System Variables in this section inform the
; PLC that an M function has been requested.
;------------------------------------------------------------------------------
M3                            IS SV_M94_M95_1 ;(Spindle CW)
M4                            IS SV_M94_M95_2 ;(Spindle CCW)
M8                            IS SV_M94_M95_3 ;(Flood On)
M10L                          IS SV_M94_M95_4 ;SET OpenChuck, RST CloseChuck
M7                            IS SV_M94_M95_5 ;(Mist)
M11L                          IS SV_M94_M95_6 ;RST OpenChuck, SET CloseChuck
M6                            IS SV_M94_M95_7 ;
ManualLubePump_SV             IS SV_M94_M95_8 ;Activates LubePump Manually
;                             IS SV_M94_M95_9 ;
M10M                          IS SV_M94_M95_10; SET TurnClampOn, M11 RST TurnClampOn
;                             IS SV_M94_M95_11;
;                             IS SV_M94_M95_12;
M13                           IS SV_M94_M95_13; Cutoff On, M14 Cutoff Off
;                             IS SV_M94_M95_14;
M15                           IS SV_M94_M95_15; M15 Tool Unclamp On, M16 Tool Unclamp Off
;                             IS SV_M94_M95_16;

M18							  IS SV_M94_M95_18;

M19                           IS SV_M94_M95_19;(Spindle Orient), M20 Off
;                             IS SV_M94_M95_20;

M22                           IS SV_M94_M95_22; Turn on PartChute, M23 off
;                             IS SV_M94_M95_23;

M27                           IS SV_M94_M95_27; Turn on VacuumOn, M28 off

DustFootActivate_SV           IS SV_M94_M95_28; DustFootActivate Output
LaserAlignActivate_SV		  IS SV_M94_M95_29; LaserAlignActivate Output
PopUpPins_SV				  IS SV_M94_M95_30; PopUpPins Output
SpindleCooling_SV			  IS SV_M94_M95_31; SpindleCooling Output

M32							  IS SV_M94_M95_32; TailStockInOut On, M33 TailStockInOut Off

M35                           IS SV_M94_M95_35; SET DustCollectionOn, M36 RST DustCollectionOn

M37                           IS SV_M94_M95_37; Set Laser Enable
PWMSelect_SV                  IS SV_M94_m95_38; Set PWMSelect
LaserReset_SV				  IS SV_M94_M95_39; Set LaserReset

PutbackComplete_SV			  IS SV_M94_M95_40;
M41                           IS SV_M94_M95_41 ;(Spindle Low Range)
M42                           IS SV_M94_M95_42 ;(Spindle Medium Low Range)
M43                           IS SV_M94_M95_43 ;(Spindle Medium High Range)

OscillationOn_SV              IS SV_M94_M95_46 ;(OscillationOn)

M51_SV                        IS SV_M94_M95_51 ;(C-Axis Enable)

M61                           IS SV_M94_M95_61; OUTPUT1 (NOT the same as OUT1), M81 Off
M62                           IS SV_M94_M95_62; OUTPUT2 (NOT the same as OUT2), M82 Off
M63                           IS SV_M94_M95_63; OUTPUT3 (NOT the same as OUT3), M83 Off
M64                           IS SV_M94_M95_64; OUTPUT4 (NOT the same as OUT4), M84 Off
M65                           IS SV_M94_M95_65; OUTPUT5 (NOT the same as OUT5), M85 Off
M66                           IS SV_M94_M95_66; OUTPUT6 (NOT the same as OUT6), M86 Off
M67                           IS SV_M94_M95_67; OUTPUT7 (NOT the same as OUT7), M87 Off
M68                           IS SV_M94_M95_68; OUTPUT8 (NOT the same as OUT8), M88 Off

M80_SV						  IS SV_M94_M95_80; (CarouselIn)
M81_SV						  IS SV_M94_M95_81; (CarouselOut)

DisableAxis1Limit             IS SV_M94_M95_101
DisableAxis2Limit             IS SV_M94_M95_102
DisableAxis3Limit             IS SV_M94_M95_103
DisableAxis4Limit             IS SV_M94_M95_104

