Help with KBSI-240D signal isolator wiring

All things related to the Centroid Acorn CNC Controller

Moderator: cnckeith

martyscncgarage
Posts: 9914
Joined: Tue Mar 28, 2017 12:01 pm
Acorn CNC Controller: Yes
Allin1DC CNC Controller: Yes
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC12: Yes
CNC11: Yes
CPU10 or CPU7: Yes
Location: Mesa, AZ

Re: Help with KBIC 240D signal isolator wiring

Post by martyscncgarage »

BillB wrote: Mon Jan 10, 2022 3:53 am
martyscncgarage wrote: Sun Jan 09, 2022 10:30 am Power it up when you power up the control cabinet. Spindle motor should have its own overcurrent(fuse) protection.(usually provided on the spindle drive)
You should be using an Estop contactor to ENABLE/DISABLE the Spindle Drive and the axis drives when there is a control fault/Estop condition.

Marty
When Testing, I hit E-stop mid program spindle and axis motors shut down as you would want. Hit E-stop when spindle is running and it also shuts down. I did not have to configure anything else in Wizard to make that work. Is that correct?
Post a fresh report. F7 Utility, F7 Create report. Post a picture of your control cabinet. The report will show us how you have CNC12 configured.
Yes, hitting estop will have CNC12 stop motion. But you are then only relying on software as the safety device. By using an Estop contactor and an Estop button with two ND contact blocks, you are then physically using the estop contactor to open circuits. Axis drives and spindle cont4ol go through the estop contactor. When Estop button is in its run state, CNC12 knows it is closed and the circuit controlling the estop contactor is closed, energizing the estop contactor and closing the contactor contacts allowing spindle and axis motion.

Marty
Reminder, for support please follow this post: viewtopic.php?f=20&t=383
We can't "SEE" what you see...
Mesa, AZ
BillB
Posts: 447
Joined: Thu Jul 15, 2021 1:43 pm
Acorn CNC Controller: Yes
Allin1DC CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No

Re: Help with KBIC 240D signal isolator wiring

Post by BillB »

Here you go.
Attachments
report_6433DB044D1E-0623214856_2022-01-10_20-19-05.zip
(601.38 KiB) Downloaded 38 times
martyscncgarage
Posts: 9914
Joined: Tue Mar 28, 2017 12:01 pm
Acorn CNC Controller: Yes
Allin1DC CNC Controller: Yes
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC12: Yes
CNC11: Yes
CPU10 or CPU7: Yes
Location: Mesa, AZ

Re: Help with KBIC 240D signal isolator wiring

Post by martyscncgarage »

BillB:
Take a look at your error logs, you have some PC/MPU resends (F7 Utility, F9 Logs, F1 Errors) Those are usually caused by noise in the control cabinet, using an UNSHIELDED Ethernet cable from the CNC PC to Acorn, bad ethernet cable PC needing to update ethernet drivers, flakey ethernet port on the PC,

You have no outputs to turn on and off your spindle motor, you do have a NoFault output assigned, this relay should control a larger contactor that will close when CNC12 is in the normal ready state and open when there is a fault or an Estop press. The contactor will usually have 3 sets of contacts. They are used just like switches. You can power up and down the axis drives and the spindle drive with it.

;------------------------------------------------------------------------------
; Output Definitions
; Logic 1 = OUTPUT ON (Green), 0 = OUTPUT OFF (Red)
;------------------------------------------------------------------------------

; DO NOT MODIFY
; #wizardregion Outputs
NoFaultOut IS OUT1
Mist IS OUT2
OUTPUT3 IS OUT3
OUTPUT4 IS OUT4
OUTPUT5 IS OUT5
OUTPUT6 IS OUT6
OUTPUT7 IS OUT7
OUTPUT8 IS OUT8

Hope this helps a bit.
Marty
Reminder, for support please follow this post: viewtopic.php?f=20&t=383
We can't "SEE" what you see...
Mesa, AZ
BillB
Posts: 447
Joined: Thu Jul 15, 2021 1:43 pm
Acorn CNC Controller: Yes
Allin1DC CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No

Re: Help with KBIC 240D signal isolator wiring

Post by BillB »

martyscncgarage wrote: Tue Jan 11, 2022 12:29 pm BillB:
Take a look at your error logs, you have some PC/MPU resends (F7 Utility, F9 Logs, F1 Errors) Those are usually caused by noise in the control cabinet, using an UNSHIELDED Ethernet cable from the CNC PC to Acorn, bad ethernet cable PC needing to update ethernet drivers, flakey ethernet port on the PC,

You have no outputs to turn on and off your spindle motor, you do have a NoFault output assigned, this relay should control a larger contactor that will close when CNC12 is in the normal ready state and open when there is a fault or an Estop press. The contactor will usually have 3 sets of contacts. They are used just like switches. You can power up and down the axis drives and the spindle drive with it.

