Acorn drive interface question
I have seen a few references from members that when connecting to Leadshine hybrid drives you need to use the DB25 connection method. Also, the sample schematics reflect the same. For wiring convenience, I would rather use the screw terminals. The Leadshine prefers 5V pull up on step+ and dir+. In looking at the Acorn manual (relevant page attached), it appears to me that should be fine. The 24V on the Acorn outputs is on the cathode side of 24V so really doesn't affect the outputs dealing with the 5V logic. Am I missing something?
Also, does it buy you anything to hook up the enable lines? The drive defaults to automatically being in the enabled state. From my bench test, the Enable lights come on for the first move and seem to stay on from there on. If the board faults, it seems like it would just as likely stop sending step pulses as releasing the enable line. Any thoughts on that?
Thanks
Also, does it buy you anything to hook up the enable lines? The drive defaults to automatically being in the enabled state. From my bench test, the Enable lights come on for the first move and seem to stay on from there on. If the board faults, it seems like it would just as likely stop sending step pulses as releasing the enable line. Any thoughts on that?
Thanks
- Attachments
-
- manual_pg3.pdf
- (147.24 KiB) Downloaded 164 times
(Note: Liking will "up vote" a post in the search results helping others find good information faster)
-
- Posts: 2357
- Joined: Sat Nov 18, 2017 2:32 pm
- Acorn CNC Controller: Yes
- Plasma CNC Controller: No
- AcornSix CNC Controller: Yes
- Allin1DC CNC Controller: No
- Hickory CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: Acorn 238
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
- Location: Bergland, MI, USA
- Contact:
Re: Acorn drive interface question
These questions have been answered ad nauseum and the answers will not change. Some stepper drives will work properly on the open collector terminals, but no LeadShine that I have tried, the prefer the line drive ttl signal from the DB25.
Acorns enable signal operates in a way much more compatible with servo than stepper drives. You could use it if you invert the logic by reprogramming the drives, but I don't know what you would gain.
Acorns enable signal operates in a way much more compatible with servo than stepper drives. You could use it if you invert the logic by reprogramming the drives, but I don't know what you would gain.
GCnC Control
CNC Control & Retrofits
CNC Depot Modular ATC kits
https://www.youtube.com/user/Islaww1/videos
CNC Control & Retrofits
CNC Depot Modular ATC kits
https://www.youtube.com/user/Islaww1/videos
(Note: Liking will "up vote" a post in the search results helping others find good information faster)
-
- Posts: 124
- Joined: Fri Nov 27, 2020 11:34 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: waiting on delivery
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
- Location: Pattison, TX
- Contact:
Re: Acorn drive interface question
Well, guess that’s pretty clear
(Note: Liking will "up vote" a post in the search results helping others find good information faster)
-
- Community Expert
- Posts: 9955
- Joined: Tue Mar 28, 2017 12:01 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: Yes
- Oak CNC controller: No
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC12: Yes
- CNC11: Yes
- CPU10 or CPU7: Yes
- Location: Mesa, AZ
Re: Acorn drive interface question
The Leadshine CS-D508 will work from the Acorn header provided you provide +5VDC to the +Pul, +Dir, +ENA (IF Used) from the Acorn power supply, and then the -Pul, -Dir, -Ena
to the Acorn ST, DR, EN.
I did 3 systems with them in that fashion and 2 using the current revision of CNC4PC's C86_Acorn board along with the C34 interface boards for the hybrid drives connected by their RJ45 cables:
https://www.cnc4pc.com/c86-connector-bo ... oller.html
https://www.cnc4pc.com/c34-for-hybrid-servo-drive.html
Leadshine drives and motors can be purchased from CNC4PC as well
Reminder, for support please follow this post: viewtopic.php?f=20&t=383
We can't "SEE" what you see...
Mesa, AZ
We can't "SEE" what you see...
Mesa, AZ
(Note: Liking will "up vote" a post in the search results helping others find good information faster)
-
- Posts: 124
- Joined: Fri Nov 27, 2020 11:34 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: waiting on delivery
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
- Location: Pattison, TX
- Contact:
Re: Acorn drive interface question
Thanks Marty. I had it working on the bench hooked up as you suggest. It seemed ok, but I decided if the TTL drivers were the proven way, why risk flakey operation. So, I built a DB25 cable.
I still get a bad t confused about why you s really what with the screw terminals and DB25. The manual indicates that the screw terminals allow for additional I/O. I read somewhere else that if you use input 1 on the DB25, you can’t use IN1 on the terminals. I assume the two connection approaches are the same logic signal, but different circuit interface (I.e. ttl driver versus open collector). If that’s the case, I don’t see how it adds I/o. But, I don’t need any more so am ok
I still get a bad t confused about why you s really what with the screw terminals and DB25. The manual indicates that the screw terminals allow for additional I/O. I read somewhere else that if you use input 1 on the DB25, you can’t use IN1 on the terminals. I assume the two connection approaches are the same logic signal, but different circuit interface (I.e. ttl driver versus open collector). If that’s the case, I don’t see how it adds I/o. But, I don’t need any more so am ok

(Note: Liking will "up vote" a post in the search results helping others find good information faster)
-
- Community Expert
- Posts: 9955
- Joined: Tue Mar 28, 2017 12:01 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: Yes
- Oak CNC controller: No
- CNC Control System Serial Number: none
- DC3IOB: No
- CNC12: Yes
- CNC11: Yes
- CPU10 or CPU7: Yes
- Location: Mesa, AZ
Re: Acorn drive interface question
You are best to use the Input and Output terminals on Acorn.
