Re: New Build: SYIL X4 CNC Mill, Clearpath SDSK, C86ACCP & Centroid Acorn
Hi Clay,
You bring up some good points that deserve some further clarification.
The section of the ClearPath manual that you posted is specifically regarding the connecting and disconneting of power cables. The purpose of this sequence is to prevent the arc (spark) when a live connection is made (or removed) to the motor. The repeated arcing at the connector can cause damage to the terminals in the connector. By removing the AC power going to the power supply, it prevents this arcing nature because there is no voltage.
You are correct that the E-Stop should be wired on the AC side of the power supply (sorry Marty). For safety certifications, this is the only way to get certified. It is also a good idea for a DIY machine. If the power supply is left "energized" by disconnecting the DC side of the power supply, there is "some potential" for that energy to get distributed even after the E-stop is pressed. If the AC line going to the power supply is interupted, this risk is eliminated. As you mentioned, you can also take advantage of the regen circuitry of the IPC-5 intelligent power center during deceleration.
I should make one more clarifying statement. There is a dynamic brake function in the motor that is set "on" by default when the motor ships from the factory. The ClearPath dynamic brake (not to be confused with a spring-applied power-off brake) shunts the regenerative energy produced by the motor in a power off, regenerative enregy condition. The amount of braking power that can be dissipated by the motor during deceleration depends on the size of the motor and the style of motor winding used (P, S, or D winding).
The dynamic brake function will be disabled when the encoder stops moving for 1 second. So if the motor is left with the dynamic brake configured from the factory, the motor is not truly "free-wheeling" when power is removed with an E-stop.
Hope this helps.
Tom T.
You bring up some good points that deserve some further clarification.
The section of the ClearPath manual that you posted is specifically regarding the connecting and disconneting of power cables. The purpose of this sequence is to prevent the arc (spark) when a live connection is made (or removed) to the motor. The repeated arcing at the connector can cause damage to the terminals in the connector. By removing the AC power going to the power supply, it prevents this arcing nature because there is no voltage.
You are correct that the E-Stop should be wired on the AC side of the power supply (sorry Marty). For safety certifications, this is the only way to get certified. It is also a good idea for a DIY machine. If the power supply is left "energized" by disconnecting the DC side of the power supply, there is "some potential" for that energy to get distributed even after the E-stop is pressed. If the AC line going to the power supply is interupted, this risk is eliminated. As you mentioned, you can also take advantage of the regen circuitry of the IPC-5 intelligent power center during deceleration.
I should make one more clarifying statement. There is a dynamic brake function in the motor that is set "on" by default when the motor ships from the factory. The ClearPath dynamic brake (not to be confused with a spring-applied power-off brake) shunts the regenerative energy produced by the motor in a power off, regenerative enregy condition. The amount of braking power that can be dissipated by the motor during deceleration depends on the size of the motor and the style of motor winding used (P, S, or D winding).
The dynamic brake function will be disabled when the encoder stops moving for 1 second. So if the motor is left with the dynamic brake configured from the factory, the motor is not truly "free-wheeling" when power is removed with an E-stop.
Hope this helps.
Tom T.
Last edited by teknic_servo on Tue Apr 06, 2021 8:36 am, edited 1 time in total.
-
- Posts: 102
- Joined: Tue Dec 15, 2020 11:12 am
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: 0035FF8A1900-10082038
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
Re: New Build: SYIL X4 CNC Mill, Clearpath SDSK, C86ACCP & Centroid Acorn
Thanks for the clarification! It’s great to hear that the servos won’t be damaged by these types of e stops with high inertial loads.teknic_servo wrote: ↑Fri Apr 02, 2021 3:36 pm Hi Clay,
You bring up some good points that deserve some further clarification.
The section of the ClearPath manual that you posted is specifically regarding the connecting and disconneting of power cables. The purpose of this sequence is to prevent the arc (spark) when a live connection is made (or removed) to the motor. The repeated arcing at the connector can cause damage to the terminals in the connector. By removing the AC power going to the power supply, it prevents this arcing nature because there is no voltage.