;------------------------------------------------------------------------------
; Output Definitions
; Logic 1 = OUTPUT ON (Green), 0 = OUTPUT OFF (Red)
;------------------------------------------------------------------------------

; DO NOT MODIFY
; #wizardregion Outputs
NoFaultOut IS OUT1
Mist IS OUT2
OUTPUT3 IS OUT3
OUTPUT4 IS OUT4
OUTPUT5 IS OUT5
OUTPUT6 IS OUT6
OUTPUT7 IS OUT7
OUTPUT8 IS OUT8

Hope this helps a bit.
Marty

Marty I think the resends are (flakey ethernet port on the PC) An issue Ive had since day 1 its a used mini PC If you remember you recommend this one to me. I think I just got a bad one. Just have not gotten to it yet.

Regarding the set up on the spindle motor, can you provide me with a link for a suitable contactor and show me exactly how to configure the outputs and wire the relays?
martyscncgarage
Posts: 9914
Joined: Tue Mar 28, 2017 12:01 pm
Acorn CNC Controller: Yes
Allin1DC CNC Controller: Yes
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC12: Yes
CNC11: Yes
CPU10 or CPU7: Yes
Location: Mesa, AZ

Re: Help with KBIC 240D signal isolator wiring

Post by martyscncgarage »

Look at a schematic for a Generic VFD and follow its lead. Does your spindle need to reverse?
You can run the ENAble signal through a contactor.
I believe you have a small Sherline lathe with what kind of axis motors?
Marty
Reminder, for support please follow this post: viewtopic.php?f=20&t=383
We can't "SEE" what you see...
Mesa, AZ
BillB
Posts: 447
Joined: Thu Jul 15, 2021 1:43 pm
Acorn CNC Controller: Yes
Allin1DC CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No

Re: Help with KBIC 240D signal isolator wiring

Post by BillB »

martyscncgarage wrote: Tue Jan 11, 2022 7:17 pm Look at a schematic for a Generic VFD and follow its lead. Does your spindle need to reverse?
You can run the ENAble signal through a contactor.
I believe you have a small Sherline lathe with what kind of axis motors?
Marty
Although I did not plan for it originally reverse would be really nice to have. Would it give me the ability to ridged tap center holes?
Yes Sherline Chucker lathe.
HT Nema 23s
martyscncgarage
Posts: 9914
Joined: Tue Mar 28, 2017 12:01 pm
Acorn CNC Controller: Yes
Allin1DC CNC Controller: Yes
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC12: Yes
CNC11: Yes
CPU10 or CPU7: Yes
Location: Mesa, AZ

Re: Help with KBIC 240D signal isolator wiring

Post by martyscncgarage »

BillB wrote: Wed Jan 12, 2022 4:05 am
martyscncgarage wrote: Tue Jan 11, 2022 7:17 pm Look at a schematic for a Generic VFD and follow its lead. Does your spindle need to reverse?
You can run the ENAble signal through a contactor.
I believe you have a small Sherline lathe with what kind of axis motors?
Marty
Although I did not plan for it originally reverse would be really nice to have. Would it give me the ability to ridged tap center holes?
Yes Sherline Chucker lathe.
HT Nema 23s
The only way to have reverse is if the spindle drive you have is reversible.
Would need details/schematic of your current spindle drive. Manual to make a suggestion how to wire it up so that Acorn will turn the spindle on and off when issued an M3/M5 command.
Reminder, for support please follow this post: viewtopic.php?f=20&t=383
We can't "SEE" what you see...
Mesa, AZ
Miamijerry
Posts: 17
Joined: Sat Nov 20, 2021 12:04 pm
Acorn CNC Controller: Yes
Allin1DC CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No

Re: Help with KBIC 240D signal isolator wiring

Post by Miamijerry »

There is the option of the Kbcc-125r which would replace the Kbic motor controller and provide reverse.

https://centroidcncforum.com/viewtopic. ... bcc#p10067
https://centroidcncforum.com/viewtopic. ... 402#p12402
martyscncgarage
Posts: 9914
Joined: Tue Mar 28, 2017 12:01 pm
Acorn CNC Controller: Yes
Allin1DC CNC Controller: Yes
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC12: Yes
CNC11: Yes
CPU10 or CPU7: Yes
Location: Mesa, AZ

Re: Help with KBIC 240D signal isolator wiring

Post by martyscncgarage »

Miamijerry wrote: Wed Jan 12, 2022 11:21 am There is the option of the Kbcc-125r which would replace the Kbic motor controller and provide reverse.

https://centroidcncforum.com/viewtopic. ... bcc#p10067
https://centroidcncforum.com/viewtopic. ... 402#p12402
Agreed.
Reminder, for support please follow this post: viewtopic.php?f=20&t=383
We can't "SEE" what you see...
Mesa, AZ
BillB
Posts: 447
Joined: Thu Jul 15, 2021 1:43 pm
Acorn CNC Controller: Yes
Allin1DC CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No

Re: Help with KBIC 240D signal isolator wiring

Post by BillB »

I looked into the use of reverse with Sherline set up and the bottom line is the configuration is not capable of doing any reverse or Ridgid tapping so for me that's the end story. I would not need reverse unless I would gain rigid tapping. Thanks for the input on this guys.
Post Reply