I tell ya this board came just in time for me. Hopefully I dont drive everyone crazy with all my inquiries. I purchased a "Teco 50" inverter and of coarse the diagram verbage does not match the Ajax verbage. I was wandering if you guys could translate for me on some of these connections. The first picture is the connections on the Dc310. The second and third picture is from the inverter itself. Thanks in advance.
(Note: Liking will "up vote" a post in the search results helping others find good information faster)
-
- Site Admin
- Posts: 8952
- Joined: Wed Mar 03, 2010 4:23 pm
- Acorn CNC Controller: Yes
- Allin1DC CNC Controller: Yes
- Oak CNC controller: Yes
- CNC Control System Serial Number: none
- DC3IOB: Yes
- CNC11: Yes
- CPU10 or CPU7: Yes
- Contact:
Re: spindle inverter and dc310
sure thing.. the photos of the inverter are a little hard to see, do you have a link to the Teco 50 manual?
Need support? READ THIS POST first. http://centroidcncforum.com/viewtopic.php?f=60&t=1043
All Acorn Documentation is located here: viewtopic.php?f=60&t=3397
Answers to common questions: viewforum.php?f=63
and here viewforum.php?f=61
Gear we use but don't sell. https://www.centroidcnc.com/centroid_di ... _gear.html
All Acorn Documentation is located here: viewtopic.php?f=60&t=3397
Answers to common questions: viewforum.php?f=63
and here viewforum.php?f=61
Gear we use but don't sell. https://www.centroidcnc.com/centroid_di ... _gear.html
(Note: Liking will "up vote" a post in the search results helping others find good information faster)
Re: spindle inverter and dc310
(Note: Liking will "up vote" a post in the search results helping others find good information faster)
Re: TECO FM50 Spindle Inverter Wiring Diagram and DC3IOB
RPMAN,
This is the wiring diagram for your TECO FM50 inverter. Please make sure you set SW1 to "1" for 0-10VDC and be sure to review the TECO documentation for information on setting the parameters in the TECO.
Download the full size PDF here:
This is the wiring diagram for your TECO FM50 inverter. Please make sure you set SW1 to "1" for 0-10VDC and be sure to review the TECO documentation for information on setting the parameters in the TECO.
Download the full size PDF here:
(Note: Liking will "up vote" a post in the search results helping others find good information faster)
Re: TECO FM50 Spindle Inverter Wiring and DC3IOB
Wow, wasnt expecting for you to have to make a drawing, but thanks a million!! I would guess that somebody else in the future will need this info also. Thanks again.
(Note: Liking will "up vote" a post in the search results helping others find good information faster)
Re: TECO FM50 Spindle Inverter Wiring and DC3IOB
Rather than wiring directly from "SPIN RESET COM" to "SPIN EN COM", you should route that wire through an open pole of your emergency stop contactor or relay. This will ensure that the run signal (forward or reverse) gets cut off when you press emergency stop, even if the computer, MPU11, and/or DC3IOB have stopped cooperating for any reason.
Scott: where can I find a DC3IOB manual that documents the internal connection and jumper between OUT14/NO and OUT13/COM?
Scott: where can I find a DC3IOB manual that documents the internal connection and jumper between OUT14/NO and OUT13/COM?
(Note: Liking will "up vote" a post in the search results helping others find good information faster)
TRe: TECO FM50 Spindle Inverter Wiring and DC3IOB
Thanks cncsnw for the input. I was just getting on here to ask that question being all the other diagrams I have show that wire going through the e-stop contactor. The jumper you are talking about is J28 between "out14 no" and "out13 com"
(Note: Liking will "up vote" a post in the search results helping others find good information faster)
Re: TECO FM50 Spindle Inverter Wiring and DC3IOB
What Marc points out is correct. In fact, technically, the drawing should also instruct the user to wire the incoming 3 phase through the E stop contactor as well.
I should have mentioned that the drawing was/is for general reference only. It's intent is to show only the bare minimum number of connections needed.
That said, the reason the drawing does not show an interlocked enable or direction bits routed through the Estop contactor is that, more often than not (as judged by the shear number of support requests generated regarding Estop/interlock wiring) end users often don't have the extra poles and/or auxiliary contacts their Estop contactor. -On a seperate but related issue, apparently end user supplied Estop switches rarely have two sets of contacts either
I should have mentioned that the drawing was/is for general reference only. It's intent is to show only the bare minimum number of connections needed.
That said, the reason the drawing does not show an interlocked enable or direction bits routed through the Estop contactor is that, more often than not (as judged by the shear number of support requests generated regarding Estop/interlock wiring) end users often don't have the extra poles and/or auxiliary contacts their Estop contactor. -On a seperate but related issue, apparently end user supplied Estop switches rarely have two sets of contacts either

(Note: Liking will "up vote" a post in the search results helping others find good information faster)
Re: TECO FM50 Spindle Inverter Wiring and DC3IOB
So let me get this right. I should run the "spin EN COM" and the incomming power for the inverter through the e-stop contactor? The incomming line to the inverter is single phase so it would only take up space for two positions. Positive/Neutral or do i just wire positive though it? Either way I have room. The only other wire i have running through the contactor is for the DC power to the DC310B. Thanks for all the input guys. I have done wiring before but nothing like this and I am just tring to avoid a big cloud of smoke and the smell of cash wasted !!! 

(Note: Liking will "up vote" a post in the search results helping others find good information faster)
Re: TECO FM50 Spindle Inverter Wiring and DC3IOB
RPMAN,
I've just added the interlock wiring to the drawing. I did not include the 3 phase interlock through the Estop contactor because this inverter does not have a sep. power input for it's digital functions. That means that if we take the 3 phase off, the inverter goes dark and has to reboot when power is re-applied which can/could be problematic for some inverters.
In practice, physically "taking the enable away" when the estop is pressed will shut the spindle down. In "theory" some people might say that the ONLY way to be SURE the spindle will shut down is to physically remove the 3 phase from the inverter -and they would be right.
I've just added the interlock wiring to the drawing. I did not include the 3 phase interlock through the Estop contactor because this inverter does not have a sep. power input for it's digital functions. That means that if we take the 3 phase off, the inverter goes dark and has to reboot when power is re-applied which can/could be problematic for some inverters.
In practice, physically "taking the enable away" when the estop is pressed will shut the spindle down. In "theory" some people might say that the ONLY way to be SURE the spindle will shut down is to physically remove the 3 phase from the inverter -and they would be right.
(Note: Liking will "up vote" a post in the search results helping others find good information faster)