You are coprrect that the E-Stop should be wired on the AC side of the power supply (sorry Marty). For safety certifications, this is the only way to get certified. It is also a good idea for a DIY machine. If the power supply is left "energized" by disconnecting the DC side of the power supply, there is "some potential" for that energy to get distributed even after the E-stop is pressed. If the AC line going to the power supply is interupted, this risk is eliminated. As you mentioned, you can also take advantage of the regen circuitry of the IPC-5 intelligent power center during deceleration.
I should make one more clarifying statement. There is a dynamic brake function in the motor that is set "on" by default when the motor ships from the factory. The ClearPath dynamic brake (not to be confused with a spring-applied power-off brake) shunts the regenerative energy produced by the motor in a power off, regenerative enregy condition. The amount of braking power that can be dissipated by the motor during deceleration depends on the size of the motor and the style of motor winding used (P, S, or D winding).
The dynamic brake function will be disabled when the encoder stops moving for 1 second. So if the motor is left with the dynamic brake configured from the factory, the motor is not truly "free-wheeling" when power is removed with an E-stop.
Hope this helps.
Tom T.
Thanks! It’s always great to hear from you guys on the forum!
-Clay
-
- Posts: 9915
- Joined: Tue Mar 28, 2017 12:01 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: Yes
- Oak CNC controller: No
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC12: Yes
- CNC11: Yes
- CPU10 or CPU7: Yes
- Location: Mesa, AZ
Re: New Build: SYIL X4 CNC Mill, Clearpath SDSK, C86ACCP & Centroid Acorn
Clay,
I have followed Centroid schematics in my build. Centroid uses an appropriately specified contactor to break DC voltage and current to its All in One DC FROM the DC power supply (Bridge rectifier, filter capacitor, transformer) The contactor must be rated for the voltage and current. Those are the contactors I use. (Eaton/Moeller and have spoken with their staff about their ratings). Centroid Engineers design and build their cabinets that way.
Please see attached All in One DC Schematic as an example. (That contactor is carrying about 155VDC across its contacts for example, and the drive is on the load side of the contactor)
Teknic documentation says it is permissible to disconnect DC power. So, I followed the traditional course as depicted in the schematic. If that is not correct, then Teknic should address or clarify it.
Respectfully,
Marty
I have followed Centroid schematics in my build. Centroid uses an appropriately specified contactor to break DC voltage and current to its All in One DC FROM the DC power supply (Bridge rectifier, filter capacitor, transformer) The contactor must be rated for the voltage and current. Those are the contactors I use. (Eaton/Moeller and have spoken with their staff about their ratings). Centroid Engineers design and build their cabinets that way.
Please see attached All in One DC Schematic as an example. (That contactor is carrying about 155VDC across its contacts for example, and the drive is on the load side of the contactor)
Teknic documentation says it is permissible to disconnect DC power. So, I followed the traditional course as depicted in the schematic. If that is not correct, then Teknic should address or clarify it.
Respectfully,
Marty
- Attachments
-
- S14747 Mill, 220 110VAC, ALLIN1DC, Direct 110VAC Rectification, Spindle Reversing Contactors.pdf
- (301.9 KiB) Downloaded 184 times
Reminder, for support please follow this post: viewtopic.php?f=20&t=383
We can't "SEE" what you see...
Mesa, AZ
We can't "SEE" what you see...
Mesa, AZ
-
- Posts: 150
- Joined: Wed Jan 01, 2020 2:40 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
Re: New Build: SYIL X4 CNC Mill, Clearpath SDSK, C86ACCP & Centroid Acorn
Marty,
I understand your logic following the All-in-One schematic. However on the Acorn schematic utilizing the 100 Ohm Resistors and the C86ACCP, the contactor disabling the motor DC voltage is not included.
