All,
A few years ago I retrofitted my lathe with Acorn with a Ether1616 expansion board and things have been working great. On Monday during normal a routine turning operation the machine stopped and fault called out. unable to restart software for any movement. After a little investigating found the power supply for the expansion board was not online. I thought power supply went bad. Ordered new power supply and installed it this morning. I still have same indications.
I removed wires the load side of powers supply and the power supply then comes online.
I re-attached the wires to power supply and disconnected the power connection from acorn board. Power supply powers up fine.
I re-attached the power connector and disconnected the connector from the inputs and ribbon cable going to output relay boards. Power supply does not come online.
I think there is a short somewhere in the expansion board. I removed and expansion board and did visual inspection and did not see and indication of faulty component (no burnt marks or any other damage).
Is there any testing I can do with the expansion board to verify the problem? I am not one for Easter egg hunting to fix a problem. I searched the forum and could not find anything similar to this. I did not attach a report because I do not think it is a software issue but a hardware problem.
Thank you for any help.
A few years ago I retrofitted my lathe with Acorn with a Ether1616 expansion board and things have been working great. On Monday during normal a routine turning operation the machine stopped and fault called out. unable to restart software for any movement. After a little investigating found the power supply for the expansion board was not online. I thought power supply went bad. Ordered new power supply and installed it this morning. I still have same indications.
I removed wires the load side of powers supply and the power supply then comes online.
I re-attached the wires to power supply and disconnected the power connection from acorn board. Power supply powers up fine.
I re-attached the power connector and disconnected the connector from the inputs and ribbon cable going to output relay boards. Power supply does not come online.
I think there is a short somewhere in the expansion board. I removed and expansion board and did visual inspection and did not see and indication of faulty component (no burnt marks or any other damage).
Is there any testing I can do with the expansion board to verify the problem? I am not one for Easter egg hunting to fix a problem. I searched the forum and could not find anything similar to this. I did not attach a report because I do not think it is a software issue but a hardware problem.
Thank you for any help.
-
- Posts: 273
- Joined: Thu Apr 14, 2022 2:46 pm
- Acorn CNC Controller: No
- Allin1DC CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC12: No
- CNC11: No
- CPU10 or CPU7: No
Re: Ether1616 expansion board Fault
It does sound like something was shorted on the Ether1616. That board does not have easy test points for checking the supply rails but a quick check starts with disconnecting everything from it. There will be a point labeled "GND" in the center of the board by the edge connector. Look for shorts between that test point and pins 1 and 3 of the voltage regulators. Those are the black boxes with "RECOM" on top.
If you have a short on pin 1, then one of the regulators is shorted. If you have a short on pin 3 of one of them, then there's a short on that rail. I think the first case is more likely.
If you have a short on pin 1, then one of the regulators is shorted. If you have a short on pin 3 of one of them, then there's a short on that rail. I think the first case is more likely.
-
- Posts: 144
- Joined: Thu Nov 22, 2018 6:27 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: Yes
- Oak CNC controller: No
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC12: Yes
- CNC11: Yes
- CPU10 or CPU7: No
Re: Ether1616 expansion board Fault
Thank you for the information. I currently have:
4K ohm from pin 1 to gnd and 407 ohm from pin 3 to gnd for IC17
5K ohm from pin 1 to gnd and 414 ohm from pin 3 to gnd for U1
5K ohm from pin 1 to gnd and 413 ohm from pin 3 to gnd for u2.
I am not seeing a direct short but there is something somewhere.
4K ohm from pin 1 to gnd and 407 ohm from pin 3 to gnd for IC17
5K ohm from pin 1 to gnd and 414 ohm from pin 3 to gnd for U1
5K ohm from pin 1 to gnd and 413 ohm from pin 3 to gnd for u2.
I am not seeing a direct short but there is something somewhere.
