cant figure out how to hookup, yes I read all docs

All things related to the Centroid Acorn CNC Controller

Moderator: cnckeith

shreddedcurbs
Posts: 100
Joined: Sat Nov 14, 2020 6:33 am
Acorn CNC Controller: Yes
Allin1DC CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No

Re: cant figure out how to hookup, yes I read all docs

Post by shreddedcurbs »

Ok stuck on a couple wires coming from my VFD that are labelled different than what the acorn schematic has.. im sure its just from being new and not centroid fault..

VFD - "10V" connects to MACh3 Controller as 10V in (in the second spindle category)
VFD - "AVI" connects to mach3 controller as AVI
VFD - "ACM" connects to MACH3 controller as ACM

When looking up the VFD's manual... https://salecnc.com/manuals/Inverter/BE ... nglish.pdf...
it has vague answers as to what they might be. The manual reads..

AVI - Terminal Name "Frequency voltage input setting" Explanation: Input 0-10V, PID Given or feedback
ACI - Terminal Name "Frequency voltage input setting" Explanation: Input 4-20mA, PID given or feedback
10V - Terminal Name "Frequency auxiliary power setting" Explanation: And AVI, COMD Connected potentiometer (4.7k-10k)

Other than those wires in question I've already hooked up the DCM (common ground) to relay 4,5,6 and the Spindle Forward to the correct relay (OUT4). It seems this VFD didnt have wires hooked up to RESET, or REVERSE.

The rest of the wires I have not wired for the spindle that are in the Acorn Installation Manual are:
0-10V VDC (which im assuming is AVI.)
0-10V VDC COM (which im assuming is ACI)
FAULT COM (not sure?)
FAULT NC (not sure?)
martyscncgarage
Posts: 9915
Joined: Tue Mar 28, 2017 12:01 pm
Acorn CNC Controller: Yes
Allin1DC CNC Controller: Yes
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC12: Yes
CNC11: Yes
CPU10 or CPU7: Yes
Location: Mesa, AZ

Re: cant figure out how to hookup, yes I read all docs

Post by martyscncgarage »

Do not hook up 10vdc FROM the VFD.
Acorn provides the 0-10vdc analog signal.
AVI is probably what you want and it's Common.
Read the VFD manual

Fault Com gets Connected to Acorn Common.
Fault NC gets Connected to an Acorn input and assigned Spindle OK.
Reminder, for support please follow this post: viewtopic.php?f=20&t=383
We can't "SEE" what you see...
Mesa, AZ
shreddedcurbs
Posts: 100
Joined: Sat Nov 14, 2020 6:33 am
Acorn CNC Controller: Yes
Allin1DC CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No

Re: cant figure out how to hookup, yes I read all docs

Post by shreddedcurbs »

Sorry I realize my last part of that post might've been poorly written. I don't have any other wires from the VFD except the AVI, ACI and 10V. The 10V I will just unhook from the VFD and forget about. I will hook the AVI and ACI into the proper places into the controller main board.

I dont have anything from my VFD that I can wire into the Fault Com or Fault NC. so do I just forget about these and keep on trucking to the next steps of the install?
martyscncgarage
Posts: 9915
Joined: Tue Mar 28, 2017 12:01 pm
Acorn CNC Controller: Yes
Allin1DC CNC Controller: Yes
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC12: Yes
CNC11: Yes
CPU10 or CPU7: Yes
Location: Mesa, AZ

Re: cant figure out how to hookup, yes I read all docs

Post by martyscncgarage »

First, I am a little skeptical of the inexpensive Chinese drive you have. I hope it does not cause you headaches in EMI noise and programming..
Second, the manual you linked to shows it has relay contact outputs. YOU have to program them using the parameters as to how they function.
I skimmed through the manual Relay output Y1 is controlled by parameter 101. You would program it to value 4 Fault. That is, if the VFD faults the relay will activate, in turn when wired to SpindleOk input on Acorn, will allow CNC12 to see there is a problem and fault stopping the control.

Take a little time to read through the VFD manual and familiarize yourself with it and how to program it.

I strongly encourage you to program and use this VFD output. You can imagine what could happen if the cutter is engaged with the work piece and stops cutting. Use the Centroid Generic VFD Schematic for guidance. Schematics and other Acorn documentation can be found here: https://centroidcncforum.com/viewtopic.php?f=60&t=3397

Marty
Reminder, for support please follow this post: viewtopic.php?f=20&t=383
We can't "SEE" what you see...
Mesa, AZ
shreddedcurbs
Posts: 100
Joined: Sat Nov 14, 2020 6:33 am
Acorn CNC Controller: Yes
Allin1DC CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No

Re: cant figure out how to hookup, yes I read all docs

Post by shreddedcurbs »

Ok so I went into the VFD's programming menu and P101 is assigned to 4. So that seems to be good. What I am not understanding is what I need to wire up. Going by what you mentioned I need to connect Y1 to the spindleOK input on acorn board in the spot H1 - IN5. Ok I get that. The schematic says that comes from the FAULT NC from the VFD. So I assume that will be the Y1.

