Well I got an error this morning. I just reset it and turned the feed down. and re-homed it.
I did Pump a lot of way lube out the Z slide just to check that.
I will reset tools I will be using to ensure correct offset.
Jumping Z axis when homing!
Moderator: cnckeith
-
- Posts: 56
- Joined: Tue Dec 26, 2017 11:16 am
- Acorn CNC Controller: No
- Allin1DC CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: 102978, 8121, REV233
- DC3IOB: No
- CNC11: Yes
- CPU10 or CPU7: Yes
Re: Jumping Z axis when homing!
(Note: Liking will "up vote" a post in the search results helping others find good information faster)
-
- Community Expert
- Posts: 9944
- Joined: Tue Mar 28, 2017 12:01 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: Yes
- Oak CNC controller: No
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC12: Yes
- CNC11: Yes
- CPU10 or CPU7: Yes
- Location: Mesa, AZ
Re: Jumping Z axis when homing!
You might consider lubricating/replacing the Z+ home/limit switch. Make sure it is a little lower than the hard stop.
That "differs by X number of counts" is that the last time the control stored the number of counts between when the mechanical switch was tripped and the Z axis encoder index has changed by the number of counts displayed. Make sure mechanically all pulleys and belts are snug.
That "differs by X number of counts" is that the last time the control stored the number of counts between when the mechanical switch was tripped and the Z axis encoder index has changed by the number of counts displayed. Make sure mechanically all pulleys and belts are snug.
Reminder, for support please follow this post: viewtopic.php?f=20&t=383
We can't "SEE" what you see...
Mesa, AZ
We can't "SEE" what you see...
Mesa, AZ
(Note: Liking will "up vote" a post in the search results helping others find good information faster)
-
- Community Expert
- Posts: 3525
- Joined: Tue Mar 22, 2016 10:03 am
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: Yes
- Oak CNC controller: Yes
- CNC Control System Serial Number: 100505
100327
102696
103432
7804732B977B-0624192192 - DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
- Location: Boston, MA
- Contact:
Re: Jumping Z axis when homing!
You might also run into this if your Z encoder index pulse is close to where your limit switch actuates. If this is the case, simple things like temperature difference can affect where your limit switch trips by a small amount making what used to be a small turn to the encoder pulse now almost a full turn.
The fix is easy - just disconnect your motor from the ballscrew and rotate the motor 1/2 turn and reconnect it. You'll get the encoder counts message the first time you home it afterwards, say yes, and hopefully you'll never see the message again.
The fix is easy - just disconnect your motor from the ballscrew and rotate the motor 1/2 turn and reconnect it. You'll get the encoder counts message the first time you home it afterwards, say yes, and hopefully you'll never see the message again.
Cheers,
Tom
Confidence is the feeling you have before you fully understand the situation.
I have CDO. It's like OCD, but the letters are where they should be.
Tom
Confidence is the feeling you have before you fully understand the situation.
I have CDO. It's like OCD, but the letters are where they should be.
(Note: Liking will "up vote" a post in the search results helping others find good information faster)
-
- Community Expert
- Posts: 9944
- Joined: Tue Mar 28, 2017 12:01 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: Yes
- Oak CNC controller: No
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC12: Yes
- CNC11: Yes
- CPU10 or CPU7: Yes
- Location: Mesa, AZ
Re: Jumping Z axis when homing!
I just looked at the SYSTEST.OUT file found in the report. ASSUMING these are the results of your Systemtest conducted on 1/4/2018
Seems as it never passed the system test. So you are probably getting a white box on power up saying System test not completed and to Contact your dealer?
Here is your SYSTEST.OUT file:
-------------------------------------------
Starting system test
-------------------------------------------
Version Information
$Id: systest.cnc,v 1.1.1.1 2006/01/05 14:30:21 kdennison Exp $
;;;;;;;;;;;;;;;;;;;;;;;
System is NOT configured for ATC
;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;
; Checking travel limits and home set
Travel limits set and machine is homed.
;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;
; Starting home switch testing
;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;
Homing axis 1 minus
1 / 8 turn distance is 0.0246
7 / 8 turn distance is 0.1722
full turn distance is 0.1969
Off switch| error | home | error | differnce
-0.1290 0.0000 0.0000 0.0000 0.1290
Off switch Max Min Difference
-0.1290 -0.1290 0.0000
home posiiton Max Min Difference
0.0000 0.0000 0.0000
;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;
Homing axis 1 plus
1 / 8 turn distance is 0.0246
7 / 8 turn distance is 0.1722
full turn distance is 0.1969
Off switch| error | home | error | differnce
39.6927 0.0000 39.5675 0.0000 0.1252
Off switch Max Min Difference
39.6927 39.6927 0.0000
home posiiton Max Min Difference
39.5675 39.5675 0.0000
Axis has both minus and plus home switches
-Distance between home positions is 39.5674
-Distance between travel limits is 39.6250
-Difference between distances is -0.0576
*** FAILURE Travel limits set incorrectly
;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;
Homing axis 2 minus
1 / 8 turn distance is 0.0246
7 / 8 turn distance is 0.1723
full turn distance is 0.1969
Off switch| error | home | error | differnce
-19.5429 0.0000 -19.4909 0.0000 0.0520
Off switch Max Min Difference
-19.5429 -19.5429 0.0000
home posiiton Max Min Difference
-19.4909 -19.4909 0.0000
;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;
Homing axis 2 plus
1 / 8 turn distance is 0.0246
7 / 8 turn distance is 0.1723
full turn distance is 0.1969
Off switch| error | home | error | differnce
0.0800 0.0000 -0.0000 0.0000 0.0800
Off switch Max Min Difference
0.0800 0.0800 0.0000
home posiiton Max Min Difference
-0.0000 -0.0000 0.0000
Axis has both minus and plus home switches
-Distance between home positions is 19.4909
-Distance between travel limits is 19.4770
-Difference between distances is 0.0139
;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;
Homing axis 3 minus
1 / 8 turn distance is 0.0116
7 / 8 turn distance is 0.0811
full turn distance is 0.0926
Off switch| error | home | error | differnce
-19.7498 0.0000 -19.6715 0.0000 0.0782
Off switch Max Min Difference
-19.7498 -19.7498 0.0000
home posiiton Max Min Difference
-19.6715 -19.6715 0.0000
;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;
Homing axis 3 plus
1 / 8 turn distance is 0.0116
7 / 8 turn distance is 0.0811
full turn distance is 0.0926
Off switch| error | home | error | differnce
0.0722 0.0000 0.0604 0.0000 0.0118
Off switch Max Min Difference
0.0722 0.0722 0.0000
home posiiton Max Min Difference
0.0604 0.0604 0.0000
Axis has both minus and plus home switches
-Distance between home positions is 19.7320
-Distance between travel limits is 19.6500
-Difference between distances is 0.0820
Finished testing home/limit switches
*** FAILED SYSTEM TEST ***
Seems as it never passed the system test. So you are probably getting a white box on power up saying System test not completed and to Contact your dealer?