-
- Posts: 273
- Joined: Thu Apr 14, 2022 2:46 pm
- Acorn CNC Controller: No
- Allin1DC CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC12: No
- CNC11: No
- CPU10 or CPU7: No
Re: Ether1616 expansion board Fault
Hmm, those seem about normal. When you had it all hooked up, was the power supply's LED blinking every few seconds? If so, that would be the overcurrent or overvoltage protection - likely overcurrent in this case.
Have you tried powering it up off the machine? You might be able to find what is shorted by temperature.
Have you tried powering it up off the machine? You might be able to find what is shorted by temperature.
-
- Posts: 144
- Joined: Thu Nov 22, 2018 6:27 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: Yes
- Oak CNC controller: No
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC12: Yes
- CNC11: Yes
- CPU10 or CPU7: No
Re: Ether1616 expansion board Fault
When it was all hooked up the power supply light was not on at all, that is why my initial thought was bad power supply. I disconnect all the input and output and tried powering it up again and no power supply light is lit. I disconnected the expansion board and power supply light then would light. It is like something (short) is drawing down the power supply.
-
- Posts: 273
- Joined: Thu Apr 14, 2022 2:46 pm
- Acorn CNC Controller: No
- Allin1DC CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC12: No
- CNC11: No
- CPU10 or CPU7: No
Re: Ether1616 expansion board Fault
That is odd. Usually these power supplies will go into overcurrent protect mode when there is a short and the LED blinks occasionally as it tries to restart. I suggest contacting tech support for an RMA number.
-
- Posts: 144
- Joined: Thu Nov 22, 2018 6:27 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: Yes
- Oak CNC controller: No
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC12: Yes
- CNC11: Yes
- CPU10 or CPU7: No
Re: Ether1616 expansion board Fault
I tried contacting tech support and I can not get anyone to answer the phone. I would like to get a new board with out having to get all the extra stuff I dont need.
-
- Posts: 373
- Joined: Tue Dec 11, 2018 4:03 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: F045DA80C8B8-0905181172
E415F6F70BC3-0318203049
98F07B91FC6B-0123236802 - DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
- Location: UK
Re: Ether1616 expansion board Fault
Send an email to DIYSales@centroidcnc.com
Hope this helps
Nigel
"You can lead a horse to water but you cannot force it to drink"
Nigel
"You can lead a horse to water but you cannot force it to drink"
-
- Posts: 7363
- Joined: Wed Mar 03, 2010 4:23 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: Yes
- Oak CNC controller: Yes
- CNC Control System Serial Number: none
- DC3IOB: Yes
- CNC11: Yes
- CPU10 or CPU7: Yes
- Contact:
Re: Ether1616 expansion board Fault
support@centroidcnc.com
814-353-9256 press 4
if they are on the phone it goes to next extension in support, if they are on phone it goes to VM, VM is then checked by the office staff which might take a day to get back to you.
814-353-9256 press 4
if they are on the phone it goes to next extension in support, if they are on phone it goes to VM, VM is then checked by the office staff which might take a day to get back to you.
Need support? READ THIS POST first. http://centroidcncforum.com/viewtopic.php?f=60&t=1043
All Acorn Documentation is located here: viewtopic.php?f=60&t=3397
Answers to common questions: viewforum.php?f=63
and here viewforum.php?f=61
Gear we use but don't sell. https://www.centroidcnc.com/centroid_di ... _gear.html
All Acorn Documentation is located here: viewtopic.php?f=60&t=3397
Answers to common questions: viewforum.php?f=63
and here viewforum.php?f=61
Gear we use but don't sell. https://www.centroidcnc.com/centroid_di ... _gear.html
-
- Posts: 144
- Joined: Thu Nov 22, 2018 6:27 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: Yes
- Oak CNC controller: No
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC12: Yes
- CNC11: Yes
- CPU10 or CPU7: No
Re: Ether1616 expansion board Fault
I finally talked with tech support today. The tech was at a loss like me and was unable to help. I am trying to understand why the board failed before I go putting in a new board.