I see the VFD has a COM port on there as well. So would that be the FAULT COM that would connect to H9 section on the acorn board?

Only thing left in the VFD section would be Spindle Reverse, but thats not an existing thing so either my spindle is not set up to go in reverse, or its another menu i have to program for the VFD. Either way, I dont ever run the spindle in reverse so it might not be that big of a deal. Again, maybe my inexperience is speaking on that matter.

After this I can finally move onto the touch probe thankfully. This has taken one week, for which I had planned on but definitely was hoping to be doneby now haha
martyscncgarage
Posts: 9915
Joined: Tue Mar 28, 2017 12:01 pm
Acorn CNC Controller: Yes
Allin1DC CNC Controller: Yes
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC12: Yes
CNC11: Yes
CPU10 or CPU7: Yes
Location: Mesa, AZ

Re: cant figure out how to hookup, yes I read all docs

Post by martyscncgarage »

Please take a picture of the VFD showing its terminals and upload it here
The Chinese manual is terrible, shows NO diagram of the VFD and its connections

From page 11 of your manual:
Page 11.JPG
Great manual. (SARCASM)
With the VFD powered OFF,
Run a continuity test from Y1A to Y1B and Y1A to Y1C.
I think you should read continuity between Y1A and Y1C

IF you do THEN:
Connect Acorn Power Supply COM to Y1A and connect a free input to Y1C and assign the input chosen to SpindleOk

If a router, don't bother with reverse

Marty
Reminder, for support please follow this post: viewtopic.php?f=20&t=383
We can't "SEE" what you see...
Mesa, AZ
shreddedcurbs
Posts: 100
Joined: Sat Nov 14, 2020 6:33 am
Acorn CNC Controller: Yes
Allin1DC CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No

Re: cant figure out how to hookup, yes I read all docs

Post by shreddedcurbs »

Yes the manual is trash. Lol. It says I have a "X8" port but I don't..

I tried to get most of the labelling in the photo. Behind the ACM it is marked 'COM' thats the only port i couldnt get a clear photo of
Attachments
222333.jpg
111222.jpg
shreddedcurbs
Posts: 100
Joined: Sat Nov 14, 2020 6:33 am
Acorn CNC Controller: Yes
Allin1DC CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No

Re: cant figure out how to hookup, yes I read all docs

Post by shreddedcurbs »

So I disconnected the power to the control cabinet and shut off the breaker. MY old multimeter was not working to test continuity (edited)
Last edited by shreddedcurbs on Fri Dec 10, 2021 8:56 pm, edited 2 times in total.
tblough
Posts: 3174
Joined: Tue Mar 22, 2016 10:03 am
Acorn CNC Controller: Yes
Allin1DC CNC Controller: Yes
Oak CNC controller: Yes
CNC Control System Serial Number: 100505
100327
102696
103432
7804732B977B-0624192192
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No
Location: Boston, MA
Contact:

Re: cant figure out how to hookup, yes I read all docs

Post by tblough »

Common terminal for relay 1 is Y1B. You should have continuity between Y1B and Y1C when the power is off and Y1B and Y1A when the relay is energized. Relay #2 is normally open between Y2A and Y2B. There is no Y3 in either the terminal listing in the manual or the photo above.
Cheers,

Tom
Confidence is the feeling you have before you fully understand the situation.
I have CDO. It's like OCD, but the letters are where they should be.
shreddedcurbs
Posts: 100
Joined: Sat Nov 14, 2020 6:33 am
Acorn CNC Controller: Yes
Allin1DC CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No

Re: cant figure out how to hookup, yes I read all docs

Post by shreddedcurbs »

tblough wrote: Fri Dec 10, 2021 7:15 pm Common terminal for relay 1 is Y1B. You should have continuity between Y1B and Y1C when the power is off and Y1B and Y1A when the relay is energized. Relay #2 is normally open between Y2A and Y2B. There is no Y3 in either the terminal listing in the manual or the photo above.
Apologies I mean I tested Y1A and Y1B and it didnt show continuity, do I need power connected to the CNC control box just powered off? Because I removed the plug from the power receptacle.. I just like to be safe when working around electricity lol
Post Reply