generated 3 phase wild leg connection.

All things related to Centroid Oak, Allin1DC, MPU11 and Legacy products

Moderator: cnckeith

Post Reply
MMCDesign
Posts: 9
Joined: Sun Oct 07, 2018 1:10 am
Acorn CNC Controller: No
Allin1DC CNC Controller: Yes
Oak CNC controller: No
CNC Control System Serial Number: K21145
DC3IOB: No
CNC11: No
CPU10 or CPU7: Yes

generated 3 phase wild leg connection.

Post by MMCDesign »

Good afternoon,

I have watched the training video on YouTube and the instruction there is to ensure the manufactured leg of the power is on L1 of the main disconnect switch. I noticed my original hook up seems to have it in the middle terminal (see photo), L2? The Z phase, i.e. the manufactured one, is connected to the white wire).
The voltage to ground from the manufactured leg is higher than 120v.
My questions are what are the terminals? The switch is not labeled. Is L1 the one on the right or the left?
My second question is did I damage the system running it this way?

Thanks,
Mike
Attachments
Wiring drawing version
Wiring drawing version
Disconnect drawing
Disconnect drawing
Disconnect in box as it is now
Disconnect in box as it is now


polaraligned
Posts: 232
Joined: Mon Feb 07, 2011 8:03 pm
Acorn CNC Controller: No
Allin1DC CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: 1030090103
DC3IOB: Yes
CNC12: Yes
CNC11: Yes
CPU10 or CPU7: No
Location: Montvale, NJ

Re: generated 3 phase wild leg connection.

Post by polaraligned »

The generated phase is not clean and best used for motor run only. The other 2 phases are used for all electronics including relays, etc. I don't know your machine, but I had problems on a 16x60" lathe when the factory diagram was incorrect and the generated phase was being supplied to relays on a non-CNC machine.

I would suggest tracing the wires out carefully and making sure the generated leg only goes to the motor and not any electronics.


cncsnw
Community Expert
Posts: 4540
Joined: Wed Mar 24, 2010 5:48 pm

Re: generated 3 phase wild leg connection.

Post by cncsnw »

Identify which two legs, coming off the bottom of the rotary disconnect switch, are feeding the transformer that is immediately behind and below it.

Hook your clean utility legs to those two. Hook your wild leg to the remaining one.


MMCDesign
Posts: 9
Joined: Sun Oct 07, 2018 1:10 am
Acorn CNC Controller: No
Allin1DC CNC Controller: Yes
Oak CNC controller: No
CNC Control System Serial Number: K21145
DC3IOB: No
CNC11: No
CPU10 or CPU7: Yes

Re: generated 3 phase wild leg connection.

Post by MMCDesign »

The 2nd and 3rd terminals from the left seem to be feeding the transformer. I get a connection check on them with my multimeter when the disconnector is switched to the on position and the two input lines on the transformer are touched. That would indicate the left most terminal is the line to connect the wild leg to.


Dave_C
Posts: 669
Joined: Wed Nov 15, 2017 8:25 pm
Acorn CNC Controller: Yes
Allin1DC CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: none
DC3IOB: No
CNC11: No
CPU10 or CPU7: No
Location: Springfield, MO. USA
Contact:

Re: generated 3 phase wild leg connection.

Post by Dave_C »

The voltage to ground from the manufactured leg is higher than 120v.
This is common on many three phase power supplies but if you measure line to line you will see a different voltage.

Wild legs were never intended to be used as a power source to ground, only line to line!

Dave C.
Grizzly G0678 Mill ,CNC conversion with Acorn. G4004G Lathe, Mach 3 conversion to Acorn.


Post Reply