allin1dc MP11 probe help with pictures

All things related to Centroid Oak, Allin1DC, MPU11 and Legacy products

Moderator: cnckeith

craigc
Posts: 22
Joined: Sun Sep 12, 2021 12:34 pm
Acorn CNC Controller: Yes
Plasma CNC Controller: No
AcornSix CNC Controller: No
Allin1DC CNC Controller: No
Hickory CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No

allin1dc MP11 probe help with pictures

Post by craigc »

I need suggestions on wiring a Renishaw MP11 probe on a conversion of a Bridgeport V2XT / DX32 NC system to a Centroid Allin1DC system.
Here is the photos / info I have.

There is a 1K ohm resistor between the wires in the Bridgeport schematic shown as White (170) Brown wire (40) but the actual wire color is wire 170 yellow and wire 40 orange at the connector.
Does the Allin1DC probe connector supply a voltage and how can I wire this for probe detect. I haven't found info for the Allin1DC and Renishaw MP11. As you can see in the Renishaw manual it SSR can only support 50ma.
I have researched all I can and haven't found how to do this.
Thanks


eng199
Posts: 447
Joined: Fri Jan 10, 2014 11:29 am
Acorn CNC Controller: Yes
Plasma CNC Controller: No
AcornSix CNC Controller: Yes
Allin1DC CNC Controller: Yes
Hickory CNC Controller: Yes
Oak CNC controller: Yes
CNC Control System Serial Number: none
DC3IOB: Yes
CNC12: Yes
CNC11: Yes
CPU10 or CPU7: Yes
Location: Howard, PA

Re: allin1dc MP11 probe help with pictures

Post by eng199 »

craigc wrote: Tue Mar 08, 2022 9:44 pm Does the Allin1DC probe connector supply a voltage and how can I wire this for probe detect.
Thanks
ALLIN1DC probe inputs are pulled up to 12V. Pull them down to activate. The input current draw is 9-15mA when pulled down.

The ALLIN1DC Probe Cable drawing is attached. It includes a chart that lists the signals. 12V is available from that connector to power your probe.
Attachments
s14779.r1.pdf
(8.51 KiB) Downloaded 76 times


craigc
Posts: 22
Joined: Sun Sep 12, 2021 12:34 pm
Acorn CNC Controller: Yes
Plasma CNC Controller: No
AcornSix CNC Controller: No
Allin1DC CNC Controller: No
Hickory CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No

Re: allin1dc MP11 probe help with pictures

Post by craigc »

Thank you for your help. I really appreciate it.


craigc
Posts: 22
Joined: Sun Sep 12, 2021 12:34 pm
Acorn CNC Controller: Yes
Plasma CNC Controller: No
AcornSix CNC Controller: No
Allin1DC CNC Controller: No
Hickory CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No

Re: allin1dc MP11 probe help with pictures

Post by craigc »

I have the probe partially working but it touches off 4-5 times and errors out. Error 915 unable to find surface. The inputs 770 and 771 work correctly I think, I set the probe to be normally closed first then normally open. I used the Centroid dp4 probe guide to configure the suggested parameters. I set the Renishaw probe as a DSP type probe because it has a SSR in it which may be incorrect. The probe manual says 15-30 VDC so I did not use the 12VDC available at the Allin1DC but the system 24VDC. The negatives of both DC power supplies are tied together.

New report

Probe plugged in
IMG_20220323_172442_4.jpg
Probe tripped
IMG_20220323_172412_3.jpg
some photos of the info I used
IMG_20220323_172746_1.jpg
IMG_20220323_172858_5.jpg
IMG_20220323_172948_7.jpg
Attachments
dp4_probe_manual.pdf
(2.71 MiB) Downloaded 44 times


eng199
Posts: 447
Joined: Fri Jan 10, 2014 11:29 am
Acorn CNC Controller: Yes
Plasma CNC Controller: No
AcornSix CNC Controller: Yes
Allin1DC CNC Controller: Yes
Hickory CNC Controller: Yes
Oak CNC controller: Yes
CNC Control System Serial Number: none
DC3IOB: Yes
CNC12: Yes
CNC11: Yes
CPU10 or CPU7: Yes
Location: Howard, PA

Re: allin1dc MP11 probe help with pictures

Post by eng199 »

Use input 769 for mechanical probe. The DSP input is a proprietary thing for some Centroid probes.

Input 771 probe detect should be pulled low when the probe is connected. It looks like your probe pulls up. Did you sort that out?

The probe should be set for normally open if you have the option to configure the output. That will match Centroid's probes used on servo systems. It is the most tested configuration, therefore least likely to have any issues.


craigc
Posts: 22
Joined: Sun Sep 12, 2021 12:34 pm
Acorn CNC Controller: Yes
Plasma CNC Controller: No
AcornSix CNC Controller: No
Allin1DC CNC Controller: No
Hickory CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No

Re: allin1dc MP11 probe help with pictures

Post by craigc »

Ah, Ok I will switch it to the mechanical input and wire it for normally open. I thought I had the detect sorted out, I just cant seem to get how it should be wired with the Renishaw MP11 to probe detect. There is a picture in the first post of the mill probe connector with wire numbers and the pictures above if would be so kind to give me a shove in the right direction how to connect it to the Allin1DC.

Thanks for your help.


eng199
Posts: 447
Joined: Fri Jan 10, 2014 11:29 am
Acorn CNC Controller: Yes
Plasma CNC Controller: No
AcornSix CNC Controller: Yes
Allin1DC CNC Controller: Yes
Hickory CNC Controller: Yes
Oak CNC controller: Yes
CNC Control System Serial Number: none
DC3IOB: Yes
CNC12: Yes
CNC11: Yes
CPU10 or CPU7: Yes
Location: Howard, PA

Re: allin1dc MP11 probe help with pictures

Post by eng199 »

Honestly, I don't understand what "REMOTE SOCKET (Park Position)" is. I would probably wire detect to a ground in the connector at the MP11 end of the cable. This would not be the best since it would only be a cable detect. There may be a better way, but I don't see it right now.


craigc
Posts: 22
Joined: Sun Sep 12, 2021 12:34 pm
Acorn CNC Controller: Yes
Plasma CNC Controller: No
AcornSix CNC Controller: No
Allin1DC CNC Controller: No
Hickory CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No

Re: allin1dc MP11 probe help with pictures

Post by craigc »

Thanks again, I know its confusing to me. I'll follow your previous info and mess with the detect.


craigc
Posts: 22
Joined: Sun Sep 12, 2021 12:34 pm
Acorn CNC Controller: Yes
Plasma CNC Controller: No
AcornSix CNC Controller: No
Allin1DC CNC Controller: No
Hickory CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No

Re: allin1dc MP11 probe help with pictures

Post by craigc »

Is there a way to connect a 3 wire hall effect / magnet to a Allin1dc spindle encoder input just to display RPM in CNC 12.
Top


craigc
Posts: 22
Joined: Sun Sep 12, 2021 12:34 pm
Acorn CNC Controller: Yes
Plasma CNC Controller: No
AcornSix CNC Controller: No
Allin1DC CNC Controller: No
Hickory CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No

Re: allin1dc MP11 probe help with pictures

Post by craigc »

Is there a way to set the Probe PLC to work with a normally closed probe. Most probes are NC. Thanks


Post Reply