As the Enable- line is run thru the E-Stop on the Centroid Schematic and the C86ACCP utilizes Relay 1 to disable the motors in an E-Stop condition, I am trying to understand the need to remove the AC or DC power from the Clearpath motors in an E-Stop condition.
Following the latest wiring diagram for the Acorn with multiple SDSK Teknic motors provided by Centroid and following the wiring diagram from my spindle manufacturer, When I create an E-Stop condition the motors disengage, the spindle stops, and I get an Emergency Stop notification which pops up in CNC-12. With the Clear Path motors configured to move to the commanded position after a fault, and +24V provided on the Teknic power distribution board, the servos move to the commanded position when the E-stop is released and motion is commanded on the VCP or Wireless pendant.
I understand your logic following the All-in-One schematic. However on the Acorn schematic utilizing the 100 Ohm Resistors and the C86ACCP, the contactor disabling the motor DC voltage is not included.
As the Enable- line is run thru the E-Stop on the Centroid Schematic and the C86ACCP utilizes Relay 1 to disable the motors in an E-Stop condition, I am trying to understand the need to remove the AC or DC power from the Clearpath motors in an E-Stop condition.
Following the latest wiring diagram for the Acorn with multiple SDSK Teknic motors provided by Centroid and following the wiring diagram from my spindle manufacturer, When I create an E-Stop condition the motors disengage, the spindle stops, and I get an Emergency Stop notification which pops up in CNC-12. With the Clear Path motors configured to move to the commanded position after a fault, and +24V provided on the Teknic power distribution board, the servos move to the commanded position when the E-stop is released and motion is commanded on the VCP or Wireless pendant.
-
- Posts: 9915
- Joined: Tue Mar 28, 2017 12:01 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: Yes
- Oak CNC controller: No
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC12: Yes
- CNC11: Yes
- CPU10 or CPU7: Yes
- Location: Mesa, AZ
Re: New Build: SYIL X4 CNC Mill, Clearpath SDSK, C86ACCP & Centroid Acorn
It's good practice to remove power from servo motors during a fault or Estop condition. It's the only way you can nearly ensure there is no unintended axis movement.
I run the VFD common through the Estop contactor as well. In my build I am using 4 contacts on the contactor. 1 to enable C86ACCP, for VFD common (controlling FWD/REV) and I am running DC+ and DC- from the Teknic power supply through two contacts. Spears the current across two contacts instead of one. Overkill? Perhaps.
I personally choose to treat my small conversions as if they were large conversions.
Marty
I run the VFD common through the Estop contactor as well. In my build I am using 4 contacts on the contactor. 1 to enable C86ACCP, for VFD common (controlling FWD/REV) and I am running DC+ and DC- from the Teknic power supply through two contacts. Spears the current across two contacts instead of one. Overkill? Perhaps.
I personally choose to treat my small conversions as if they were large conversions.
Marty
Reminder, for support please follow this post: viewtopic.php?f=20&t=383
We can't "SEE" what you see...
Mesa, AZ
We can't "SEE" what you see...
Mesa, AZ
-
- Posts: 23
- Joined: Thu Mar 28, 2019 4:11 pm
- Acorn CNC Controller: No
- Allin1DC CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
Re: New Build: SYIL X4 CNC Mill, Clearpath SDSK, C86ACCP & Centroid Acorn
All-
There are many ways to skin a...potato (dodged that one). I do some things at home that probably would not pass the OSHA or CE certification boards. That said, I feel safe, trust my work, and know how my devices should be used.
That said, and for clarity, the recommended procedure (or required in some instances) for removing power in an E-stop condition is to remove power from the 75VDC power supply. This leaves the bus power for the motors disabled. The logic inside the motors can be kept active with the 24VDC power supply that is "throttled back" so that it cannot move any motors under its own power. In this way, nobody that sticks their arm inside the machine under an E-stop will end up being called "lefty" because the motors unexpectedly move. (however, an axis can still potentially drop, right?)
