Hammer HNC Table Top Router - VFD Intermediate Spindle Speed Errors <resolved>

All things related to the Centroid Acorn CNC Controller

Moderator: cnckeith

Post Reply
Nigelo
Posts: 416
Joined: Tue Dec 11, 2018 4:03 pm
Acorn CNC Controller: Yes
Plasma CNC Controller: No
AcornSix CNC Controller: No
Allin1DC CNC Controller: No
Hickory CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: F045DA80C8B8-0905181172
E415F6F70BC3-0318203049
98F07B91FC6B-0123236802
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No
Location: UK East Coast

Hammer HNC Table Top Router - VFD Intermediate Spindle Speed Errors <resolved>

Post by Nigelo »

Following Mike Richards Oscilloscope thread and a prompt from Gary Campbell on another thread for tuning, I got myself a reliable laser tacho and found huge Spindle Speed errors at lower speeds I didn't know existed. My system had otherwise been running with zero problems with several jobs up to 1 hour each.

Machine bought new direct from Felder UK without the standard Eding Controller.

Setup:
  • Leadshine MX4660 driver, Meanwell RSP-320-48 48v PSU and relays all under-slung the router deck
IMG_20201208_1720280.jpg
IMG_20200919_1329150.jpg
  • Router's External connection interface presented as DB25 (I/O) and DB9 (E-Stop)
IMG_20201208_1722560.jpg
  • Schneider Altivar 320 VFD (Model ATV320U22M2C) mounted in separate steel case with incoming line filter. The VFD is hard wired to Router with extended 2 metre lead
IMG_20210307_1723098.jpg
  • Both Router and VFD case have their own mains power plugs with earth connection
  • All above installed, pre-wired and configured by Felder prior delivery
  • VFD parameters set by Felder to min 100Hz (6,000 rpm) max 400Hz (24,000 rpm) and control uses AI1 set for 0-10Vdc
    VFD Settings HNC HF V1 3 (2).xlsx
    (76.48 KiB) Downloaded 84 times
  • Control cabinet therefore just houses the Acorn and its PSU, 8 x Relay board and 2 channel E-Stop plus DB25 BoBs and presenting an external DB25 and DB9 to match the Router's external conectors
    Interconnection Schema Table.JPG
  • Control Cab to router connections: 25 core shielded parallel and 4 core shielded CY cables. Both shields grounded at Control Cab only
Observations:
1) OEM's VFD to spindle power cable shielded but NOT connected to GND at either end
2) OEM's Internal control cable to VFD not shielded (LAPP Olflex Classic 110 7 core x 0.75mm)
3) Felder has directly tied the Router chassis ground to the onboard 0Vdc COM at control cable connection to VFD COM
4) VFD control cable routed parallel to Spindle Power cable over full chassis length and extension to VFD enclosure with no separation.
Router bottom view.jpg
Test results:
Tests.GIF

I've attached the VFD installation and Programming manuals. The usual report and the Electrical Layout as provided by Felder in German with my rough translation to follow.

Any ideas?
Attachments
ATV320_Programming_Manual_EN_NVE41295_03.pdf
(2.5 MiB) Downloaded 100 times
ATV320_Installation_manual_EN_NVE41289_06.pdf
(10.55 MiB) Downloaded 100 times
Hope this helps
Nigel

"You can lead a horse to water but you cannot force it to drink"


Nigelo
Posts: 416
Joined: Tue Dec 11, 2018 4:03 pm
Acorn CNC Controller: Yes
Plasma CNC Controller: No
AcornSix CNC Controller: No
Allin1DC CNC Controller: No
Hickory CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: F045DA80C8B8-0905181172
E415F6F70BC3-0318203049
98F07B91FC6B-0123236802
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No
Location: UK East Coast

Re: Hammer HNC Table Top Router - VFD Intermediate Spindle Speed Errors

Post by Nigelo »

Attatch usual Report and Felder's Electrical Layout
Attachments
report_E415F6F70BC3-0318203049_2021-03-08_15-18-34.zip
(667.25 KiB) Downloaded 76 times
Hammer Electrical Layout.pdf
(3.74 MiB) Downloaded 98 times
Hope this helps
Nigel

"You can lead a horse to water but you cannot force it to drink"


cncsnw
Community Expert
Posts: 4595
Joined: Wed Mar 24, 2010 5:48 pm

Re: Hammer HNC Table Top Router - VFD Intermediate Spindle Speed Errors

Post by cncsnw »

If you graph "Observed VFD Hz" vs. "Observed Acorn VDC", is it approximately linear?

There are different ways to enforce a minimum speed (e.g. 100Hz / 6000RPM). One is a cutoff, where the speed command (analog voltage reference) is still scaled from zero, but any command below the minimum speed results in the minimum speed instead. Another is to change the bias and gain of the analog voltage reference, so that a zero-volt reference commands the minimum speed, and it goes up linearly from there.

The standard Acorn PLC program is written to assume the former. It looks like your drive may be set up as the latter.


