Wiring Confirmation
Moderator: cnckeith
-
- Posts: 21
- Joined: Sat Jan 08, 2022 10:16 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
Re: Wiring Confirmation
As marty stated that your sizes are correct. You would just need to ensure which ever one you purchased had at least one normally open contact and you would not want the early open variant. You would put those two terminals on the auxilary Normally open to the No fault for the C86ACCP
You don't need a snubber if you use auxiliary contacts as they are mechanically actuated by the main contactor. They are not interconnected with the coil in any way
You don't need a snubber if you use auxiliary contacts as they are mechanically actuated by the main contactor. They are not interconnected with the coil in any way
Last edited by firebrick43 on Wed Jan 19, 2022 10:24 am, edited 2 times in total.
-
- Posts: 9915
- Joined: Tue Mar 28, 2017 12:01 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: Yes
- Oak CNC controller: No
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC12: Yes
- CNC11: Yes
- CPU10 or CPU7: Yes
- Location: Mesa, AZ
Re: Wiring Confirmation
All relays should have a snubber. Some relays have flyback diodes built into them. (I drew it in as a matter of being consistent with the Acorn schematic)
I am not sure what is confusing you.
You simply add another small relay, you PARALLEL the coils of the two relays together, so that they are both energized and deenergized at the same time.
You have terminals for the relay coil (2)
And you have terminals for your contacts (3 in the case of my drawing, One is Common, Normally Open and Normaly closed) No different that the relay on Acorn output board.
Marty
I am not sure what is confusing you.
You simply add another small relay, you PARALLEL the coils of the two relays together, so that they are both energized and deenergized at the same time.
You have terminals for the relay coil (2)
And you have terminals for your contacts (3 in the case of my drawing, One is Common, Normally Open and Normaly closed) No different that the relay on Acorn output board.
Marty
Reminder, for support please follow this post: viewtopic.php?f=20&t=383
We can't "SEE" what you see...
Mesa, AZ
We can't "SEE" what you see...
Mesa, AZ
-
- Posts: 9915
- Joined: Tue Mar 28, 2017 12:01 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: Yes
- Oak CNC controller: No
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC12: Yes
- CNC11: Yes
- CPU10 or CPU7: Yes
- Location: Mesa, AZ
Re: Wiring Confirmation
The jist of all of this is you need another pair of contacts to close the C86ACCP IF you are using all 4 contacts on your current contactor.
Take a picture of your contactor and sketch how you have it wired and post it here please
Take a picture of your contactor and sketch how you have it wired and post it here please
Reminder, for support please follow this post: viewtopic.php?f=20&t=383
We can't "SEE" what you see...
Mesa, AZ
We can't "SEE" what you see...
Mesa, AZ
-
- Posts: 2270
- Joined: Fri May 24, 2019 8:34 am
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: 7804734C6498-0401191832
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
- Location: Clearwater, FL
Re: Wiring Confirmation
As noted already, if you just need one more NO contact block you don't need another contactor, snubber or relay, just add an auxiliary contact block to your existing contactor like the ones on the link you provided. It snaps right on to your current contactor and you're done. You can buy NO or NC aux contacts.
Here's a direct link: https://klocknermoeller.com/xstart/dilm32-xhi11-s.htm
Here's a direct link: https://klocknermoeller.com/xstart/dilm32-xhi11-s.htm
-
- Posts: 21
- Joined: Sat Jan 08, 2022 10:16 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
Re: Wiring Confirmation
The main page shows all of the contacts for several different sizes(and this is common across manufactures lines)
However if you go to the side mounted auxliary contact page it does say for 17, 25 and 32 sized contactors only.
The top/front mount contactors however are for all sizes. So contactor DILA-XHI20 would work.
https://klocknermoeller.com/xstart/dila-xhi20.htm
'
Looks like they are finally going with just the eaton brand name so eaton XTCEXFAC20 would work as well
However if you go to the side mounted auxliary contact page it does say for 17, 25 and 32 sized contactors only.
The top/front mount contactors however are for all sizes. So contactor DILA-XHI20 would work.
https://klocknermoeller.com/xstart/dila-xhi20.htm
'
Looks like they are finally going with just the eaton brand name so eaton XTCEXFAC20 would work as well
-
- Posts: 21
- Joined: Sat Jan 08, 2022 10:16 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
Re: Wiring Confirmation
Yes, you would use 33/34tuffduck wrote: ↑Wed Jan 19, 2022 10:37 am Wi this one have enough terminals?
https://www.ebay.ca/itm/392759921540?ep ... SwL9pek2nB
Thanks
-
- Posts: 101
- Joined: Mon Mar 03, 2014 4:24 pm
- Allin1DC CNC Controller: Yes
- CNC Control System Serial Number: none
- DC3IOB: Yes
- CNC11: Yes
- CPU10 or CPU7: Yes
Re: Wiring Confirmation
S15117 is depicting 3 phase motor power connections requiring 3 contacts (L1,L2,L3), if the motor power is single phase 120vac then only the line lead (hot) would need to be routed through the E-stop contactor leaving the other contacts available for other circuits. Earth ground should never be routed through a disconnect switch or contactor as a matter of safety.
When requesting support READ THIS POST first. viewtopic.php?f=60&t=1043
Please ALWAYS post a FRESH report. To make a report: https://www.youtube.com/watch?v=Ecvg0VJp1oQ.
(We pride ourselves on providing timely solid technical support but, without good information we may not be able to help and/or reply until such information is posted.)
Please ALWAYS post a FRESH report. To make a report: https://www.youtube.com/watch?v=Ecvg0VJp1oQ.
(We pride ourselves on providing timely solid technical support but, without good information we may not be able to help and/or reply until such information is posted.)
-
- Posts: 2270
- Joined: Fri May 24, 2019 8:34 am
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: 7804734C6498-0401191832
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
- Location: Clearwater, FL
Re: Wiring Confirmation
You have one contact on your current contactor that is NO, terminal 13 and 14, are you using it already? How many more do you need? Are you using single phase power or three phase?tuffduck wrote: ↑Wed Jan 19, 2022 10:37 am Wi this one have enough terminals?
https://www.ebay.ca/itm/392759921540?ep ... SwL9pek2nB
Thanks
-
- Posts: 9915
- Joined: Tue Mar 28, 2017 12:01 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: Yes
- Oak CNC controller: No
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC12: Yes
- CNC11: Yes
- CPU10 or CPU7: Yes
- Location: Mesa, AZ
Re: Wiring Confirmation
Agreed.Centroid_Tech2 wrote: ↑Wed Jan 19, 2022 10:44 am S15117 is depicting 3 phase motor power connections requiring 3 contacts (L1,L2,L3), if the motor power is single phase 120vac then only the line lead (hot) would need to be routed through the E-stop contactor leaving the other contacts available for other circuits. Earth ground should never be routed through a disconnect switch or contactor as a matter of safety.
That's why I asked for a picture and a sketch of what he actually has and how he has it wired.
Reminder, for support please follow this post: viewtopic.php?f=20&t=383
We can't "SEE" what you see...
Mesa, AZ
We can't "SEE" what you see...
Mesa, AZ