Here is your SYSTEST.OUT file:
-------------------------------------------
Starting system test
-------------------------------------------
Version Information
$Id: systest.cnc,v 1.1.1.1 2006/01/05 14:30:21 kdennison Exp $
;;;;;;;;;;;;;;;;;;;;;;;
System is NOT configured for ATC
;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;
; Checking travel limits and home set
Travel limits set and machine is homed.
;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;
; Starting home switch testing
;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;
Homing axis 1 minus
1 / 8 turn distance is 0.0246
7 / 8 turn distance is 0.1722
full turn distance is 0.1969
Off switch| error | home | error | differnce
-0.1290 0.0000 0.0000 0.0000 0.1290
Off switch Max Min Difference
-0.1290 -0.1290 0.0000
home posiiton Max Min Difference
0.0000 0.0000 0.0000
;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;
Homing axis 1 plus
1 / 8 turn distance is 0.0246
7 / 8 turn distance is 0.1722
full turn distance is 0.1969
Off switch| error | home | error | differnce
39.6927 0.0000 39.5675 0.0000 0.1252
Off switch Max Min Difference
39.6927 39.6927 0.0000
home posiiton Max Min Difference
39.5675 39.5675 0.0000
Axis has both minus and plus home switches
-Distance between home positions is 39.5674
-Distance between travel limits is 39.6250
-Difference between distances is -0.0576
*** FAILURE Travel limits set incorrectly
;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;
Homing axis 2 minus
1 / 8 turn distance is 0.0246
7 / 8 turn distance is 0.1723
full turn distance is 0.1969
Off switch| error | home | error | differnce
-19.5429 0.0000 -19.4909 0.0000 0.0520
Off switch Max Min Difference
-19.5429 -19.5429 0.0000
home posiiton Max Min Difference
-19.4909 -19.4909 0.0000
;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;
Homing axis 2 plus
1 / 8 turn distance is 0.0246
7 / 8 turn distance is 0.1723
full turn distance is 0.1969
Off switch| error | home | error | differnce
0.0800 0.0000 -0.0000 0.0000 0.0800
Off switch Max Min Difference
0.0800 0.0800 0.0000
home posiiton Max Min Difference
-0.0000 -0.0000 0.0000
Axis has both minus and plus home switches
-Distance between home positions is 19.4909
-Distance between travel limits is 19.4770
-Difference between distances is 0.0139
;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;
Homing axis 3 minus
1 / 8 turn distance is 0.0116
7 / 8 turn distance is 0.0811
full turn distance is 0.0926
Off switch| error | home | error | differnce
-19.7498 0.0000 -19.6715 0.0000 0.0782
Off switch Max Min Difference
-19.7498 -19.7498 0.0000
home posiiton Max Min Difference
-19.6715 -19.6715 0.0000
;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;;
Homing axis 3 plus
1 / 8 turn distance is 0.0116
7 / 8 turn distance is 0.0811
full turn distance is 0.0926
Off switch| error | home | error | differnce
0.0722 0.0000 0.0604 0.0000 0.0118
Off switch Max Min Difference
0.0722 0.0722 0.0000
home posiiton Max Min Difference
0.0604 0.0604 0.0000
Axis has both minus and plus home switches
-Distance between home positions is 19.7320
-Distance between travel limits is 19.6500
-Difference between distances is 0.0820
Finished testing home/limit switches
*** FAILED SYSTEM TEST ***
Reminder, for support please follow this post: viewtopic.php?f=20&t=383
We can't "SEE" what you see...
Mesa, AZ
We can't "SEE" what you see...
Mesa, AZ
(Note: Liking will "up vote" a post in the search results helping others find good information faster)
Re: Jumping Z axis when homing!
Note that the reason for failing the system test was an X travel limit 0.057" too long, and not the marginal Z+ homing search distance.
(Note: Liking will "up vote" a post in the search results helping others find good information faster)
-
- Community Expert
- Posts: 9944
- Joined: Tue Mar 28, 2017 12:01 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: Yes
- Oak CNC controller: No
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC12: Yes
- CNC11: Yes
- CPU10 or CPU7: Yes
- Location: Mesa, AZ
Re: Jumping Z axis when homing!
Yes, I failed to mention that....
Reminder, for support please follow this post: viewtopic.php?f=20&t=383
We can't "SEE" what you see...
Mesa, AZ
We can't "SEE" what you see...
Mesa, AZ
(Note: Liking will "up vote" a post in the search results helping others find good information faster)