Acorn with CL-HSS57 Steppers, and KBMG212D, C89
Bill Griggs
Re: Acorn with CL-HSS57 Steppers, and KBMG212D, C89
Post by Bill Griggs »
Marty,
I have the second stepper running now. I watched your Emco Compact 5 bench testing video where you explained how to set up CNC12 Lathe. Great video.
The thing I am having the most trouble with (SOLVED) is setting the motor to revolve once per inch like yours did. The information on the motor indicates that it has 1.8 degrees per step and also has a 1000 line encoder. Default microstepping settings for the drive are either 400 or 1000 (depending on which manual you read).
I found another manual that indicated that the micro stepping is set to 400. When I set this as the axis configuration I now get 1 turn per inch. Should I change the dip switches to set micro stepping at 1000 or just leave it as is?
Plasma CNC Controller: Yes
Bill Griggs wrote: Thu Jul 29, 2021 11:37 am Marty,
You should change the dipswitches on the drive to at least 2000
Bill Griggs
I installed the spindle drive and motor today for bench testing. KBMG212D with C89 board.
I am not getting any rotation out of the motor so I must have something configured wrong. M3 S1000 command turns on relay 4 (Enable) but that is as far as it gets. I am not sure what to test yet. So I am rereading the KBMG manual.
The power light is on on the KBMG212D and also on the C89. Suggestions?
One thing that was not clear in the video was the signal and COM wires from the C89 to the Acorn. Since both wire were black in the video, it was not clear which wire went to which terminal. I have the orange wire going into the Analog and the black wire into GND on the C89. On the Acorn I have the orange wire going into the VOUT and the Black to COM on the Acorn analog terminals.
Acorn Analog Out
Acorn Analog Out
C89 analog Output
C89 analog Output
C89 board
C89 board
KBMG212D
KBMG212D
It almost came off the bench today. Partially disconnected it. 'll revisit. I have too many irons in the fire.....
Just added:
viewtopic.php?f=61&t=6097
I hope this helps. Its up to you to set the KBMG up for your motor.
Bill Griggs
I decided to buy a second KBMG-212D driver to see if something was wrong with the driver.
I swapped out all the connectors to the new driver after setting all the jumpers to match the original setup.
After I checked my wiring a few times I decided to power up the system. When AC is applied to the Acorn and to the driver the motor begins spinning prior to CNC12 being loaded. However I don't have control over the motor when CNC12 boots.
I need to take some measurements at Acorn to make sure I am still getting 0-10V. I also suspect I may need to adjust the POTS on the drive.
Bill
Did you take the enable jumper OFF SIMG?
You will definitely have to adjust the posts on SIMG AFTER you have CNC control of the drive
Bill Griggs
martyscncgarage wrote: Mon Aug 09, 2021 5:47 pm Did you take the enable jumper OFF SIMG?
Yes. The jumper is not connected for Enable.
Then you had a closure of that enable circuit. Are you sure you are on NORMALLY OPEN contact on Acorn relay board?