Lube Pump Alarm 405 on M400s
Moderator: cnckeith
-
- Community Expert
- Posts: 4660
- Joined: Wed Mar 24, 2010 5:48 pm
- Acorn CNC Controller: No
- Plasma CNC Controller: No
- AcornSix CNC Controller: No
- Allin1DC CNC Controller: No
- Hickory CNC Controller: No
- Oak CNC controller: No
Re: Lube Pump Alarm 405 on M400s
If there is nothing plugged into H2 (the smaller power header), then I assume you have a 4-wire plug from the power supply plugged into H3 (the larger power header)?
What is the DC voltage between the yellow wire and either black wire, on the power plug on H3?
What is the DC voltage between the yellow wire and either black wire, on the power plug on H3?
(Note: Liking will "up vote" a post in the search results helping others find good information faster)
-
- Community Expert
- Posts: 4660
- Joined: Wed Mar 24, 2010 5:48 pm
- Acorn CNC Controller: No
- Plasma CNC Controller: No
- AcornSix CNC Controller: No
- Allin1DC CNC Controller: No
- Hickory CNC Controller: No
- Oak CNC controller: No
Re: Lube Pump Alarm 405 on M400s
Also, what is your control serial number?
It would be on the door of the control cabinet, and also on the back or side of the console.
It is probably somewhere in the neighborhood of 20170.
It would be on the door of the control cabinet, and also on the back or side of the console.
It is probably somewhere in the neighborhood of 20170.
(Note: Liking will "up vote" a post in the search results helping others find good information faster)
-
- Posts: 40
- Joined: Wed Aug 14, 2019 11:29 pm
- Acorn CNC Controller: Yes
- Plasma CNC Controller: No
- AcornSix CNC Controller: No
- Allin1DC CNC Controller: No
- Hickory CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: many
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: Yes
- Location: New Jersey
- Contact:
Re: Lube Pump Alarm 405 on M400s
i have a blurry pic at home with me looks like 20192 i can verify in the morning
thanks
Joe
thanks
Joe
(Note: Liking will "up vote" a post in the search results helping others find good information faster)
-
- Posts: 40
- Joined: Wed Aug 14, 2019 11:29 pm
- Acorn CNC Controller: Yes
- Plasma CNC Controller: No
- AcornSix CNC Controller: No
- Allin1DC CNC Controller: No
- Hickory CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: many
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: Yes
- Location: New Jersey
- Contact:
Re: Lube Pump Alarm 405 on M400s
verified SN #20192
(Note: Liking will "up vote" a post in the search results helping others find good information faster)
-
- Posts: 40
- Joined: Wed Aug 14, 2019 11:29 pm
- Acorn CNC Controller: Yes
- Plasma CNC Controller: No
- AcornSix CNC Controller: No
- Allin1DC CNC Controller: No
- Hickory CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: many
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: Yes
- Location: New Jersey
- Contact:
Re: Lube Pump Alarm 405 on M400s
sorry i missed this onecncsnw wrote: ↑Wed Feb 08, 2023 8:09 pm If there is nothing plugged into H2 (the smaller power header), then I assume you have a 4-wire plug from the power supply plugged into H3 (the larger power header)?
What is the DC voltage between the yellow wire and either black wire, on the power plug on H3?
Yes there is a 4 wire plug plugged into H2
Yellow and either black 12v
Yellow and either red 5v
(Note: Liking will "up vote" a post in the search results helping others find good information faster)
-
- Community Expert
- Posts: 4660
- Joined: Wed Mar 24, 2010 5:48 pm
- Acorn CNC Controller: No
- Plasma CNC Controller: No
- AcornSix CNC Controller: No
- Allin1DC CNC Controller: No
- Hickory CNC Controller: No
- Oak CNC controller: No
Re: Lube Pump Alarm 405 on M400s
I assume you meant red to black was 5V. If so, then your power supply is okay.Yellow and either black 12v
Yellow and either red 5v
Blacks are commons (0VDC)
Red is the +5VDC supply
Yellow is the +12VDC supply.
It is likely that your SERVO3IO unit has an on-board failure in the drive section, and will need to be sent to Centroid for repair or swap-out. I recommend contacting Centroid Tech Support to get an RMA and find out availability of a swap-out unit.
(Note: Liking will "up vote" a post in the search results helping others find good information faster)
-
- Posts: 40
- Joined: Wed Aug 14, 2019 11:29 pm
- Acorn CNC Controller: Yes
- Plasma CNC Controller: No
- AcornSix CNC Controller: No
- Allin1DC CNC Controller: No
- Hickory CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: many
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: Yes
- Location: New Jersey
- Contact:
Re: Lube Pump Alarm 405 on M400s
Ok i will give them a call. thank you so much for your help.
Joe
Joe
(Note: Liking will "up vote" a post in the search results helping others find good information faster)
-
- Site Admin
- Posts: 9083
- Joined: Wed Mar 03, 2010 4:23 pm
- Acorn CNC Controller: Yes
- Plasma CNC Controller: No
- AcornSix CNC Controller: No
- Allin1DC CNC Controller: Yes
- Hickory CNC Controller: No
- Oak CNC controller: Yes
- CNC Control System Serial Number: none
- DC3IOB: Yes
- CNC11: Yes
- CPU10 or CPU7: Yes
- Contact:
Re: Lube Pump Alarm 405 on M400s
Need support? READ THIS POST first. http://centroidcncforum.com/viewtopic.php?f=60&t=1043
All Acorn Documentation is located here: viewtopic.php?f=60&t=3397
Answers to common questions: viewforum.php?f=63
Gear we use but don't sell. https://www.centroidcnc.com/centroid_di ... _gear.html
All Acorn Documentation is located here: viewtopic.php?f=60&t=3397
Answers to common questions: viewforum.php?f=63
Gear we use but don't sell. https://www.centroidcnc.com/centroid_di ... _gear.html
(Note: Liking will "up vote" a post in the search results helping others find good information faster)
-
- Posts: 40
- Joined: Wed Aug 14, 2019 11:29 pm
- Acorn CNC Controller: Yes
- Plasma CNC Controller: No
- AcornSix CNC Controller: No
- Allin1DC CNC Controller: No
- Hickory CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: many
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: Yes
- Location: New Jersey
- Contact:
Re: Lube Pump Alarm 405 on M400s
thanks Keith, sent email to support at 10:30 this morning. waiting to hear back
Joe