When you try and jog one axis before Homing or using MDI, CNC12 will enable that axis, try and jog another axis, it will generally enable that axis.
Take a look at the drive enable LED's on Acorn when you jog an axis after starting CNC12. Should be as I described.
Keep in mind, I have not hardwired Clearpath motors using the Centroid schematic. And for $50 and knowing it has been approved for use by Teknic,
I will continue to use the C86ACCP WHEN the terminal version comes out and IF I do more conversions with CP motors.
Mystery solved:
I used the $10.00 relay board that Gary Campbell recommended years ago. I have only one input set for "drive Fault" and so I daisy chain the NO contacts of three of the relays so that if one relay opens on a drive fault I get the alarm. It does not matter which drive faults.
Marty said you can use the VCP to move the table on startup and Acorn will enable that drive and, yes it will but therein lies the issue. Acorn only enables the
one drive and so drive movement is tried but the other two HLFB relays are open and so I get a drive fault.
If I touch the F3 key (MDI) all three drives enable and I can then exit MDI and they stay enable just as if I had homed the machine.
Nothing wrong, just all depend on how your wired your HLFB for drive fault. If you have an ether16 and plenty of ports this is not an issue. Just use one input for each drive fault input.
Grizzly G0678 Mill ,CNC conversion with Acorn. G4004G Lathe, Mach 3 conversion to Acorn.