Nigelo
Posts: 416
Joined: Tue Dec 11, 2018 4:03 pm
Acorn CNC Controller: Yes
Plasma CNC Controller: No
AcornSix CNC Controller: No
Allin1DC CNC Controller: No
Hickory CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: F045DA80C8B8-0905181172
E415F6F70BC3-0318203049
98F07B91FC6B-0123236802
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No
Location: UK East Coast

Re: Hammer HNC Table Top Router - VFD Intermediate Spindle Speed Errors

Post by Nigelo »

cncsnw wrote: Fri Mar 12, 2021 1:06 pm If you graph "Observed VFD Hz" vs. "Observed Acorn VDC", is it approximately linear?

There are different ways to enforce a minimum speed (e.g. 100Hz / 6000RPM). One is a cutoff, where the speed command (analog voltage reference) is still scaled from zero, but any command below the minimum speed results in the minimum speed instead. Another is to change the bias and gain of the analog voltage reference, so that a zero-volt reference commands the minimum speed, and it goes up linearly from there.

The standard Acorn PLC program is written to assume the former. It looks like your drive may be set up as the latter.
Thanks, much appreciated.
Graph as follows:

As Installed
As Installed Observed Hz vs Vdc Graph.JPG
Analog 0-10v & COM Rerouted: Acorn direct to VFD (CY Cable: Shield to GND both ends)
Observed Hz vs Vdc Graph.JPG
This raises 2 questions:

1) The difference between the 2 graphs appears to show that shielded cabling has improved signalling. The 2nd graph is linear whereas the 1st is not although almost. Do you think the problem is with the VFD config rather than Ground Shielding?

2) The ATV320 is highly configurable. What type of VFD parameter should I look at for correcting this?

Nigel
edit to correct Graph titles: "Observed VFD Vdc" should read "Observed Acorn Vdc"
Hope this helps
Nigel

"You can lead a horse to water but you cannot force it to drink"


cncsnw
Community Expert
Posts: 4595
Joined: Wed Mar 24, 2010 5:48 pm

Re: Hammer HNC Table Top Router - VFD Intermediate Spindle Speed Errors

Post by cncsnw »

My guess would be:
LSP [Low Speed] Motor frequency at minimum reference, can be set between 0 and [High speed] (HSP).
If that is where the 100Hz minimum is set, you could change that to 0Hz.

Then, if you still want to prevent the spindle trying to run slower than 6000RPM, set a minimum of 6000 in CNC12 Control Configuration.


Nigelo
Posts: 416
Joined: Tue Dec 11, 2018 4:03 pm
Acorn CNC Controller: Yes
Plasma CNC Controller: No
AcornSix CNC Controller: No
Allin1DC CNC Controller: No
Hickory CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: F045DA80C8B8-0905181172
E415F6F70BC3-0318203049
98F07B91FC6B-0123236802
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No
Location: UK East Coast

Re: Hammer HNC Table Top Router - VFD Intermediate Spindle Speed Errors

Post by Nigelo »

Many thanks Marc, resetting LSP to 0Hz cracked most of the issue as follows:

Original "as installed" but with LSP set to 0
As installed with LSP at 0.JPG
In addition to LSP set to 0, I redirected Acorn's Analog Vout / COM direct to VFD with CY cable (fully grounded shield) to simulate replacing the VFD control cable with a fully shielded CY variant.
Direct CY cable with LSP set to 0.JPG
Final Comparison
Final Comparison.JPG
RPM Comparison
RPM Comparison.JPG
RPM Comparison.JPG (39.12 KiB) Viewed 2979 times
Following the excellent results above, it's clear I need to leave the VFD's low speed LSP parameter at zero and replace the VFD control cable. Whilst I can live with the very small speed difference, I will try tuning that out by slightly increasing Acorn's Max Spindle RPM. The minimum speed will of course be controlled by setting 6,000 rpm in Acorn

Again Marc, very many thanks, really appreciated

Nigel
Hope this helps
Nigel

"You can lead a horse to water but you cannot force it to drink"


Nigelo
Posts: 416
Joined: Tue Dec 11, 2018 4:03 pm
Acorn CNC Controller: Yes
Plasma CNC Controller: No
AcornSix CNC Controller: No
Allin1DC CNC Controller: No
Hickory CNC Controller: No
Oak CNC controller: No
CNC Control System Serial Number: F045DA80C8B8-0905181172
E415F6F70BC3-0318203049
98F07B91FC6B-0123236802
DC3IOB: No
CNC12: Yes
CNC11: No
CPU10 or CPU7: No
Location: UK East Coast

Re: Hammer HNC Table Top Router - VFD Intermediate Spindle Speed Errors

Post by Nigelo »

Having replaced the VFD control cable with a shielded version grounded at both ends; properly grounded the VFD to spindle power cable; and following Marc's advice left the LSP parameter set to 0, I carried further out RPM tests.

Acorn's analog output appears to be effectively an opamp, and therefore is presumably affected by downstream capacitance and/or resistance. As the preliminary results indicated proper grounding had actually increased the Commanded vs Observed RPM errors in the lower ranges, I tried installing a 0.1 uF capacitor (actually 97 nF or 0.097 uF) as recommended for stability reasons. Incredibly that completely resolved the problem in conjunction with leaving the LSP set at 0.

For completeness and to help other in the same situation, I attach the final RPM comparison
Final Spindle RPM Comparison
Final Spindle RPM Comparison

Could someone mark this thread as resolved - Many thanks

Nigel
Hope this helps
Nigel

"You can lead a horse to water but you cannot force it to drink"


Post Reply