Wiring Confirmation
Moderator: cnckeith
-
- Posts: 359
- Joined: Mon Mar 02, 2020 5:07 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
- Location: Scotland, ON, Canada
Wiring Confirmation
Hello,
I am wiring up a contactor and the C86ACCP board and noticed they both share the output 1 relay terminals. Is this correct?
Thanks
I am wiring up a contactor and the C86ACCP board and noticed they both share the output 1 relay terminals. Is this correct?
Thanks
- Attachments
-
- s15117.r1circe.pdf
- (111.78 KiB) Downloaded 68 times
-
- S15072.r4circe.pdf
- (118.83 KiB) Downloaded 56 times
-
- Posts: 2251
- Joined: Fri May 24, 2019 8:34 am
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: 7804734C6498-0401191832
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
- Location: Clearwater, FL
Re: Wiring Confirmation
I haven't looked but that sounds right as output 1 is usually set to NoFaultOut because after you press reset at startup it closes output 1 and energizes the contactor to send power to whatever is connected to the contactor. Makes sense that you would also energize/enable the C86ACCP at this time. Make sense?
-
- Posts: 9914
- Joined: Tue Mar 28, 2017 12:01 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: Yes
- Oak CNC controller: No
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC12: Yes
- CNC11: Yes
- CPU10 or CPU7: Yes
- Location: Mesa, AZ
Re: Wiring Confirmation
If you are wiring an Estop contactor, then you will run C86ACCP (NoFault) through a spare set of contacts on the Estop contactor instead of relay output
The only thing Acorn Relay Output 1 (NoFault) is controlling is your Estop contactor. Your Estop contactor will control your drives and spindle drive.
Marty
The only thing Acorn Relay Output 1 (NoFault) is controlling is your Estop contactor. Your Estop contactor will control your drives and spindle drive.
Marty
Reminder, for support please follow this post: viewtopic.php?f=20&t=383
We can't "SEE" what you see...
Mesa, AZ
We can't "SEE" what you see...
Mesa, AZ
-
- Posts: 359
- Joined: Mon Mar 02, 2020 5:07 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
- Location: Scotland, ON, Canada
Re: Wiring Confirmation
Do you have a diagram?
-
- Posts: 9914
- Joined: Tue Mar 28, 2017 12:01 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: Yes
- Oak CNC controller: No
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC12: Yes
- CNC11: Yes
- CPU10 or CPU7: Yes
- Location: Mesa, AZ
Re: Wiring Confirmation
Use a spare set of contacts on your Estop contactor. You would wire them to No Fault on C86ACCP
When the Estop contactor closes, it will close the input on C86ACCP
Marty
Reminder, for support please follow this post: viewtopic.php?f=20&t=383
We can't "SEE" what you see...
Mesa, AZ
We can't "SEE" what you see...
Mesa, AZ
-
- Posts: 359
- Joined: Mon Mar 02, 2020 5:07 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
- Location: Scotland, ON, Canada
Re: Wiring Confirmation
There aren't any. I have it wired like drawing S15117.
Contactor:
https://www.ebay.ca/itm/303348917509
Contactor:
https://www.ebay.ca/itm/303348917509
-
- Posts: 9914
- Joined: Tue Mar 28, 2017 12:01 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: Yes
- Oak CNC controller: No
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC12: Yes
- CNC11: Yes
- CPU10 or CPU7: Yes
- Location: Mesa, AZ
Re: Wiring Confirmation
You also used L4? (NO)tuffduck wrote: ↑Mon Jan 17, 2022 11:44 pm There aren't any. I have it wired like drawing S15117.
Contactor:
https://www.ebay.ca/itm/303348917509
Doing this from my phone so don't have access to the drawing you referenced until the morning...
Reminder, for support please follow this post: viewtopic.php?f=20&t=383
We can't "SEE" what you see...
Mesa, AZ
We can't "SEE" what you see...
Mesa, AZ
-
- Posts: 359
- Joined: Mon Mar 02, 2020 5:07 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
- Location: Scotland, ON, Canada
Re: Wiring Confirmation
Can you open a PDF.
- Attachments
-
- s15117.r1.pdf
- (142.83 KiB) Downloaded 66 times
-
- Posts: 9914
- Joined: Tue Mar 28, 2017 12:01 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: Yes
- Oak CNC controller: No
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC12: Yes
- CNC11: Yes
- CPU10 or CPU7: Yes
- Location: Mesa, AZ
Re: Wiring Confirmation
Yes.
Are your then using three phase servo drives?
If so add another contactor in parallel to your existing contactor....or is that what you were asking if you could do to begin with?
Marty
Reminder, for support please follow this post: viewtopic.php?f=20&t=383
We can't "SEE" what you see...
Mesa, AZ
We can't "SEE" what you see...
Mesa, AZ
-
- Posts: 359
- Joined: Mon Mar 02, 2020 5:07 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
- Location: Scotland, ON, Canada
Re: Wiring Confirmation
No I just want to use 1 contactor. Do I need to run 4 wire to output 1