The message is not intended to say that Centroid is "wrong" or Marty is "wrong" but more a matter of degree of compliance. If you are at home and not going to get your machine certified by a saftey group, follow the method you believe in to keep you safe. Sometimes certification requirements can be taken to an extreme, and I get it. Do I persoanlly consider removing machine power from the DC side of the power supply to be safe enough? Perhaps. But I am not allowed to fully endorse it based on many conversations with certification companies. Carry on...
Tom T.
There are many ways to skin a...potato (dodged that one). I do some things at home that probably would not pass the OSHA or CE certification boards. That said, I feel safe, trust my work, and know how my devices should be used.
That said, and for clarity, the recommended procedure (or required in some instances) for removing power in an E-stop condition is to remove power from the 75VDC power supply. This leaves the bus power for the motors disabled. The logic inside the motors can be kept active with the 24VDC power supply that is "throttled back" so that it cannot move any motors under its own power. In this way, nobody that sticks their arm inside the machine under an E-stop will end up being called "lefty" because the motors unexpectedly move. (however, an axis can still potentially drop, right?)
The message is not intended to say that Centroid is "wrong" or Marty is "wrong" but more a matter of degree of compliance. If you are at home and not going to get your machine certified by a saftey group, follow the method you believe in to keep you safe. Sometimes certification requirements can be taken to an extreme, and I get it. Do I persoanlly consider removing machine power from the DC side of the power supply to be safe enough? Perhaps. But I am not allowed to fully endorse it based on many conversations with certification companies. Carry on...
Tom T.
-
- Posts: 29
- Joined: Thu Feb 11, 2021 9:16 pm
- Acorn CNC Controller: No
- Allin1DC CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC12: No
- CNC11: No
- CPU10 or CPU7: No
Re: New Build: SYIL X4 CNC Mill, Clearpath SDSK, C86ACCP & Centroid Acorn
Any word on the C86accp with terminal blocks? I think it would be an easier install, but if it is going to be another couple of weeks, I may just order the one with the normal connectors.
-
- Posts: 9915
- Joined: Tue Mar 28, 2017 12:01 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: Yes
- Oak CNC controller: No
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC12: Yes
- CNC11: Yes
- CPU10 or CPU7: Yes
- Location: Mesa, AZ
Re: New Build: SYIL X4 CNC Mill, Clearpath SDSK, C86ACCP & Centroid Acorn
CNC4PC got their first batch of C86ACCP Rev2.5 in. I was sent one to test and comment on. They work fine, they are making some very minor modifications and have placed a larger order. They should be in by end of May 2021. IF you need one they have a handful of the first run left.
They have both the Molex and Terminal blocks.
Here are a few pictures:
They have both the Molex and Terminal blocks.
Here are a few pictures:
Reminder, for support please follow this post: viewtopic.php?f=20&t=383
We can't "SEE" what you see...
Mesa, AZ
We can't "SEE" what you see...
Mesa, AZ
-
- Posts: 29
- Joined: Thu Feb 11, 2021 9:16 pm
- Acorn CNC Controller: No
- Allin1DC CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC12: No
- CNC11: No
- CPU10 or CPU7: No
Re: New Build: SYIL X4 CNC Mill, Clearpath SDSK, C86ACCP & Centroid Acorn
What are the revisions? if they aren't a big deal, I'll order one right now.
-
- Posts: 9915
- Joined: Tue Mar 28, 2017 12:01 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: Yes
- Oak CNC controller: No
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC12: Yes
- CNC11: Yes
- CPU10 or CPU7: Yes
- Location: Mesa, AZ
Re: New Build: SYIL X4 CNC Mill, Clearpath SDSK, C86ACCP & Centroid Acorn
Not enough to worry about. Screen printing is going to change a bit and the screw terminals are going to be spaced away from the Molex connectors a bit more. He only has a handful leftTaylorPilot wrote: ↑Wed Apr 21, 2021 12:03 am What are the revisions? if they aren't a big deal, I'll order one right now.
Reminder, for support please follow this post: viewtopic.php?f=20&t=383