Huanyang VFD Settings - Trying to understand.
Moderator: cnckeith
-
- Posts: 86
- Joined: Sat Feb 27, 2021 10:55 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: E415F6F2C7C9-0211214367
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
- Location: Quincy, MA
Re: Huanyang VFD Settings - Trying to understand.
If your interested you can have this Delta VFD, just pay the shipping, works fine. Building a new control cabinet and went with a different inverter.
Bill
Bill
-
- Posts: 79
- Joined: Fri Aug 05, 2022 8:58 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
Re: Huanyang VFD Settings - Trying to understand.
Oh wow! That is incredibly generous of you!
I noticed it is 220V and presently I only have 120. But I was thinking of running 220 anyway.
However, it appears that the input is 220V 3 phase. Will it run off of regualar 220V (single phase) at a home residence?
Again, I am shocked at your genersosity!
And I very much appreciate the help of everyone else that has given input on this VFD issue. Slowly I am learning.
I noticed it is 220V and presently I only have 120. But I was thinking of running 220 anyway.
However, it appears that the input is 220V 3 phase. Will it run off of regualar 220V (single phase) at a home residence?
Again, I am shocked at your genersosity!
And I very much appreciate the help of everyone else that has given input on this VFD issue. Slowly I am learning.
-
- Posts: 388
- Joined: Tue Dec 11, 2018 4:03 pm
- Acorn CNC Controller: Yes
- Plasma CNC Controller: No
- AcornSix CNC Controller: No
- Allin1DC CNC Controller: No
- Hickory CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: F045DA80C8B8-0905181172
E415F6F70BC3-0318203049
98F07B91FC6B-0123236802 - DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
- Location: UK East Coast
Re: Huanyang VFD Settings - Trying to understand.
I'm no expert but it still seems 9 amps setting is incorrect. If you configure your online calculator with line to line voltage instead of line to neutral (assuming only 3 power wires + ground between VFD and spindle i.e. no 4th wire neutral) and a power factor of 0.8 (80 being stamped on motor next to PF symbol) you will see considerably higher than 9 amps.
Hope this helps
Hope this helps
Hope this helps
Nigel
"You can lead a horse to water but you cannot force it to drink"
Nigel
"You can lead a horse to water but you cannot force it to drink"
-
- Posts: 86
- Joined: Sat Feb 27, 2021 10:55 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: E415F6F2C7C9-0211214367
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
- Location: Quincy, MA
Re: Huanyang VFD Settings - Trying to understand.
It runs on 1PH 220v.
here is a link for the manual
https://downloadcenter.deltaww.com/down ... 1&hl=en-US
here is a link for the manual
https://downloadcenter.deltaww.com/down ... 1&hl=en-US
-
- Posts: 79
- Joined: Fri Aug 05, 2022 8:58 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
Re: Huanyang VFD Settings - Trying to understand.
In that case I would love to give this a try! It may take a bit before I can afford to run 220 to my shop and purchase a 220 spindle, but I have a 220 bench and access to a 3ph motor at work and I can at least learn the interface! I have been trying to understand VFDs and this will help tremendously!bleiler60 wrote: ↑Sun Nov 13, 2022 5:18 pm It runs on 1PH 220v.
here is a link for the manual
https://downloadcenter.deltaww.com/down ... 1&hl=en-US
I will send a private message with my details.
-
- Posts: 79
- Joined: Fri Aug 05, 2022 8:58 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
Re: Huanyang VFD Settings - Trying to understand.
Nigelo wrote: ↑Sun Nov 13, 2022 5:00 pm I'm no expert but it still seems 9 amps setting is incorrect. If you configure your online calculator with line to line voltage instead of line to neutral (assuming only 3 power wires + ground between VFD and spindle i.e. no 4th wire neutral) and a power factor of 0.8 (80 being stamped on motor next to PF symbol) you will see considerably higher than 9 amps.
Hope this helps
You might not be an expert but I'll wager that you know more than I do so I am grateful for your input.
I would really need to see a wiring diagram of the spindle motor. If the motor was a delta winding then no neutral would be needed and I would think that Line to Line would be the right way to go. If the motor is using a star winding then I would think that the line to neutral would be it.
I really wish I knew.
I work for a utility company. I think I may call the motor shop tomorrow and pick their brains.
-
- Posts: 79
- Joined: Fri Aug 05, 2022 8:58 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
Re: Huanyang VFD Settings - Trying to understand.
Ok.... I found the issue. Or maybe I should say I was given something to try and it worked. I wrote to Huanyang Electrical and they told me all of the same things I was getting here. After a few messages they told me to try the setting below:
PD070=0 (This may need to be set to 1 if Control Voltage is 0-5v)
I originally left it at 0 since I will be using the Acorn to control the VFD eventually.
I switched it to 1 and it allowed me to reach the 400Hz/24kRPM. (From the pot on the front panel)
I guess I will have to play with it when I connect it to the Acorn this weekend.
PD070=0 (This may need to be set to 1 if Control Voltage is 0-5v)
I originally left it at 0 since I will be using the Acorn to control the VFD eventually.
I switched it to 1 and it allowed me to reach the 400Hz/24kRPM. (From the pot on the front panel)
I guess I will have to play with it when I connect it to the Acorn this weekend.
-
- Posts: 2333
- Joined: Fri May 24, 2019 8:34 am
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: 7804734C6498-0401191832
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
- Location: Clearwater, FL
Re: Huanyang VFD Settings - Trying to understand.
Glad you got it sorted out. Make sure you run the spindle bench test one last time before you hook it up to Acorn. And don't forget to set PD070 to 0 when you do. ![Very Happy :D](./images/smilies/icon_e_biggrin.gif)
You will probably need a .1 MFD cap to place across the analog output of Acorn for a stable signal and RPM.
![Very Happy :D](./images/smilies/icon_e_biggrin.gif)
You will probably need a .1 MFD cap to place across the analog output of Acorn for a stable signal and RPM.
-
- Posts: 79
- Joined: Fri Aug 05, 2022 8:58 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
Re: Huanyang VFD Settings - Trying to understand.
Thanks! I just happen to have .1 MFD caps as I was using them to make snubber circuits for the contactors.
-
- Posts: 79
- Joined: Fri Aug 05, 2022 8:58 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
Re: Huanyang VFD Settings - Trying to understand.
Looks like you were right! While I had an e-mail thread going with Huanyang I asked them about the amps and number of poles.Nigelo wrote: ↑Sun Nov 13, 2022 5:00 pm I'm no expert but it still seems 9 amps setting is incorrect. If you configure your online calculator with line to line voltage instead of line to neutral (assuming only 3 power wires + ground between VFD and spindle i.e. no 4th wire neutral) and a power factor of 0.8 (80 being stamped on motor next to PF symbol) you will see considerably higher than 9 amps.
Hope this helps
This was their response.
HI , PD142 and PD143 , these parameters do not need to be set because the default parameters of the VFD are sufficient. Has been able to correctly match the motor
If you still want to know. The rated current is 20A and the spindle is 2 poles.Thanks