If you use input and output terminals on the DB25, you may not use them on Acorn.
It does NOT add I/O.
Simply put, there are 8 inputs and 8 outputs for use on Acorn.
A few of them are shared on the DB25
If you use input and output terminals on the DB25, you may not use them on Acorn.
It does NOT add I/O.
Simply put, there are 8 inputs and 8 outputs for use on Acorn.
A few of them are shared on the DB25
Reminder, for support please follow this post: viewtopic.php?f=20&t=383
We can't "SEE" what you see...
Mesa, AZ
We can't "SEE" what you see...
Mesa, AZ
(Note: Liking will "up vote" a post in the search results helping others find good information faster)
-
- Posts: 12
- Joined: Thu Sep 30, 2021 8:40 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: 4562
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
Re: Acorn drive interface question
martyscncgarage wrote: ↑Wed Dec 30, 2020 12:15 pmThe Leadshine CS-D508 will work from the Acorn header provided you provide +5VDC to the +Pul, +Dir, +ENA (IF Used) from the Acorn power supply, and then the -Pul, -Dir, -Ena
to the Acorn ST, DR, EN.
I did 3 systems with them in that fashion and 2 using the current revision of CNC4PC's C86_Acorn board along with the C34 interface boards for the hybrid drives connected by their RJ45 cables:
https://www.cnc4pc.com/c86-connector-bo ... oller.html
https://www.cnc4pc.com/c34-for-hybrid-servo-drive.html
Leadshine drives and motors can be purchased from CNC4PC as well
Thanks Marty. I have the Stepperonline CL86T which I believe is re-branded Leadshine CS-D808. There is conflicting Info, just want to be sure that this is OK for hooking up these drives. It seems to be working, although I have not used the machine much yet. I had some misalignment on a 2 sided part that could have been bad registration on my part, although I used alignment pins. I just want to make sure that I do not loose steps. Unfortunately using the DB25 header would require a remodel of my finally completed cabinet.
(Note: Liking will "up vote" a post in the search results helping others find good information faster)
-
- Site Admin
- Posts: 8962
- Joined: Wed Mar 03, 2010 4:23 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: Yes
- Oak CNC controller: Yes
- CNC Control System Serial Number: none
- DC3IOB: Yes
- CNC11: Yes
- CPU10 or CPU7: Yes
- Contact:
Re: Acorn drive interface question
Need support? READ THIS POST first. http://centroidcncforum.com/viewtopic.php?f=60&t=1043
All Acorn Documentation is located here: viewtopic.php?f=60&t=3397
Answers to common questions: viewforum.php?f=63
and here viewforum.php?f=61
Gear we use but don't sell. https://www.centroidcnc.com/centroid_di ... _gear.html
All Acorn Documentation is located here: viewtopic.php?f=60&t=3397
Answers to common questions: viewforum.php?f=63
and here viewforum.php?f=61
Gear we use but don't sell. https://www.centroidcnc.com/centroid_di ... _gear.html
(Note: Liking will "up vote" a post in the search results helping others find good information faster)
-
- Posts: 45
- Joined: Thu Mar 05, 2020 1:15 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: No
- Oak CNC controller: No
- CNC Control System Serial Number: A81087B4FFCB-0712192265
- DC3IOB: No
- CNC12: Yes
- CNC11: No
- CPU10 or CPU7: No
- Location: Farmington Hills, MI
Re: Acorn drive interface question
Per the schematic, it looks like you are feeding +5VDC into the +24VDC of terminal H4 on the Acorn board.... There is conflicting Info, just want to be sure that this is OK for hooking up these drives. It seems to be working, although I have not used the machine much yet. I had some misalignment on a 2 sided part that could have been bad registration on my part, although I used alignment pins. I just want to make sure that I do not loose steps. Unfortunately using the DB25 header would require a remodel of my finally completed cabinet.
(Note: Liking will "up vote" a post in the search results helping others find good information faster)
-
- Site Admin
- Posts: 8962
- Joined: Wed Mar 03, 2010 4:23 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: Yes
- Oak CNC controller: Yes
- CNC Control System Serial Number: none
- DC3IOB: Yes
- CNC11: Yes
- CPU10 or CPU7: Yes
- Contact:
Re: Acorn drive interface question
screw terminals are open collector, they use the power you provide 5,12,24 vdc .
see this post.
viewtopic.php?f=63&t=1699
see this post.
viewtopic.php?f=63&t=1699
Need support? READ THIS POST first. http://centroidcncforum.com/viewtopic.php?f=60&t=1043
All Acorn Documentation is located here: viewtopic.php?f=60&t=3397
Answers to common questions: viewforum.php?f=63
and here viewforum.php?f=61
Gear we use but don't sell. https://www.centroidcnc.com/centroid_di ... _gear.html
All Acorn Documentation is located here: viewtopic.php?f=60&t=3397
Answers to common questions: viewforum.php?f=63
and here viewforum.php?f=61
Gear we use but don't sell. https://www.centroidcnc.com/centroid_di ... _gear.html
(Note: Liking will "up vote" a post in the search results helping others find good information faster)