M94M95111_SV					  IS SV_M94_M95_111
M94M95112_SV					  IS SV_M94_M95_112
M94M95113_SV					  IS SV_M94_M95_113
M94M95114_SV					  IS SV_M94_M95_114
M94M95115_SV					  IS SV_M94_M95_115
M94M95116_SV					  IS SV_M94_M95_116
M94M95117_SV					  IS SV_M94_M95_117
M94M95118_SV					  IS SV_M94_M95_118
M94M95119_SV					  IS SV_M94_M95_119
M94M95120_SV					  IS SV_M94_M95_120
M94M95121_SV					  IS SV_M94_M95_121
M94M95122_SV					  IS SV_M94_M95_122
M94M95123_SV					  IS SV_M94_M95_123
M94M95124_SV					  IS SV_M94_M95_124
M94M95125_SV					  IS SV_M94_M95_125
M94M95126_SV					  IS SV_M94_M95_126


suntravel
Community Expert
Posts: 3651
Joined: Thu Sep 23, 2021 3:49 pm
Acorn CNC Controller: Yes
Allin1DC CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: 6433DB0446C1-08115074
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No
Location: Germany

Re: I/O mapping for M94/95

Post by suntravel »



de4thm4st3r
Posts: 1
Joined: Wed Nov 01, 2023 7:47 am
Acorn CNC Controller: Yes
Plasma CNC Controller: No
AcornSix CNC Controller: No
Allin1DC CNC Controller: No
Hickory CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No

Re: I/O mapping for M94/95

Post by de4thm4st3r »

I need some help with my DIY cnc milling machine. I am trying to take over control of the spindle motor.
I have successfully done it with an arduino nano, and a little bit of code. The thing is I would like to control it with the acorn
alone. But I need to turn on/off a relay for the mill too start, and on/off for the mill to stop. and also for reverse. example
relay #1 relay #2
on/off = spincw
on/off = spinstop
on/off = spincw on/off=spinccw
on/off = spinstop on/off=spincw

the controller in the mill works with momentary buttons. so my hope is I can edit the m3/m4/m5 macros and get the mill
to run without the need of a seperate microcontroller. but i am not entirely sure how to do this, yet. Any help would be amazing, Thanks in advance


cnckeith
Site Admin
Posts: 8956
Joined: Wed Mar 03, 2010 4:23 pm
Acorn CNC Controller: Yes
Allin1DC CNC Controller: Yes
Oak CNC controller: Yes
CNC Control System Serial Number: none
DC3IOB: Yes
CNC11: Yes
CPU10 or CPU7: Yes
Contact:

Re: I/O mapping for M94/95

Post by cnckeith »

de4thm4st3r wrote: Tue Aug 27, 2024 9:47 pm I need some help with my DIY cnc milling machine. I am trying to take over control of the spindle motor.
I have successfully done it with an arduino nano, and a little bit of code. The thing is I would like to control it with the acorn
alone. But I need to turn on/off a relay for the mill too start, and on/off for the mill to stop. and also for reverse. example
relay #1 relay #2
on/off = spincw
on/off = spinstop
on/off = spincw on/off=spinccw
on/off = spinstop on/off=spincw

the controller in the mill works with momentary buttons. so my hope is I can edit the m3/m4/m5 macros and get the mill
to run without the need of a seperate microcontroller. but i am not entirely sure how to do this, yet. Any help would be amazing, Thanks in advance

please start your own thread. please follow the posting guidelines so we can give you good advice.
viewtopic.php?f=60&t=1043
Need support? READ THIS POST first. http://centroidcncforum.com/viewtopic.php?f=60&t=1043
All Acorn Documentation is located here: viewtopic.php?f=60&t=3397
Answers to common questions: viewforum.php?f=63
and here viewforum.php?f=61
Gear we use but don't sell. https://www.centroidcnc.com/centroid_di ... _gear.html


Post Reply